The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve

Flow Regulating Valve

It’s fascinating to watch how low-temperature heating is evolving in the UK. For decades, domestic heating has largely been defined by the simplicity and forgiving nature of fossil fuel boilers. Stick a gas or oil boiler in a home with any radiators and it’ll usually cope, no matter how slapdash the system design might be.

But heat pumps have changed the game. Unlike boilers, heat pumps demand finesse, care and a touch of engineering discipline to deliver their best. They reward good design and punish lazy shortcuts. And one area that’s gaining more attention (but still doesn’t get the headlines it deserves) is radiator balancing.

In traditional boiler systems running at higher flow temperatures (70C+) you can get away with poor balancing. One radiator might boil you out of the living room while the spare bedroom stays stubbornly chilly, but the boiler just keeps pumping out heat, masking the imbalance with brute force.

With heat pumps, it’s different. Because they run at lower flow temperatures (typically 35-50C) you don’t have that huge headroom to paper over design flaws. Every degree counts. If the flow rates through your radiators aren’t right, you’re more likely to find cold spots, inconsistent room temperatures and higher running costs.

A well-balanced system ensures the right amount of heated water reaches every radiator. That means each room warms up as it should, the heat pump operates more efficiently, and you enjoy steady, comfortable warmth without some rooms feeling like saunas while others never get warm enough.

The Balancing Act: Easier Said Than Done

Traditionally, balancing means tweaking each radiator’s lockshield valve to control how much water flows through it. It sounds simple on paper but in reality, it’s a fiddly, time-consuming process that few installers do well, and even fewer homeowners attempt at all.

Ask any heat pump installer what’s involved and you’ll probably get a wry smile. It’s a painstaking cycle of adjusting one radiator, then another, then another, then going back to check the first one because your previous tweak has thrown it out of balance again.

So for years, balancing has been a best practice that’s often neglected or done half-heartedly. But when you’re spending £10,000-£20,000 on a heat pump system that could cost you thousands to run over its lifetime, it really shouldn’t be optional.

Enter the Flow Regulating Valve

This is where a new product comes in that’s turning heads among heating pros: the Flow Regulating Valve, or FRV for short.

At first glance, the FRV is deceptively simple. It replaces your radiator’s standard lockshield valve, but unlike the old-school version, it lets you quickly and precisely set and check the exact flow rate for each radiator.

No more guesswork with screwdrivers and temperature probes. No more vague instructions about “turning it a quarter turn and hoping for the best.” With the FRV, you fit the valve, consult the simple flow rate chart to find the right setting for that radiator, adjust the dial to the correct flow rate, and you’re done.

The clear visual indicator shows you exactly what’s happening inside. Once set, the valve holds the flow steady, ensuring each radiator gets exactly the right share of heat, all the time.

You can still use TRVs (thermostatic radiator valves) at the other end if you want extra room-by-room control which is handy in rooms with big windows or unpredictable heat gains. But the real magic is that the balancing is now built into the system by design, not left to chance.

Perfect for Heat Pumps… and Boilers Too

While the Flow Regulating Valve is a game-changer for low-temperature heat pump systems, it’s just as useful on conventional gas, oil and biomass boilers. After all, any hydronic system benefits from better flow balance, whether you’re running weather compensation, open loops or good old on/off boiler control.

The FRV is also a retrofit dream. Just swap out the old lockshield valve for the FRV, set it up and forget about it. No massive system overhaul, no smart gadgets that break or need an app… just simple, robust engineering that does what it says on the tin.

A Little Bonus for RHH Readers

We’re excited to share that the team at Firepower, who distribute and sell the Flow Regulating Valve, have given us an exclusive 10% discount code for our community.

If you’d like to get the discount, just email us (editor@renewableheatinghub.co.uk) and we’ll send the code straight to your inbox.

Balancing radiators might not be glamorous, but it’s one of the most impactful things you can do to make your heating system, especially a heat pump, perform to its full potential. On the surface of it, the Flow Regulating Valve makes that job easier, quicker and more accurate than ever before.

If you’re serious about comfort and keeping running costs down, this is one piece of kit worth looking into.

Related posts

How Government Grants May Be Inflating Heat Pump Installation Prices and What Could Happen If They’re Scrapped

Mars

Volumisers in Heat Pump Systems: Does Placement Matter?

Mars

6 Red Flags to Avoid When Considering a Heat Pump Installation

Simon Murray
Subscribe
Notify of
guest
21 Comments
Oldest
Newest Most Voted
Inline Feedbacks
View all comments
JamesPa

Great video again this week @Mars, I am very interested in the FRV valves referenced in the part about balancing. I had a disastrous attempt at balancing my rads last time around and basically gave up and just opened them all up again. I got the rads to all be about DT5 but the next day after I headed of to work the system went crazy and sounded like it was going to explode, leading to a severe bollocking from the missus who had to deal with it. Note self never ever tinker with the system unless you are around to fix it lol!

@Grantmethestrength

 

There are a couple of subtle points to make here which might explain the noise you experienced:

1: did you ensure that, when you balanced them, the LSV on at least one radiator (normally the one furthest from the heat source, but maybe also a couple of adjacent ones) was fully open (and yet still in balance).  

2: Balancing for DT5 is a mistake unless the design is perfect (which it almost certainly isnt) and the OAT is the design OAT and has been for at least 24 hrs (which is rarely if ever the case). 

Getting wither of these wrong will lead, in most cases, to turning the LSVs down too far and thus throttling the flow unnecessarily, increasing noise and wear on the water pump and increasing running costs.  

The objective is just to achieve ‘balance’ ie either the same DT (not necessarily 5, in many cases it will be less) across each radiator or the same room temperature (or the desired difference in room temperature) in each room, whilst keeping the valves as open as possible so as not to restrict flow more than is necessary.  Hence why you should start with and maintain at least one LSV fully open and not worry about adjusting the LSVs for DT5 (if, for some reason, you want to adjust for DT5 then its the water pump speed that should be changed).

Grantmethestrength

@JamesPa You are right I must have cranked them down too much. I am struggling to get my noodle around what balancing is I thought it was getting the DT the same on each radiator so I am obvs not grasping the fundamentals of it. But thanks for the explanation. I think I am falling into most of the categories you mention incorrect design, not at design OAT etc. As was said in the video balancing a radiator is a simple task in principle 😝

JamesPa

I am struggling to get my noodle around what balancing is I thought it was getting the DT the same on each radiator

My understanding (someone may correct me) it that it is this, but not a specific DT for the reasons outlined above.  Alternatively its getting the same flow rate. In a system where the radiators are precisely sized to match the load, they will occur at the same point.  In both cases, however, the aim is to do so without restricting flow more than you absolutely need to.

A refinement is is getting the same room temperature (or the desired differences in room temperature).  This ‘takes out’ the inevitable variations in radiator sizing from the ideal.  Heat Geek says something about this in their videos on balancing.

In reality any of these may be good enough (because rooms share heat) unless you have gross imbalances in radiator sizing in which case the last is what you really want, but its much more time consuming.  

If you are going to balance for same DT then it needs to be large enough to be measurable.  Some heat pumps turn their water pump speed up or down to maintain eg DT5 at the heat pump, but many don’t and so DT is going to be <5 most of the time.  If yours doesn’t then, at this time of year, the DT wont be large enough to measure unless you whack the flow temperature up well above the target so the house overheats, and then allow it to stabilise for a while.   Similar considerations apply to balancing for same room temp.    It may be that professional installers (which I am not) have some other tricks to deal with this.

FWIW I found balancing my house, at least to a ‘comfort’ point, quite easy.  After doing a very rough balance for DT (really no more than the ‘feel’ test plumbers reputedly use – effectively making sure all rads are getting a reasonable flow and at least one is fully open), I simply turned down a couple where the room overheated, and turned up a couple where the room underheated.  Fortunately it was cold outside so it was relatively easy.  Perhaps I could do better with a more precise/scientific balancing, but its comfortable, I get a COP I’m happy with and I have other things to do in life!

Grantmethestrength



I am struggling to get my noodle around what balancing is I thought it was getting the DT the same on each radiator

I get a COP I’m happy with and I have other things to do in life!

I may need to adopt this technique lol!
 

Fred Gray

When adjusting the FRV you need to use the area of the radiator. Does the radiator type (K1, K2, K3 etc) need to be taken into account?

JamesPa

When adjusting the FRV you need to use the area of the radiator. Does the radiator type (K1, K2, K3 etc) need to be taken into account?

Good question.  Based on physics I think the short answer is yes.

I have actually been thinking about this area since I posted above with the comment that balancing for DT and balancing for equal flow rate will achieve the same result. 

I now think I was wrong and your question has cemented my belief that Im wrong.  If you balance flow rate per unit output it will result in equal deltaT.  The output for any particular rad type is proportional to area, but the proportionality constant is different depending on the radiator type (K1, K2, K3, K+)

I just looked at the FRV data sheet and it says to multiply by the area, but doesn’t specify the radiator type.  Something isn’t right! 

@Mars I think you are in contact with these guys, maybe you know?

 

Grantmethestrength

@JamesPa that is quite important. It would be good if they had a video tutorial on how to set them up, with some examples of the maths for us dummies! I wonder if you would put one on the rad that is supposed to be fully open?

JamesPa

I wonder if you would put one on the rad that is supposed to be fully open?

With their balancing process Im pretty sure all rads could end up being restricted at least a bit.  Its unlikely however that the restriction would be so great as to cause a problem.  Personally I would probably adopt a slightly different process but the difference would be marginal.

Doing some maths on their figures 1.3l/min/sqm at DT5 is 1.3*5*4200/60 = 455W/sq m (assuming water not glycol). 

At room DeltaT of 20 thats equivalent to (20/50)^1.3 =1496W/sqm at room DeltaT of 50 (which is how rads are normally quoted). 

Stelrad Type 11 500mm high rads are quoted as 1548W/sq m at room DeltaT50, so it seems that the figures in the FRV leaflet are for Type 11.   

The Stelrad figures for other variants, and the ratio relative to type 11, are

Type – W/sqm – ratio relative to Type 11

11-1548-1

21-2106-1.4

22-2666-1.7

33-3786-2.44

Assuming my logic is right that enables the calculation to be done for other rad types. 

So, for example, a 0.5m*1.2m (0.6sqm) type 22 needs a flow rate of 0.6*1.3 * 1.7 =1.33l/min to get DT5 at 20C room to rad deltaT.

 

 

JamesPa

Watched the latest homeowners qa and they mentioned some easy to balance lock shield valves. It’s something I need to look at in the winter as not had the HP that long. Or if they are not an option is there a reasonably accurate, or one I can calibrate, temp meter I can use to balance them.

If you don’t need your trvs (and you shouldnt)  you can repurpose them as lsvs by removing the heads and replacing with  decorators caps.  Trvs generally have better ‘valve authority’ than old lsvs, ie the response to turning them occurs over a wider range of positions.  Old lsvs (and many new ones) are basically shut off valves so difficult to set precisely.  There is a heat geek video on valve authority. 

This doesn’t have the easy set, calibrated, advantage of the frvs but may be easier than using your lsvs and avoids replumbing.

In addition its worth noting that some trv bodies have an adjustable flow rate restriction built in, eg Drayton ones, which you need a tool to set.  Again thus doesn’t have the calibrated self maintaining functionality of the frvs, but may be useful in some cases.

That said I managed to balance my rads on the lsvs even though the adjustment on some of them was only in the last half turn.

 

Toodles

@JamesPa I found the same about the last half turn being the only effective part of the mechanism. Some chap called Toodles wrote an article for RHH and he found the same too!😉 Regards, Toodles.

Grantmethestrength


@JamesPa I found the same about the last half turn being the only effective part of the mechanism. Some chap called Toodles wrote an article for RHH and he found the same too!😉 Regards, Toodles.

It is deffo a me thing as it was your guide I was trying to follow lol! 2/10 go see the headmaster and try harder!!!!
 

Toodles

@Grantmethestrength Sorry! I must try harder then! Toodles.

Grantmethestrength


@Grantmethestrength Sorry! I must try harder then! Toodles.
I think it is very much me that is sitting outside the headmasters office for being unable to follow instructions lol!
 

JamesPa

Some chap called Toodles wrote an article for RHH and he found the same too!

I know.

 

Sadly many dont read articles, I keep referring people to the ABC guide that cathoderay wrote!  I must add yours to my list of referrals.

Toodles

@JamesPa Thank you!😊 Toodles.

Sune

@JamesPa That is a great point about waste – and I think you’re right. I think perhaps we need to think of carrying alternative caps as an extra on the shelf instead of in the box. We have a loflow insert now for low output rads, but that then means wasting the standard insert – so we’re having them assembled as a loflow, pre-assembled set to combat that – which is dealing with the same issue you mention, so i should have been thinking along those lines already, so my thanks for telling me! @Mars good question – and yes they are needed as they provide physical protection for the gauge once set. They’re pretty robust, but not enough to leave exposed in a boisterous household. In a calm household, inhabitated by people obsessed by heating, then perhaps visibly seeing the flow to each rad would add a point of interest!?

Grantmethestrength

@Sune would these work in a horizontal rather than a vertical orientation, as I have 4 vertical rads that have the valves horizontally?

Grantmethestrength

I would probably have them in white as that would match the rads. 