Moving to single zone
Posted by: @profzarkovI have two wireless receivers. I was going to connect the signal lines together, so when the Hive stat calls for heat it signals both. I'd then switch off the other stat.
Sorry but there is no way I can tell from the photo what they are doing/controlling and there are several possibilities. Nor can I tell whether connecting the signal lines together will work or where in the house the zones correspond to (and thus what you might want to do with them - basically why are there two zones anyway?)
However what you almost certainly want is both valves permanently open, and the hive (set a couple of degrees above the target temp except when you want a setback) simply telling the heat pump whether to switch on or off, via the relevant signal input to the heat pump controller. Indirectly telling the heat pump to switch off by closing off the water circulation route completely (which is what will happen if both valves are closed under instruction from the Hive) is NOT a good idea, heat pumps do things like run anti-seize programs during summer or if switched off for a long time, and anti-freeze programs. Some also 'sniff' the flow temperature when off by running the water pump for a minute or so, and during defrost you need the pump to be able to call on the water in the system, even if the house is over-temp.
The call for heat contact on the Samsung is probably zero volts, not 230V, depending on the what hive does (which I don't know) you may need a relay. Alternatively you may find it simpler to use an alternative way to do whatever you actually do with the Hive, basically they aren't particularly designed for use with heat pumps and heat pump controllers are designed to be the principal, or indeed only, system control so there is possibly a bit of over-engineering here. Samsung is, however, one of the less feature rich controllers so it is possible that there is in fact something that the Hive can do which the Samsung controller cant.
I hope that helps, feel free to ask for further clarification.
I’m sure I’ve read somewhere that Samsung pumps don’t like going down to temperatures in the 20s so the 32C at the upper outside temperature end might be the limit. Other Samsung owners will able to advise.
I can’t recall if you said which rooms the Neostat controls. Would it matter if those rooms were not set back and it was permanently set to 19C.
You do need a way for the system to permanently keep a minimum of water volume and having any external thermostats, never mind two you’ve been given, might be unwise. Do you have a buffer at all? Your manual will give the minimum volume assuming you’ve been given one.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (new & still learning it)
@jamespa Hi, to be honest with the Eco4 install we had to take what they have us. Kind of all or nothing. I was disappointed that they didn't honour their promise of installing a hybrid inverter and then letting us buy a battery - friends in the village had a different installer and they were happy to do this. I guess they don't want to be caught out and refused the grant money.
They installed two rubbish neomitis thermostats. I didn't want two zones. We're in a small bungalow! The main zone is the whole house, zone 2 is just the two bedrooms!
I could manually latch the two zone valves open🤔.
Posted by: @profzarkovI could manually latch the two zone valves open
Thats not at all silly (actually its very sensible), so long as you disconnect the feed to ensure you dont risk burning out the motor.
What do you actually use the Hive for and would this defeat it?
Posted by: @judithI’m sure I’ve read somewhere that Samsung pumps don’t like going down to temperatures in the 20s so the 32C at the upper outside temperature end might be the limit. Other Samsung owners will able to advise.
I'm new to heat pumps and have only been experimenting with mine for a few weeks but I think that how efficient my Gen 6 Samsung is with low temperatures is linked to the flow rate. I don't have a PWM pump, mine has 3 speeds, and when I reduced it to speed 2 I have been able to reduce the temperature to the high 20's without the efficiency dropping off significantly, on the 3rd speed it was dropping off in the mid to low 30's. I haven't experimented with the 1st speed. With a PWM pump I have read that it isn't affected and I think the Gen 7 has the pump built in to the outdoor unit, which I would assume is fully controlled by the samsung controller.
- 21 Forums
- 1,818 Topics
- 39.1 K Posts
- 81 Online
- 2,131 Members
Join Us!
Latest Posts
-
-
RE: Is it crucial to get flow temperatures with heat pumps right?
@toodles By the way, have you balanced the system with ...
By Alfapat , 15 minutes ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I thought that they brought in CfD to stop this merry g...
By Abernyte , 48 minutes ago
-
I live in Yorkshire so am in the northern area for mete...
By MikeF , 1 hour ago
-
RE: Running my new Nibe ASHP efficiently
thank you everyone for your insightful replies @toodl...
By jamieheatpumpnew , 2 hours ago
-
RE: ASHP and how it should run and potential kw consumption?
Damn really wasn't expecting those figures, but agree t...
By jeegnesh , 2 hours ago
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
Understood. You suggest (I think) that your data sho...
By JamesPa , 3 hours ago
-
Maybe best not to sound too clever, it might upset him....
By JamesPa , 3 hours ago
-
RE: Best temperature wave form for best economy and efficiency .
Hi @ivanhoew , no worries. This is such a well-informin...
By s_gatorator , 4 hours ago
-
RE: ASHP for small garage and workshop
@transparent I spent a King’s ransom on grid chargeable...
By Toodles , 4 hours ago
-
RE: How do the settings on my Gen 5 Samsung ASHP sound?
@jamespa Some even sit under the DHW tank rather as tho...
By Toodles , 4 hours ago
-
RE: Solar thermal with combi boiler
Can you explain a bit more about the context in which y...
By Transparent , 10 hours ago
-
RE: Can you work an ASHP too hard?
As someone with an over-sized HP and the lower level of...
By HarriUp , 19 hours ago
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
Quite possibly. As I mentioned above the 'ideal' produ...
By JamesPa , 21 hours ago
-
RE: Say hello and introduce yourself
Thank you Transparent ...much appreciated 😊 ...
By ivanhoew , 23 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
Greg Jackson in the Times again just yesterday promotin...
By IanMK13 , 1 day ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Yeah we have a 40l buffer too. Problem is the App doesn...
By MikeH , 1 day ago
-
RE: Mitsubishi Ecodan 8.5kW Monobloc (FTC5) Defrost Mode
@gary no set backs. Yes see others in various forums ha...
By AlsoCold123456 , 1 day ago
-
Looking for homeowner to join our podcast as a guest
We’re looking for a homeowner to join us on the Homeown...
By Mars , 1 day ago
Latest Topics
-
By MikeF 1 hour ago
-
Running my new Nibe ASHP efficiently
By jamieheatpumpnew 8 hours ago
-
How do the settings on my Gen 5 Samsung ASHP sound?
By cyrusir 10 hours ago
-
Best temperature wave form for best economy and efficiency .
By ivanhoew 23 hours ago
-
By Potatoman 1 day ago
-
By DavidAlgarve 2 days ago
-
ASHP for small garage and workshop
By BobTSkutter 2 days ago
-
By ChandyKris 3 days ago
-
Nibe heatpump comms error when freezing
By Toody 4 days ago