My ASHP is running out of hot water

88 Posts
6 Users
11 Reactions
16.7 K Views
(@curlykatie)
Estimable Member Member
443 kWhs
Joined: 2 years ago
Posts: 77
Topic starter  

 

CB22E6B6 AE56 4943 93F5 F948BCF590FF

@derek-m thank you! I’ll have a good look at the manual, this is really useful!

before I change anything with the heating I just wanted to clarify. Both zone 1 and zone 2 were off and heating was working on both floors but controlled with the flow rate set at 55 when we moved in. The photo showing zone 1 on and zone 2 off,as when I went into wether compensation, these are the options that came up. I have only switched on zone 1 as it says ‘high temp’ and this is the curve I wanted to select. I wasn’t sure what the purpose of the low temp curve was so have left zone 2 off.
I have attached a screen shot of the manual I have been following which was sent to me by the installer!

 


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

I'm afraid that like most of the user manuals it is not very clear what is actually meant by many of the descriptions. If you could carry out the test that I suggested it may become clear what the zone settings need to be, whether that is both On, one On and one Off, or both Off.

When you first moved in I do believe that your system was set for a fixed water flow temperature of 55C, which is far from ideal.

 


   
ReplyQuote
(@curlykatie)
Estimable Member Member
443 kWhs
Joined: 2 years ago
Posts: 77
Topic starter  

@derek-m thank you. I’ll do the suggested over the weekend and get back to you,

thanks again,

katie


   
ReplyQuote
(@curlykatie)
Estimable Member Member
443 kWhs
Joined: 2 years ago
Posts: 77
Topic starter  

@derek-m here’s my results!

 

all stats turned down to 16

on ‘weather temp set’ screen (photo as previous)-

zone 1 H-mode High Temp-ON

zone 2 H-mode Low temp- OFF

Zone valve actuators- valves closed up and downstairs

 

downstairs kitchen turned up to 25 on stat- heating came on, valve opened labelled ‘UF down’

no change to the above controller display

Kitchen stat turned back down and heating went off

 

upstairs bedroom turned up to 25 on stat- heating came on, valve opened labelled ‘UF up’

no change to the above controller display.

hope this makes sense! 

I have been monitoring the DHW temp since I turned the green pump down to 1. Unfortunately it doesn’t seem to have made any difference and the tank still dropped over night but 9 degrees (without use), and continues to need re-heating 3-4 times per 24 hours (set to re-heat after a temp drop of 10 degrees).

Thank again for your help,

Katie 

 


   
👍
1
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

Posted by: @curlykatie

@derek-m here’s my results!

 

all stats turned down to 16

on ‘weather temp set’ screen (photo as previous)-

zone 1 H-mode High Temp-ON

zone 2 H-mode Low temp- OFF

Zone valve actuators- valves closed up and downstairs

 

downstairs kitchen turned up to 25 on stat- heating came on, valve opened labelled ‘UF down’

no change to the above controller display

Kitchen stat turned back down and heating went off

 

upstairs bedroom turned up to 25 on stat- heating came on, valve opened labelled ‘UF up’

no change to the above controller display.

hope this makes sense! 

I have been monitoring the DHW temp since I turned the green pump down to 1. Unfortunately it doesn’t seem to have made any difference and the tank still dropped over night but 9 degrees (without use), and continues to need re-heating 3-4 times per 24 hours (set to re-heat after a temp drop of 10 degrees).

Thank again for your help,

Katie 

 

Even with water pump speed turned down, I suspect that you will continue to lose heat energy from the hot water cylinder until you stop the pump from running.

The tests confirm that both of the zones valves appear to be functioning correctly.

The next step is to check the UFH systems, one of which appears to be located to the right of your hot water cylinder. I would expect each UFH system to have a water pump and mixing valve, but a closeup photo would be useful to confirm.

Once located carry out the above test with the thermostats, and check to see if the relevant UFH water pump starts and stops at each UFH system, and also that warm water is flowing through the orange coloured pipework.

 


   
ReplyQuote
(@curlykatie)
Estimable Member Member
443 kWhs
Joined: 2 years ago
Posts: 77
Topic starter  

@derek-m thank you- I will do this test tomorrow and feedback. I think there is a similar set up upstairs in our wardrobe but will need to clear it out to check!!

In the meantime I have attached a photo of the downstairs system. I assume the pump is the grey and black thing which is vibrating slightly?! 
some of the stats control the wrong rooms- someone is supposed to be coming to sort next week… I assume this won’t effect the test? 


   
ReplyQuote
(@curlykatie)
Estimable Member Member
443 kWhs
Joined: 2 years ago
Posts: 77
Topic starter  
C1C00BD6 CCFA 4171 BD9E C0DB02796A8A
2FBAB232 E2F2 4ADD A1DF 20B523486D11

   
ReplyQuote
(@h2009)
New Member Member
32 kWhs
Joined: 2 years ago
Posts: 2
 

Hello 

I’ve just been reading things over. I can’t comment on the HP side but your HW issues sounds exactly the same issue as I’m having. 300L tank set to 60c. I have a 40Kw boiler that needs to come on for 3 hours a day I order to give us just enough hot water for 2x showers and 1 bath. I’m using roughly 2-3.5 gas units a day (not KWH) to just heat hot water at a flow temp of 62c. 
I do have HW return system but my house is super insulated throughout and there’s very little heat loss as a result in the pipe work. Even without the HW return pump being on the issue still occurs. 

I’ve had loads of plumbers come and find out what the issue could be. So far all have no idea. 
what I have noticed my Grohe taps and Gerbrit WC frames have a hiss when the taps are in any position other than extremes positions - ie 100% hot or cold. The WC frame cold feed would hiss/vibrate until I moved the tap to an extreme position. However this is intermittently happening. I have a video of the sound if you would like to hear it.

After speaking with Grohe they said you must have an unbalanced system on the hot/cold. However all the plumbers said impossible, we’re mains fed and have a balancing valve. 
Jumping forward, I got a 8th plumber down that looked at the multiport valve and said it’s not actually a fully balanced on all supplies in the house so it’s possible, during certain times there would pressure differential causing issues. The pipework changes is due to be resolved next weekend so hopefully this fixes my issues. 

Cutting forward, this plumber believes my hot water is mixing to the cold through the taps causing a huge heat loss. However what he can’t explain is where this extra water is going, as there isn’t any leaks.

So I’m wondering do you have a similar issue to me somewhere in your system. In theory it doesn’t matter what your heat source is. 

 


   
ReplyQuote
(@curlykatie)
Estimable Member Member
443 kWhs
Joined: 2 years ago
Posts: 77
Topic starter  

@derek-m I’ve done the advised checks and all seems to be working as expected. Photo of the downstairs set up on previous post but here’s upstairs,

katie

7AD2454C 679B 469A 9E77 FCC3677744E5

 


   
ReplyQuote
(@curlykatie)
Estimable Member Member
443 kWhs
Joined: 2 years ago
Posts: 77
Topic starter  

@h2009 sounds similar for sure- and equally costing a small fortune. I’m hoping to get the pump disconnected this week to see if that helps. Keep me posted on your plumber visit!


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

Posted by: @curlykatie

@derek-m I’ve done the advised checks and all seems to be working as expected. Photo of the downstairs set up on previous post but here’s upstairs,

katie

7AD2454C 679B 469A 9E77 FCC3677744E5

 

So do the UFH water pumps switch On and Off when you operate the thermostats?

Are all the orange pipes getting warm? Note any that seem cooler.

 


   
ReplyQuote
(@curlykatie)
Estimable Member Member
443 kWhs
Joined: 2 years ago
Posts: 77
Topic starter  

@derek-m yes- the pumps switch on and off. I felt each pipe getting warm, I think they all felt a similar temperature… We do find that downstairs heats up much quicker than upstairs though! Upstairs rarely hits the temp on the stats- only set to 18…

This post was modified 2 years ago by Curlykatie

   
ReplyQuote
Page 3 / 8
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security