Thanks Craig, now lower the LWT setting to 30C and see what happens to how the system operates.
Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Posted by: @craig1980Right, finished timing. Now back to 8 mins on 20 seconds off again.
Flow temp 28.1 set to 30
Indoor 22.1Â
Outdoor 6.5
Room temp 19
Hi Craig,
I'm afraid that I have run out of suggestions.
There appears to be something fundamentally wrong with your heat pump, and/or how the system has been installed. The only thing that I can see that appears to be incorrect is the Teva_out temperature reading of -50C, which could possibly be due to a faulty or disconnected temperature sensor.
I would suggest that you e-mail Samsung Technical Help and ask them why your system may be operating as it is doing.
In the meantime set your system back onto WC mode and adjust for the required indoor temperature.
Â
Okay, many thanks for all of your help. I'll update if I find anything from Samsung. Thanks again. Much appreciated.Â
Interestingly, when I put the settings back to WC I get error E121. Upon looking this up in the manual it saysÂ
"Short-or open- circuit error of the room temperature sensor of the zone 1 indoor unit (detected only when the room thermostat is used) Error source - Hydro unit.Â
Posted by: @hughfPosted by: @mike-hAm I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
It doesn't have a buffer, no...
Which set of instructions say that the samsung needs a buffer?
Â
@hughf Please see the topic about Samsung install and buffer tank
https://renewableheatinghub.co.uk/forums/postid/11342
Freedom Heat Pumps claims a buffer tank is required to be within the Samsung warranty, even though the manual implies otherwise and Joule make a pre-plumbed cylinder without a buffer tank.
Â
@mike-h Ah yes, good old freedom. I’d trust the instructions from midsummer wholesale personally. I know that GH was always getting 911 errors (low flow) on his early installs, so they probably mandated a buffer to deal with that issue, allowing the primary pump to run at full speed to charge the buffer.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 67 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
Day 2 was a beast. All the excess zoning, on/off stats ...
By Mars , 6 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
Water pump will certainly make a hum (which could conce...
By JamesPa , 2 hours ago
-
@jamespa Thanks. Yeah any adjustments Ive made at pr...
By cliffhanger , 2 hours ago
-
RE: Mitsu PAR-WT60R Wireless Controller - options
I have been running mine in auto adapt since 2019 and i...
By Abernyte , 4 hours ago
-
RE: Powerwall 3 or Myenergi or something else?
Many of those tariffs are simple time of use tariffs, w...
By Temperature_Gradient , 14 hours ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 15 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 3 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 3 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 3 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 4 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 6 days ago