Column radiators for heat pump
I have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Posted by: @encI have seen a couple of fancy column radiator recommendations kicking about in this forum which work well with a heat pump. Currently our single panel classic convection radiator in the hallway is not large enough to match the heat loss of the hall with the door opening etc.
I really want to go traditional column rather than stelrad K2 or K3... is this a bad idea? Does anyone have a calculator for calculating the BTU at lower temperatures?
Radiator manufacturers generally provide either outputs at lower temperatures, an equation, or the 'exponent'. For radiators other than fan radiators (and possibly radiators with a very high 'aspect ratio') the equation is invariably "output is proportional to deltaT^n" where deltaT is the average temp difference radiator to room and ^n means raised to the power of n (n is 'the exponent'). Furthermore n is almost invariably 1.3 or very close, so output is proportional to deltaT^1.3.
Thus (for example) a radiator that outputs 1kW at 50C deltaT will output (25/50)^1.3x1kW at 25C deltaT = 406W.
I don't know of any reason why fancy column radiators should perform particularly badly or particularly well with a heat pump, however others might,
I have a couple of tall (1.8m) column radiators im my kitchen diner. I presently have a boiler and have assumed the usual downrating for ASHPs. One problem I have experienced with my boiler setup is that it takes an age for the radiator to heat up. Flow and return are both at the bottom of the radiator and the installer did not fit the baffle - available seperately - to divert the flow up the first column to the top of the radiator. Conequently, the flow much refers to go straight across the bottom of the radiator from inlet to outlet. I don't know what would happen with the lower flow temperatures and higher flow rate with an ASHP in this situation, but I would definitely recommend ensuring flow across diagonal corners one way or another.
We have an 1800x500x100 mm. radiator in our dining area (insufficient wall space for conventional shape. This one works with our heat pump and provides a very even radiant heat over the whole panel space and I assume the convection is equally good - but it is well above our heads! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 21 Forums
- 1,765 Topics
- 37.7 K Posts
- 38 Online
- 2,054 Members
Join Us!
Latest Posts
-
Just wondering what delta T folk use with their ASHP? ...
By TheBinMan , 7 hours ago
-
RE: Fitting emitters with output greater than room heat loss.
@jamespa Funny you said you have a Vaillant 7kw. Just t...
By bigvibes , 8 hours ago
-
Difficult positioning of air source heat pump
Hello, We are trying to get an heat pump installe...
By Rikiarn , 9 hours ago
-
RE: Battery...Full house back up
@broadsman - I'm unsure if those suggestions from @sae...
By Transparent , 11 hours ago
-
RE: Non standard houses with non standard owners
@jswhite If you design the system to suit the whole hou...
By ASHP-BOBBA , 12 hours ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Thanks, we're planning on a large normal radiator. Heat...
By RobinBennett , 13 hours ago
-
RE: Does turning down radiators preserve the heat in the water?
In my opinion, the water that doesn’t flow through the ...
By Toodles , 13 hours ago
-
RE: Samsung E911 intermittent issue
@netdonkey ok, So its sounds like the the Wilo is doing...
By ASHP-BOBBA , 18 hours ago
-
RE: Samsung ASHP scheduling help
@morh does that samsung device connect to the HP or the...
By cyrusir , 19 hours ago
-
RE: Samsung heat pump has arrived with damaged fins – do I accept it or send it back?
Damage is cosmetic is appears, but the result of poor h...
By AllyFish , 19 hours ago
-
RE: Smart meter installation – seamless or a potential nightmare?
The incomer cable probably only has a size-rating once ...
By Transparent , 19 hours ago
-
RE: How Many ASHPs Work Correctly From Commissioning Date ( The resolution page)
Oh yes, I see, interesting that one of the 1st posts wa...
By ASHP-BOBBA , 19 hours ago
-
RE: Which system is most efficient...
OK. Im not going to be able to answer the question, bu...
By JamesPa , 21 hours ago
-
Palo Alto / London – Dec. 5, 2024 – More than two dozen...
By Jeff , 23 hours ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@lokisam I am following this with interest as I also ha...
By Odynsfee , 1 day ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@thundermink can you give us an update on your tests?
By Mars , 1 day ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@editor Yes, it's their "Aira Generation 1" 8kW model: ...
By trungdong , 1 day ago
-
RE: Reducing heat pump vibrations through flat roof
@patrickvito Hi Patrick, thanks so much for taking the ...
By sten_super , 2 days ago
-
RE: Noise Issues with our Ecodan 8.5kW WM85VAA air source heat pump
@athlonoc Its unlikely the FTC is controlling a 3rd par...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan Produced energy showing 'INVALID'
Hello! I tried your idea and disabled the cooling funct...
By sorin , 2 days ago
Latest Topics
-
By TheBinMan 7 hours ago
-
Difficult positioning of air source heat pump
By Rikiarn 9 hours ago
-
Does turning down radiators preserve the heat in the water?
By Tufty 16 hours ago
-
Non standard houses with non standard owners
By jswhite 18 hours ago
-
By Jeff 23 hours ago
-
Which system is most efficient...
By bigvibes 2 days ago
-
What should we do with our Aga?
By RobinBennett 2 days ago
-
Reducing heat pump vibrations through flat roof
By sten_super 3 days ago