Posted by: @cathoderayI also note you appear to be using extremely low amounts of energy compared to me.
I am taking only the COP during my economy 7 cheap rate - so only first[ish] 7 hours of the day, and switched off the hot water. My hot water COP is down to about 1.5 right now so affects my overall cop quite a bit, I think I have an issue with my heat exchanger . So trying to exclude those numbers. So yes, this is not a whole day of consumption. My 15% delta is half of Glyns, likely because this is just the glycol difference. I am using the temperature data from the Samsung heat pump. If I put in more accurate temp sensors, my COP may go up a bit more. My target is the 5.9 achieved by "the heat geeks"
Â
You may want to review this post from Glyn.
Â
FWIW, I have calculated the weekly and overall discrepancies between my Class 1/Class B external heat pump only kWh meter (I think I am right in saying Class 1 and Class B mean the same thing, 1% accuracy) and Midea's reported kWh use, and in fairness the Midea figure's aren't that bad. Over 21 weeks, the Midea app (not modbus, I don't yet have enough data, but I think it will be the same) under-reported by 2.45%. The bad news is the discrepancy varies considerably week by week, from a 6.21% under-read to a 2.45% over-read. This variation means I can't simply apply a single correction factor to weekly reading. Grrr...Â
The external meter has an electrical pulse as well as LED pulse output and I am investigating ways of using the electrical pulse (1000 pulses per kWh) to record the meter's consumption figures. This turns out not to be as simple as I thought it would be, and no, I don't want to use an optical counter on the LED plus some ESP voodoo board to do something that should be much more straightforward.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay just on that point, If you can change the meter, there are meters with modbus outputs. I'm probably going to get an SDM120, as I'm not trusting my CT clamp. you have modbus sorted so reading it should be no issue for you?
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @william1066You may want to review this post from Glyn.
Yes, I agree, it is an interesting thread, and further confirms the smoke and mirrors we are up against.
Posted by: @william1066I am taking only the COP during my economy 7 cheap rate - so only first[ish] 7 hours of the day, and switched off the hot water.Â
This is important information! Context means a lot when interpreting COPs. As I said before, I don't really set too much store by short interval COPs, too much volatility, and in Midea's case there is also the integer problem (0.75kWh gets reported as 1kWh, the rounding errors being considerably greater over short runs when the actual numbers are small - 0.75 => 1 is a 33% over-estimate etc). I wonder is Samsung also use integers and so get the same sort of error? However, on the face of it, these rounding errors always increase to reading, yet the Midea app under-reads, so not sure how this all fits together... Consider this:
Actual kWh in/out over an hour:
0.75/2.25 (COP = 3)
Midea rounding
1/3 (COP = 3)
Actual kWh in/out over an hour:
1.25/3.75 (COP = 3)
Midea rounding
2/4 (COP = 2)
Midea thus appears to shoot itself in the foot (because the rounding is proportionally bigger on the smaller kWh in value).
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @iancalderbank@cathoderay just on that point, If you can change the meter, there are meters with modbus outputs. I'm probably going to get an SDM120, as I'm not trusting my CT clamp. you have modbus sorted so reading it should be no issue for you?
I have the SDM120 without the M suffix. M is for modbus...
I could get it changed over but it would need a qualified electrician (I don't think DIY is an option) and as you all know I am a tight wad who will never spend a penny I don't need to spend.
Â
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @iancalderbankIf you can change the meter, there are meters with modbus outputs. I'm probably going to get an SDM120
The two main manufacturers of energy meters are Acrel and Eastron.
Eastron is more commonly imported to European countries.
There are MID-certified units which have guaranteed accuracy for billing purposes, but most about £5 more.
I prefer the 2-module wide version - SDM220 (or SDM230) with Modbus
Posted by: @cathoderayI could get it changed over but it would need a qualified electrician (I don't think DIY is an option)
That depends on how/where it has been fitted.
The 'rules' for changing like-for-like aren't particularly clear to me.
Eg if I have a broken 13A socket faceplate, then it's permissible to change this for a new one without calling out an electrician.
Yes, I realise that the householder has just reconnected wires on a ring main which might not be tight enough, or might cause a 'break' in the ring.
But the alternative is that people wouldn't bother to replace broken faceplates, which is equally dangerous!
Common sense prevails, I think.
Save energy... recycle electrons!
@transparent thanks - am I right in assuming this is pretty close to your professional area of expertise? any particular reason for the recommendation? I've no hard and fast reason for suggesting I'm going to get the 120M, other than its available on openenergy monitor shop! is the 220 more accurate?
Â
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
I have used a cheap "Danfoss" Water Power meter on my Radiator circuit.
My Radiator circuit is isolated from the Heat Pump water loop by an Heat Exchanger.
I have calculated the loss of energy ,
Loss = ((Energy Generated by the SAMSUNG HEAT PUMP - ENERGY READ on the HEAT EXCHANGER OUTPUT )/( Energy Generated by the SAMSUNG HEAT PUMP)x 100 per cent...........
Comparing the COP from the SAMSUNG figures with the REAL COP as seen on the other side of the Heat Exchanger gives
The average SAMSUNG displayed COP is 3.9 while the average REAL COP on the other side of the Heat exchanger is 3.06!
These figures were obtained with the Heating Stopped .
I have not used the Bus outputs on the "Danfoss" water meter ( A £100 EBAY German Sharky under a pseudonym), only taking daily readings.
I will later connect the "Danfoss" to my PC.
iantelescope
Â
Â
Â
Â
Â
You're right @iancalderbank that this is 'very close' to my area of expertise.
I have a friendly qualified electrician who's happy for me to run mains cabling.
He then does the mechanical and electrical tests when he makes the connections within my bank of three(!) mains consumer units.
I sometimes design and create components on a 3D-printer which he hasn't previously met.
For example I have adaptor-collars to connect oval-conduit within wall-plaster to a steel flush-mounted backing-box.
But he's happy to work with me like this because he knows that I
- am pedantic about selecting the correct size wire and mcb trip parameters for a circuit
- understand the insulation and leakage-current characteristics for the materials (plastics) which I use in each situation
- know and implement the rules about having both LV (240v mains) and ELV (below 75v DC) operating within the same environment
- fit more safety and surge-suppression devices than he ever gets to see elsewhere!
Â
I work with micro-controllers (Arduino, AT-tiny, Raspberry-Pi) operating at 3.3 to 5v DC, using milliamps
  alongside solar (120-500v DC) and battery storage (48-58v DC up to 500A)
     alongside LV/mains 216-253v AC up to 40A per circuit
... so I need to have a clear grasp of what separation must be implemented, and what safety (earthing) systems should be present.
Just because I'm running appliances 'off-grid' doesn't mean that there should be any compromises on safety-margins... quite the opposite!
There may not yet be regulations which cover the equipment/systems I'm designing, but I want to develop the practices which could be adopted into 'standards' in the future.
I use a lot of measurement devices, including Modbus,
in such a way that the data-gathering continues when there is a system-failure.
There's no point trying to analyse faults if the data gets lost due to the fault occuring!
I even have volts/current/power meters which operate solely from the PV supply (fluctuating 120-500v).
So if an inverter isn't delivering a consistent output, I can see the discrepancy by comparing with the inputs.
Â
I prefer the Eastron 2-module wide meters because the writing on the lcd is horizontal and it presents more information than the single number on the SDM120-range.
There's a DC version of the Eastron power-meter visible on the left end of the DIN rail in the following photo.
Please don't copy this design of a 4-way inverter-battery protection/combiner.
There were mistakes in the layout such that
- it didn't always 'fail safe' under fault conditions
- there are circumstances under which the inverters couldn't be restarted from the battery storage
There is a new design being built and about to undergo testing.
Â
The work I'm doing is closely allied to the sort of issues which you're discussing here about monitoring and controlling heat-pumps.
In just the same way that you're aiming to avoid a heat-pump cycling, I'm trying to use battery storage whilst needing to know how much energy is stored.
They are equally complex issues to assess.
Save energy... recycle electrons!
@william1066 Grundfos PUMP PWM Frequency....
I stand corrected William........
The Frequency range of the PWM signal is indeed 100 Hz to 4Khz!
I mistakenly tested both of my pumps at a 10 Khz Frequency producing .........Â
Grundfos PUMP PWM Frequency....
I stand corrected William........
The Frequency range of the PWM signal is indeed 100 Hz to 4Khz!
I mistakenly tested both of my pumps at a 10 Khz Frequency producing .
Perfectly linear results....
Sorry....
ian
Â
Have you cured your cycling problem yet?
- 26 Forums
- 2,129 Topics
- 46.8 K Posts
- 28 Online
- 5,654 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: How much am I ‘saving’?
@old_scientist yes, assumptions are crucial. For many p...
By Tim441 , 21 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
That's the sort of good design we would expect from Tes...
By Transparent , 49 minutes ago
-
RE: ASHP heat output monitoring
@carlo I have a 16kw LG Therma V. Installed 2020 so eve...
By Tim441 , 1 hour ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@morgan They may be good but cannot service the heat pu...
By dgclimatecontrol , 1 hour ago
-
RE: Mitsu Wireless Controller and MelCloud
@davidalgarve If they are 'off' because of a timed s...
By Morgan , 4 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 2 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 2 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 2 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 3 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 3 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 3 days ago
-
RE: Who has a V2G EV installation
I agree, but a word of caution. V2X is also sometimes u...
By Majordennisbloodnok , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 4 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 6 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 6 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 1 week ago