This discussion started elsewhere but may fit better here..
Posted by: @jamespa... a safety concern which also occurs in Germany with the same or lesser risk is not legitimate (ie either the risk is sufficiently small or does not in fact exist). A 'legitimate safety concern' would therefore need to be one which does not occur in Germany at all, or which does occur in Germany but with a materially lower level of risk.
I am as puzzled as @jamespa about what could have led to a decision in the UK to effectively mandate these "bidirectional" RCDs while in Germany they do not expect them for the Ikea DIY PV kits.
The relevant addition to IET regulations (BS 7671) reads as follows:
CHAPTER 53 PROTECTION, ISOLATION, SWITCHING, CONTROL AND MONITORING
530.3.201 Selection and erection of equipment for protection shall take account of appropriate use of either a unidirectional protective device or a bidirectional protective device.
NOTE: Product standards as listed in Appendix 1 for some protective devices, including RCCBs, RCBOs, circuit-breakers and AFDDs, require these devices to be marked to indicate if they are unidirectional e.g. “in” and “out” or “line” and “load” or arrows.
The IET update refers to the BEAMA 2023 note, that mentions differing guidance from industry bodies on whether a microgenerator should or should not be installed to the load side of any RCCB that is shared with other circuits, it does not comment on the source. But electricians are expected to follow IET regulations to the letter.
Anyway, the current stance could be seen as restricting the use of DIY kits in the UK market, with the RCD needing prior replacement by an electrician.
So that the Public could lead the way, someone needs to demystify this risk.
I also wonder if the risk could be made acceptable if (assuming that there is one RCBO dedicated to the socket circuit), after plugging the DIY kit, the RCBO switch is flicked on and off a few times, some of this with a pause of a few seconds. If the RCD is still shown to work when the test button is pressed (as this IET Wiring Regulation is not retrospective) it could be left in use. If the RCD stops working, an electrician needs to swap the RCBO with one suitable for multi generation?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
@batpred I cant see how this risk relates to something that is different in German wiring practice than in the UK, unless German wiring practice has always used bidirectional RCBOs for all circuits, so that there is no chance that any randomly chosen circuit is on a unidirectional RCBO. I frankly doubt this is the case unless someone can assure me otherwise.
My suspicions are, sadly, growing.
If we want to ensure that this is not the case we would need civil servants that understand this stuff enough to grill the industry. That doesnt mean that they need to be experts, just that they need to have a level of understanding to spot likely BS/protectionism. Our culture (for 53 years out of 80) of low regulation and outsourcing government skills to industry, for better or worse, prevents that from happening.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaIf we want to ensure that this is not the case we would need civil servants that understand this stuff enough to grill the industry. That doesnt mean that they need to be experts, just that they need to have a level of understanding to spot likely BS/protectionism. Our culture (for 53 years out of 80) of low regulation and outsourcing government skills to industry, for better or worse, prevents that from happening.
I agree, I doubt that Germany regulators would have insisted on special types of RCDs without a good reason (and there would not be any before the spread of multi generation over the last decade).
On our system, I think the MPs would be expected to do the grilling, or trading standards if they still have teeth. H&S do not seem to have grilled much around the flammable external insulation.
Perhaps as @transparent says, the change needs to be from direct action by the Public that wants to use these things..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @batpredI agree, I doubt that Germany regulators would have insisted on special types of RCDs without a good reason (and there would not be any before the spread of multi generation over the last decade).
Germany, and other EU countries have historically had a single RCD for every circuit, not one per circuit. These are typically type A or F/B RCDs (Not AC type) and have been mandated since 2007 in Germany. Having multiple RCDs (4 to 6 circuits per RCD) is a fairly recent thing.
My blog where I write about all the systems in place and decisions made for my off-grid house at 63 degrees north in Finland.
Posted by: @batpredam as puzzled as @jamespa about what could have led to a decision in the UK to effectively mandate these "bidirectional" RCDs [...]
...
Anyway, the current stance could be seen as restricting the use of DIY kits in the UK market, with the RCD needing prior replacement by an electrician.
Note to readers coming across this topic in future.
In UK it is common practice to use the term RCD when referring to a device which detects leakage to earth, but has no over-current protection.
This 'shorthand' isn't to be confused with a writer referring generically to residual current breakers (rcd), as @batpred is here.
An rcd can be either an RCD or an RCBO.
In the sentences which I have just quoted, the residual current breaker being referred to is an RCBO.
Save energy... recycle electrons!
Posted by: @transparentAn rcd can be either an RCD or an RCBO.
In the sentences which I have just quoted, the residual current breaker being referred to is an RCBO.
Yes, the common practice here seems to be for the term RCD to mean an RCCB while the term RCBO (that also includes current over protection) is used for an RCBO.
The British manufacturers association defines RCDs more generically, as below.
The term RCDs covers a range of products some of which are listed below:
• RCCB (Residual Current Operated Circuit-Breaker without Integral Overcurrent Protection)
• RCBO (Residual Current Operated Circuit-Breaker with Integral Overcurrent Protection)
• SRCD (Socket-Outlet incorporating a Residual Current Device)
• FCURCD (Fused Connection Unit incorporating a Residual Current Device) PRCD (Portable Residual Current Device)
• CBR (Circuit-Breaker incorporating Residual Current Protection) IC-CPD (In-Cable Control and Protective Device for mode 2 charging of electric road vehicles)
• MRCD (Modular Residual Current Device)
The issue that lead to mandating bidirectional versions for these types of circuits occurs in multiple varieties of RCDs.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
That may be so @batpred
But you've used the term RCD (in CAPS) in a different way to the rest of us in this topic,
and meaning different things within your own posts.
That's why I needed to post clarifications.
Save energy... recycle electrons!
Posted by: @transparentThat may be so @batpred
But you've used the term RCD (in CAPS) in a different way to the rest of us in this topic,
and meaning different things within your own posts.That's why I needed to post clarifications.
I acknowledge I have not been consistent in all previous posts!
The reason I followed your post mentioning rcd and RCD with the definitions BEAMA (and probably the IET) are using is just so that future consumers reading this can easily see the full range of devices potentially impacted. As they may be more than the ones covered in the IET regulations that electricians follow to the letter.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Is there a way of testing this (without calling out an electrician)?
I am certain my rcbo bi-directional.
Our batteries and inverter are both on the same RCBO.
We did have a trip a while ago and both the batteries and inverter switched off.
Firstly @bash please post a photo showing that RCBO.
We might be able to work out which model it is, and therefore deduce if it's bi-directional.
Secondly, when you press the Test button on the RCBO, does it actually open the contacts?
Save energy... recycle electrons!
Posted by: @bashIs there a way of testing this (without calling out an electrician)?
You can press the test button.
I posted a bit more about it above.
In our case, we could use MCBs..
We may look at it again if we find a detailed analysis of an instance where this RCD issue occurred.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
I will press the test button again to confirm, but it did completely trip the inverter when I last checked.
This is the rcbo.
Wylex 40A 30mA Type A DP C Curve Bidirectional Mini RCBO
https://www.screwfix.com/p/wylex-40a-30ma-type-a-dp-c-curve-bidirectional-mini-rcbo/4298x
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 232 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
I'd be happy with what you have (so would millions of o...
By Deltona , 19 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson I see, I misunderstood obviously. So you set LW...
By Tasos , 37 minutes ago
-
This is absolutely standard for any sealed pressurised ...
By JamesPa , 10 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 10 hours ago
-
RE: What determines the SOC of a battery?
@batpred Your BMS parameters will be the same as m...
By Bash , 11 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 12 hours ago
-
RE: Setback savings - fact or fiction?
I also need to correct something I said by mistake earl...
By cathodeRay , 12 hours ago
-
RE: Electricity price predictions
@judith Thanks for sharing, and nice to see how the ...
By Batpred , 12 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 15 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 15 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 15 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 17 hours ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 17 hours ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 19 hours ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 20 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 20 hours ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 1 day ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I don't know about Solis inverters. It isn't a featur...
By Transparent , 2 days ago
-
Daikin Altherma 3 H HT - Freeze Prevention Threshold
Hi. We have an Altherma 3 HT (18kW I think) which, now ...
By RICHARDF5033 , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@petch We are not yet compatible with the R290 from Gra...
By Will H , 2 days ago