As you say, nothing appears to be changing dramatically. Though I fail to understand how your home is maintaining an indoor temperature of 18C, with an outdoor temperature of 6C.
Now try setting your system in fixed LWT mode with a setting of 35C.
Â
@derek-m I've no idea. 🤣
I turned the system off for the Octopus saving session at 17:30 room stats showing 18. Went out and came back at 20:30. Turned back on and room stats were at 17.5. Not sure if you need that info but just in case it's relevant.Â
I'll have to work out how to set fixed lwt mode. I'll do it tomorrow. Thanks again.Â
@derek-m overnight it was 4 degrees and it has struggled to keep 18. The house is at 17.5 this morning. COP is down to 3.3 and it's using more power and running for longer. 15.6kw yesterday 13.3hours operation time (that's with turning off for 3hours)and a generation of 51.7.
@derek-m overnight it was 4 degrees and it has struggled to keep 18. The house is at 17.5 this morning. COP is down to 3.3 and it's using more power and running for longer. 15.6kw yesterday 13.3hours operation time (that's with turning off for 3hours)and a generation of 51.7.
Posted by: @craig1980Is this what you mean?
Â
Yes, that would appear to be the correct method. Try running with a LWT of 35C and see how the system responds, and if it stops the 20 second off periods.
Â
Okay, that's done. It was already on standard temperature "water outlet". Could that have been an issue?Â
How is the system operating now? Is it still running 8 mins on and 20 secs off?
What is happening with the room and radiator temps?
What are the flow and temperature readings etc?
Changing the way that the system is being operated is to try to find what is causing the 20 seconds shutdown.
So, it appears to run constantly but at quite high power usage of 1.9kw instantaneous power.Â
Rads feel warmer to the touch but room temp stays at around 18 according to room stats and thermometers that I used for radiator temps.Â
Outside temp is 6.0 according to wired remote.
Water outlet 35.4
Indoor 21.5 (remember, this is in the airing cupboard with the UVC).Â
Posted by: @craig1980So, it appears to run constantly but at quite high power usage of 1.9kw instantaneous power.Â
Rads feel warmer to the touch but room temp stays at around 18 according to room stats and thermometers that I used for radiator temps.Â
Outside temp is 6.0 according to wired remote.
Water outlet 35.4
Indoor 21.5 (remember, this is in the airing cupboard with the UVC).Â
Now measure the top and bottom temperatures on two or three relevant radiators, and the flow rate and temperature readings from the information screens.
Â
- 26 Forums
- 2,136 Topics
- 46.8 K Posts
- 27 Online
- 5,662 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Powerwall 3 or Myenergi or something else?
I have a very similar set up in almost all respects, ex...
By JamesPa , 1 hour ago
-
RE: Does anyone have experience of a smart water meter?
Thanks, @technogeek. So far as I can make out, whilst...
By Majordennisbloodnok , 15 hours ago
-
RE: Mitsubishi PAR-WT60R-E Wireless Controller installation
@morgan They have been paired once but it was thought b...
By DavidAlgarve , 17 hours ago
-
RE: Isolating the system for a planned power cut
A great many ground-mounted local substation transforme...
By Transparent , 17 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Having bit the bullet and paid £250 for a service, our ...
By Old_Scientist , 2 days ago
-
@bontwoody me too. I've contacted Heat Geek today, and ...
By Mars , 2 days ago
-
New heat pump heating system underperforming in Italy... Advice needed!
hi all, first post! I've just renovated a house in sout...
By robinlawrie , 2 days ago
-
RE: Anyone still weathering it out with Agile?
I went to Agile when I had solar installed July last ye...
By NJT , 2 days ago
-
RE: Mitsu Wireless Controller and MelCloud
Well it has now become obvious that the installation of...
By DavidAlgarve , 3 days ago
-
RE: Say hello and introduce yourself
Whilst you're busy installing services (pipes and wires...
By Transparent , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@editor I know it was formally announced at Ish the oth...
By PatrickVito , 5 days ago
-
@moman0311 welcome to the forums. I've received your em...
By Mars , 5 days ago
-
RE: Thermostat for Ideal Logic Air with 3 zone support
No harm at all in plumbing it as 3 zones, I would have ...
By JamesPa , 6 days ago
-
RE: ASHP heat output monitoring
@carlo I see there is a discussion in Facebook user gro...
By Tim441 , 6 days ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 7 days ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 1 week ago
-
RE: How much am I ‘saving’?
@old_scientist like for like comparisons are almost imp...
By Tim441 , 1 week ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 1 week ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 1 week ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 1 week ago