But at the beginning of the 8 min cycle they are both within 0.5 degree of each other at 22
Outside unit heat pump fans run for around 5 mins then it's quiet until 8 mins and 20 seconds then it starts again.Â
I will have a look at the data and get back to you tomorrow.
In the meantime, with the system running, measure the temperature in the central section of each radiator at both the top and the bottom, along with the relevant room temperature.
Posted by: @transparentLet's label a few bits:
-- Attachment is not available --
Am I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
Â
@mike-h I have two small tanks above the uvc but I'm assuming they aren't buffer tanks? I have a cold water header tank in the loft and the system outside. That's all I have so unless one of those two tanks are a buffer then I don't have one.
Posted by: @mike-hAm I right in thinking that Craig's system (from Joule) does not have a buffer tank? I'm still trying to get my head round the mandatory buffer tank for Samsung ASHP question.
Â
It doesn't have a buffer, no...
Which set of instructions say that the samsung needs a buffer?
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @craig1980@mike-h I have two small tanks above the uvc but I'm assuming they aren't buffer tanks? I have a cold water header tank in the loft and the system outside. That's all I have so unless one of those two tanks are a buffer then I don't have one.
-- Attachment is not available --
The white one is the expansion vessel for the domestic hot water (from the unvented cylinder) and the grey one is the expansion vessel for the heating/ashp circuit.
As you have an unvented cylinder, there is no need for any tanks in the loft, and also no need for that shower booster pump. I'm not sure why you still have those in your installation.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Below is a link for the controller instructions. Select the home screen and monitor the outdoor temperature whilst your system goes through its cycling process.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 101 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
-
RE: Heat Pump Damage on install - useable or dealbreaker?
I would agree.Even if it does not materially effect per...
By bontwoody , 20 minutes ago
-
RE: Electricity price predictions
@diverted-energy sounds like good tariff for you. Octop...
By JulianC , 1 hour ago
-
RE: Who’s Caved and Switched the Heating On Already?
In the last week, the external temperature in south Man...
By GrahamF , 3 hours ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 3 hours ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
I hear you on the locality issue @transparent, and I ag...
By Scalextrix , 6 hours ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 7 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 8 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 9 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 1 day ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 4 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 4 days ago