Column radiators for heat pump
I have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Posted by: @encI have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Radiator manufacturers generally provide either outputs at lower temperatures, an equation, or the 'exponent'. For radiators other than fan radiators (and possibly radiators with a very high 'aspect ratio') the equation is invariably "output is proportional to deltaT^n" where deltaT is the average temp difference radiator to room and ^n means raised to the power of n (n is 'the exponent'). Furthermore n is almost invariably 1.3 or very close, so output is proportional to deltaT^1.3.
Thus (for example) a radiator that outputs 1kW at 50C deltaT will output (25/50)^1.3x1kW at 25C deltaT = 406W.
I don't know of any reason why fancy column radiators should perform particularly badly or particularly well with a heat pump, however others might,
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a couple of tall (1.8m) column radiators im my kitchen diner. I presently have a boiler and have assumed the usual downrating for ASHPs. One problem I have experienced with my boiler setup is that it takes an age for the radiator to heat up. Flow and return are both at the bottom of the radiator and the installer did not fit the baffle - available seperately - to divert the flow up the first column to the top of the radiator. Conequently, the flow much refers to go straight across the bottom of the radiator from inlet to outlet. I don't know what would happen with the lower flow temperatures and higher flow rate with an ASHP in this situation, but I would definitely recommend ensuring flow across diagonal corners one way or another.
We have an 1800x500x100 mm. radiator in our dining area (insufficient wall space for conventional shape. This one works with our heat pump and provides a very even radiant heat over the whole panel space and I assume the convection is equally good - but it is well above our heads! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 22 Forums
- 2,008 Topics
- 43.8 K Posts
- 38 Online
- 3,166 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Mitsubishi Ecodan System Pressure Changes - An Issue or Expected ?
@alsocold123456 I would have thought it would last a bi...
By ASHP-BOBBA , 5 hours ago
-
RE: Are Homeowners Being Silenced Over Faulty Heat Pumps?
This is sad to hear and should not happen, to give you ...
By ASHP-BOBBA , 5 hours ago
-
RE: Is my Samsung heat pump working too well?
@pooneil It sounds like the settings are all over the p...
By Heatgeek , 9 hours ago
-
ive had solar PV for just over 10 years and havent cons...
By AdamK , 10 hours ago
-
@editor Thank you for the information,do you have any i...
By Potatoman , 10 hours ago
-
@cathoderay Years ago (40+) I enquired about moving our...
By Toodles , 12 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
I didn't realise that Samsung even had customer support...
By JamesPa , 13 hours ago
-
RE: New Heat Pump - mixer shower pressure
Just a little update, I eventually decided to put a pre...
By Spanners , 17 hours ago
-
RE: Grant Aerona fine tuning advice needed
@grantmethestrength thank you interesting numbers. Did...
By Stopbar , 22 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Our March generation was 133% of our PVGIS prediction a...
By Old_Scientist , 1 day ago
-
RE: Setback savings - fact or fiction?
I'm not a statistician, but I have had to use statistic...
By cathodeRay , 1 day ago
-
@jamespa thanks. I will take some time to make a head-t...
By Eliuccio , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@matthew_w It's a complex area and every case is diff...
By JamesPa , 2 days ago
-
RE: Multiple simultaneous connections to Samsung R290 heat pump via Modbus
Thanks for the various replies. I've tried to summari...
By Angus , 2 days ago
-
RE: Help me keep the faith with my installation
@adamk Yes, it's a good way and an alternative to (o...
By JamesPa , 3 days ago
-
RE: Frequent power outages in the Southeast – A sign of things to come?
That's a useful observation @majordennisbloodnok I'd ...
By Transparent , 3 days ago
-
RE: NIBE F2040 12 kW heat pump and 100 liter buffer tank
Glad to hear that things are moving forward. The photo...
By JamesPa , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@judith Our peak is 5.4 kWp today and so far (16:35) we...
By Toodles , 4 days ago
-
RE: Forum updates, announcements & issues
@transparent I rather think that your LPA might refussi...
By Toodles , 4 days ago
Most Active This Week
# | Name | kWhs |
---|---|---|
1 | Mars | 355 |
2 | JamesPa | 150 |
3 | Pooneil | 113 |
4 | Majordennisbloodnok | 112 |
5 | Toodles | 108 |
6 | bontwoody | 101 |
7 | Heatgeek | 98 |
8 | Transparent | 87 |
9 | cathodeRay | 86 |
10 | Tim441 | 65 |