Posted by: @craig1980
- @derek-m I didn't set them back to 21 straight away and left them for a day. At night it was longer between but by the next day it was back to the same.Â
Had the indoor temperature changed? A further test would be to watch closely the operation of the wireless receivers for the thermostats when the system performs its short off - on cycle.
Also check that all the plug and socket connections on the circuit board are making good contact.
Â
Posted by: @craig1980@derek-m no change in the indoor temperature. The lights on the receivers do not change when it cycles on and off.
Did you close the airing cupboard door overnight? The reason I ask is that sometimes equipment, and circuit boards, can suffer intermittent faults due to thermal expansion.
What water law settings are applied at the moment?
Â
@derek-m the airing cupboard door is always shut. It doesn't get that warm in there.Â
Pics of the screen set up of water law.Â
Not sure if the set up with "floor" is correct. Whether it should be FCU instead?
Also running -2 on the home screen which I'm led to believe is a short cut to adjusting a water law setting. Assuming the 31?Â
Â
Posted by: @derek-mYes, I've seen all the different diagrams in the manuals, but it doesn't tell one which is correct. Also I don't see the point in having two pumps to do the job that one pump should be able to do.
I’d go with the one from the Jule installation manual, as it’s a Jule cylinder/heatpump package. Now that we’ve seen some more photo’s you can clearly see that the hydraulics match what is shown I their manual exactly.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @derek-mHi Hugh,
Do you know if the Samsung controller will still use WC when operating with the indoor temperature located within the controller?
I have a lot of time for Glyn Hudson over on YouTube who has just DIYd his 5kW Samsung install and has documented it with a decent video. From the comments I’ve been having with his, he says that the Samsung will still use WC when the wired controller is used as for measuring room temperature. I’ve asked him if the controller will also support load compensation and reduce the flow temperature when the room is approaching the target temp. Inversely, increasing the flow temp to recover quickly from a nighttime or away/holiday mode setback temperature.
He uses a single pump (with PWM control) on his setup but his primary pipe work is short.
Â
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Let me have a read through the manual and decipher what some of the descriptions mean. I'll get back to you tomorrow.
Glyn has his 5kW Samsung wired/plumbed up with full monitoring, the data can be viewed at:
https://emoncms.org/samsung5kw
Single grundfos PWM pump, a heatpump cylinder with a 1m2 coil (the same cylinder I’ve got - they were cheap on eBay back in the summer), and radiators throughout.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
- 26 Forums
- 2,104 Topics
- 46.3 K Posts
- 87 Online
- 3,393 Members
Join Us!
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist I found the switching between tariff jus...
By Toodles , 10 hours ago
-
RE: Plug and play solar. Thoughts?
Have a read of my previous posts on so-called Balcony S...
By Lucia , 13 hours ago
-
@editor @bart Hi, I can see a few problems with your in...
By Brendon Uys , 16 hours ago
-
RE: Ecodan consuming 100kwh per day in new build!!!
Well at least that solves the mystery of where the exce...
By JamesPa , 18 hours ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
"To tell you the truth, I don't know if HAL is homicida...
By Scalextrix , 18 hours ago
-
RE: Location of hot water isolation valve on cylinder
@rossowheels if you isolate the water supply in it will...
By ASHP-BOBBA , 1 day ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 2 days ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 2 days ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 2 days ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 2 days ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 3 days ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 3 days ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 3 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 4 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 4 days ago