@marvinator80 these are 2 different things. By way of example... I have GivEnergy kit.
Inverter is Gen1 Hybrid 5kw
Batteries are 3 x 8.2kwh = 24.6kwh capacity
My inverter can convert DC to AC up to 6.5kw
With Nominal AC Output Power 5kw
BUT the max it will charge/discharge from batteries is at 2.5kwh
So if my batteries are fully discharged it will take 10 hours to charge them! Meaning I can only fill them at say 10% per hour ... a 3 hour cheap slot filling 30%.
Not ideal - but not worth upgrading. So I just have to work with that to maximise the way I use Agile
Hope that clarifies... and helps
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@jamespa thanks James. I’d be installing a Zappi (already have an Eddi) as it seems to be compatible with both Octopus and the car (BMW i4).
And the battery seemingly does allow storage from the grid in its settings. So 6 hours at night I can charge the car, power the ASHP and charge the battery for 10 kWh of electricity for the pump and general house use at the 7p rate and then any other grid use is 25p.
think this could be excellent in winter particularly and seriously impact my ASHP costs.
@tim441 got you now. Thank you.
I have 10kW batteries and they charge at about 2.1kWh, so the 6 hours overnight 7p rate should be just about ok for me, I think.
Posted by: @marvinator80I have 10kW batteries and they charge at about 2.1kWh, so the 6 hours overnight 7p rate should be just about ok for me, I think.
The conclusion is right but just to correct the units - you have a 10kWh battery and it charges at about 2.1kW.
Think of kW like speed and kWh like distance. Alternatively remember that kWh is exactly what it says ie killowat(s) times hour(s). So 1kWh is 1kW for an hour, or 0.5kW for 2hrs, or 2 kW for half an hour etc.
Thus 2.1kW for 6 hrs is 12.6kWh, more than you need to fully charge the battery, so in fact it will stop charging after a bit less than 5 hours.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa yep, that’s my understanding. It might discharge for a bit when full and top up a little and with DoD of 90% I will prob get 10ish from a 6 hour overnight charging stretch, costing circa 70p.
I hope this is an appropriate thread to sort of re-start a topic questioning the average that those readers on OE’s Agile tariff find themselves paying per kW/h at present (or in the last few months at least). I swapped to Cosy on 1st. July and as best I can make out, this has ben consistently cheaper during the lowest rate in the tariff than any daily offerings from Agile.
I would appreciate it if any readers on Agile who select their HH’s to run their household needs and charge their storage (battery or heat store) at the most economic rates would like to say what their average unit costs are using this method.
I have been observing the daily findings for Agile as published by Agile Rates and they express the lowest rates as ‘average off-peak’ rate; this hovers around the 20-22 pence per kWh and has been in this ball park for the last few months on all but perhaps 8-10 days when there has been plunge pricing. Please, if any Agile user has the time to check their consumption and average price, I would be delighted to know.
I am keeping tabs on the published ‘average off-peak’ rates but wonder if the more savvy user (admittedly, those with time on their hands or an automation procedure to carry out the task for them) has been able to ‘better’ that average. My Cosy tariff lowest rate is still under 13 pence per kWh and I have not seen anything to approach this according to Agile Prices daily listings. Regards, Scroogely, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles I have been monitoring on a monthly basis since switching to Agile in March. I have solar & batteries.... so endeavour to import when cheap using WonderWatt as app to help. spreadsheet dates slightly wrong due to split monthly bills but totals are correct. I've now got Octopus to send invoices for calendar month
Ignoring solar ... so just Agile imports: total 4026kwh @ 10.23p
since 1st July to 31st Oct 2287kwh @9.25p
obviously last 2 or 3 weeks have not been so good due to lack of wind but even now its around 18p on the short term. so I think i will be able to get under 15p average in the next month and maybe nearer 12p if the wind blows nicely!
July was high due to hot tub! grrrrr!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@tim441 Thank you Tim, which means that July - October (The area of greatest interest at present) averaged 10.472 pence per kWh - this appears to suggest that Agile Prices algorithms use different parameters! Perhaps they use a wider time range than is actually required to fill / charge your set-up each day. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles well ... 10.472 is the simple ave of the 4 months ave prices divided by 4... but i think its more accurate to take the actual kwh and prices... which is:
1st July to 31st Oct 2287kwh @ 9.25p
i imagine Agile own averages uses a simple average through the day. But I fill batteries at night (sometimes very cheaply) and use almost nothing at peak rates
it makes all the comparisons very hard! different usage, battery sizes, charge/discharge rates etc all in the mix!
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@toodles we probably need to swap notes again at year end....and every couple of months
I see Octopus are stopping Fixed Export as an annual contract and changing to variable. For now continuing at 15p but with no term. Sadly my contract expires next March so will be interesting to see if they cut summer export rates.
I have not heard how much notice they will give of a change in export price.
During period from Oct to about end April I use everything my solar produces - so not an issue for now.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @toodles@tim441 I should have been an accountant - I know how to cook the books!😉 Toodles.
...although taking them with a pinch of salt will do nothing good for your blood pressure. 😉
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
-
Who's your electricity provider and what's your tariff?
1 month ago
-
Outcome for 2024 - with Agile, ASHP, PV, Batteries, EV
10 months ago
-
Switching tariff in Winter? or stick year round?
1 year ago
-
Confusion over Octopus Tariffs
1 year ago
-
Octopus tariffs - API & choosing best tariff
2 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,265 Topics
- 50.6 K Posts
- 673 Online
- 5,924 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Electricity price predictions
well, I expect both grid level and home level are neede...
By Batpred , 15 minutes ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 24 minutes ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@mairia Indeed, ours is on the side wall in the airing ...
By Toodles , 51 minutes ago
-
RE: My DIY Heat Pump installation
@steelbadger Good point and I will have to see how i...
By Polar bear , 51 minutes ago
-
RE: Oil Boiler & Heat Pump Hybrid System
@paultheheating ‘It’s an ill wind that does nobody any ...
By Toodles , 58 minutes ago
-
RE: UFH downstairs and radiators upstairs balancing question
@davidnolan22 First I must declare I know naff-all abou...
By Toodles , 2 hours ago
-
RE: One flow valve appears to be duff
You might want to consider the following common faults:...
By IaAck , 7 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
We are on the Intelligent Octopus Go tariff. We instal...
By GrahamF , 10 hours ago
-
RE: New build installation query
@paullacey While the others wait for more info do you m...
By ASHP-BOBBA , 19 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
I have only just spotted this post, sorry I missed it e...
By JamesPa , 23 hours ago
-
RE: British Gas Heat Pump Installation Complaint
@bgno, the other consideration for legionella cycles ar...
By Mars , 1 day ago
-
@old_scientist I dont monitor the tank temperature but ...
By bontwoody , 1 day ago
-
RE: Say hello and introduce yourself
Hello @paultheheating - I'm a rural Moderator! What's...
By Transparent , 1 day ago
-
RE: What valves to replace radbots?
Yes. Radbots just replace TRV heads. TRV heads push t...
By JamesPa , 1 day ago
-
RE: Who has a V2G EV installation
Im looking at Anderson or Simpson and Partners, somethi...
By AgentGeorge , 1 day ago
-
RE: When will fusion be producing energy?
I am thinking of the case where AI was able to distingu...
By Batpred , 2 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
Very definitely. I think the market has changed a bit...
By JamesPa , 2 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
The following diagram is taken from the Meter Operator'...
By Transparent , 2 days ago