I have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Posted by: @encI have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Radiator manufacturers generally provide either outputs at lower temperatures, an equation, or the 'exponent'. For radiators other than fan radiators (and possibly radiators with a very high 'aspect ratio') the equation is invariably "output is proportional to deltaT^n" where deltaT is the average temp difference radiator to room and ^n means raised to the power of n (n is 'the exponent'). Furthermore n is almost invariably 1.3 or very close, so output is proportional to deltaT^1.3.
Thus (for example) a radiator that outputs 1kW at 50C deltaT will output (25/50)^1.3x1kW at 25C deltaT = 406W.
I don't know of any reason why fancy column radiators should perform particularly badly or particularly well with a heat pump, however others might,
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a couple of tall (1.8m) column radiators im my kitchen diner. I presently have a boiler and have assumed the usual downrating for ASHPs. One problem I have experienced with my boiler setup is that it takes an age for the radiator to heat up. Flow and return are both at the bottom of the radiator and the installer did not fit the baffle - available seperately - to divert the flow up the first column to the top of the radiator. Conequently, the flow much refers to go straight across the bottom of the radiator from inlet to outlet. I don't know what would happen with the lower flow temperatures and higher flow rate with an ASHP in this situation, but I would definitely recommend ensuring flow across diagonal corners one way or another.
We have an 1800x500x100 mm. radiator in our dining area (insufficient wall space for conventional shape. This one works with our heat pump and provides a very even radiant heat over the whole panel space and I assume the convection is equally good - but it is well above our heads! Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,367 Topics
- 53.7 K Posts
- 114 Online
- 6,042 Members
Join Us!
Worth Watching
Latest Posts
-
-
RE: Who's your electricity provider and what's your tariff?
@majordennisbloodnok This may be a better thread to ...
By Batpred , 7 hours ago
-
RE: Help needed with Grant Aerona 3 issues
Noted. Its a pity you didnt capture the flow rate and ...
By JamesPa , 13 hours ago
-
RE: Best Heat Pump Brand in the UK
Last Call to Vote & Win! Haven't voted for your Hea...
By Mars , 13 hours ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
Interesting question. To be frank, since I have no inte...
By Majordennisbloodnok , 20 hours ago
-
RE: Changing from 4-port buffer to volumizer
@andy1618 see the very sage advice from @editor above. ...
By JamesPa , 1 day ago
-
RE: New Fogstar 15.5kWh upright solution
The video shows the JK balancer, but the connection of ...
By Batpred , 1 day ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
@9jwr9 Hi, yes this is the issue with every (stand alon...
By ASHP-BOBBA , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk FWIW I managed unintentionally to 'coax' mine in...
By JamesPa , 1 day ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
You are in essence right. Adia only works with selecte...
By JamesPa , 1 day ago
-
No, you haven’t missed out, @batpred. This thread’ll st...
By Majordennisbloodnok , 1 day ago
-
RE: Tesla Powerwall – More of a ‘Luxury’ Than an ROI Winner!
Also, though they weren’t prepared to match the price t...
By Toodles , 1 day ago
-
RE: How long will your energy contract last?
My INTELLI-FIX-12M-25-08-29 has less than 12 months to ...
By Batpred , 2 days ago
-
RE: GivEnergy 2025 forthcoming batteries and inverters
Then, perhaps @toodles , you should've made a submissio...
By Transparent , 2 days ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I am wondering if anyone with an EV could find the 7p/k...
By Batpred , 2 days ago
-
Possibly, but it would also reduce DeltaT across the em...
By JamesPa , 2 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@cathoderay It was reminiscent of the BBC Open Universi...
By Toodles , 2 days ago
-
-
@morgan They are unsupervised these days, can’t get the...
By Toodles , 5 days ago