Column radiators for heat pump
I have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Posted by: @encI have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Radiator manufacturers generally provide either outputs at lower temperatures, an equation, or the 'exponent'. For radiators other than fan radiators (and possibly radiators with a very high 'aspect ratio') the equation is invariably "output is proportional to deltaT^n" where deltaT is the average temp difference radiator to room and ^n means raised to the power of n (n is 'the exponent'). Furthermore n is almost invariably 1.3 or very close, so output is proportional to deltaT^1.3.
Thus (for example) a radiator that outputs 1kW at 50C deltaT will output (25/50)^1.3x1kW at 25C deltaT = 406W.
I don't know of any reason why fancy column radiators should perform particularly badly or particularly well with a heat pump, however others might,
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a couple of tall (1.8m) column radiators im my kitchen diner. I presently have a boiler and have assumed the usual downrating for ASHPs. One problem I have experienced with my boiler setup is that it takes an age for the radiator to heat up. Flow and return are both at the bottom of the radiator and the installer did not fit the baffle - available seperately - to divert the flow up the first column to the top of the radiator. Conequently, the flow much refers to go straight across the bottom of the radiator from inlet to outlet. I don't know what would happen with the lower flow temperatures and higher flow rate with an ASHP in this situation, but I would definitely recommend ensuring flow across diagonal corners one way or another.
We have an 1800x500x100 mm. radiator in our dining area (insufficient wall space for conventional shape. This one works with our heat pump and provides a very even radiant heat over the whole panel space and I assume the convection is equally good - but it is well above our heads! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 22 Forums
- 2,005 Topics
- 43.8 K Posts
- 10 Online
- 3,166 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Is my Samsung heat pump working too well?
You have had good advice so far, but I am just wonderin...
By guthrie , 3 hours ago
-
Yes there is, provided the buffer is tall and well desi...
By JamesPa , 3 hours ago
-
RE: Grant Aerona fine tuning advice needed
I have a Aerona3 13kW and my current settings are max F...
By Grantmethestrength , 4 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Our March generation was 133% of our PVGIS prediction a...
By Old_Scientist , 6 hours ago
-
RE: Setback savings - fact or fiction?
I'm not a statistician, but I have had to use statistic...
By cathodeRay , 6 hours ago
-
@jamespa thanks. I will take some time to make a head-t...
By Eliuccio , 10 hours ago
-
RE: Are Homeowners Being Silenced Over Faulty Heat Pumps?
Spot on. Last month, a homeowner booked a consultation ...
By Mars , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@matthew_w It's a complex area and every case is diff...
By JamesPa , 1 day ago
-
RE: Multiple simultaneous connections to Samsung R290 heat pump via Modbus
Thanks for the various replies. I've tried to summari...
By Angus , 1 day ago
-
RE: Help me keep the faith with my installation
@adamk Yes, it's a good way and an alternative to (o...
By JamesPa , 1 day ago
-
RE: Frequent power outages in the Southeast – A sign of things to come?
That's a useful observation @majordennisbloodnok I'd ...
By Transparent , 2 days ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
Glad to hear that things are moving forward. The photo...
By JamesPa , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@judith Our peak is 5.4 kWp today and so far (16:35) we...
By Toodles , 2 days ago
-
RE: Forum updates, announcements & issues
@transparent I rather think that your LPA might refussi...
By Toodles , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks
Nah, tiz them Cornish coliflour 'eads goin to announce ...
By Broadsman , 2 days ago
-
RE: Should I insulate the flow and return on my rad circuit?
red is 28mm orange is 22mm.
By AdamK , 2 days ago
-
-
RE: New Heat Pump - mixer shower pressure
Just note that this will yield a reduction in pressure ...
By Transparent , 3 days ago
-
RE: Renewable Heating Hub Partners with Heat Geek
@mars as a matter of interest have you got any near Sta...
By JamesPa , 3 days ago
Most Active This Week
# | Name | kWhs |
---|---|---|
1 | Mars | 324 |
2 | JamesPa | 114 |
3 | Majordennisbloodnok | 99 |
4 | Transparent | 79 |
5 | cathodeRay | 66 |
6 | Tim441 | 65 |
7 | Toodles | 60 |
8 | Heatgeek | 53 |
9 | Pooneil | 48 |
10 | Potatoman | 43 |