Spacing for roof fixing bolts ?
What spacing should the fixing bolts be for Solar Panel roof bars ? I've seen 0.6 to 0.8 m apart, but elsewhere I've seen 1.2 to 1.8 m apart.
Proposed panels are 1762 mm x 1134 mm and 20.6 kg. Rafters are 600 mm apart approx.
I think @saenergy will have the definitive answer for this one.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
This is determined by a wind load calculation.
the calculation will tell you the total uplift in Nm. The manufacturer will have a specification for the hook selected, you take the load for the array and divide that by the hook capacity. That tells you how many hooks are required
You then space accordingly.
general rule of thumb:
each and of array should not exceed a hook by more than 150mm
The end hooks on each rail will generally be the closest, in your case 600mm apart
Hooks through the centre of the array will likely be at 1200mm
Your installer should carry out this calculation post survey. Note that structure and location are very important here.
Internationally recognised award winning installer of heat pumps and stuff
Thanks @saenergy - I don't suppose the customer would be shown these calculations.
I should change my name to PV-newbie 😀
It’s not a requirement in the handover pack but it should definitely be available if requested
Internationally recognised award winning installer of heat pumps and stuff
@heat-pump-newbie I don’t see why they shouldn’t show and share these calculations with you, especially if you’re proceeding with the job. You need to be sure that the installers have done background work.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
There is another consideration...
but alas this doesn't feature in the installers' guidance/training by MCS.
This diagram shows a generic roof construction with the lower rail for mounting PV panels in purple:
MCS specify the ways in which the rail support brackets must be fixed, which is usually with two M8 x 80mm stainless steel coach screws (or similar).
Those brackets are screwed to the underlying rafters through the vapour barrier (roofing felt).
In turn, the rafter is fixed to the wall plate.
That's a 50x100mm piece of treated timber, bedded onto a run of mortar above the inner leaf of the cavity wall.
At intervals specified in the Building Regs, straps (in red) are fixed to the wall plate and bolted into the blocks of the inner wall.
Note the blue fixings. This is what holds the roof onto the house and prevents it being lifted off in a gale.
Wall plate straps are plastered over, and few people outside the building trade realise they're there.
It is all too common for wall plate straps to be inadequately fitted.
Indeed I've seen new-build houses where they are completely absent.
The wall-plate is simply held onto the top row of concrete blocks with a 4-inch nail. 😲
Adding a row of solar panels to the roof will significantly increase the wind-lift factor.
In strong winds, the weak point is likely to be how the wall plate is fixed to the wall below it.
If you hear timbers creaking shortly after solar panels have been fitted, I suggest you don't just ignore it !
The adjacent photo shows a wall-plate strap being added to a renovation property.
In this case the original ceiling joists had to be completely removed. The ends above the wall plate had deteriorated.
The new (more substantial) ceiling joists are now held by proper joist brackets, bolted to the wall, and lapped over the top of the wall plate.
Sheradised nails hold the joist bracket to the timber wall plate.
The wall plate strap has been fixed close to the joist bracket to add further strength.
Although not shown in the photo, that wall plate strap is actually 1200mm long and held to the wall blocks using 8 fixing points.
Save energy... recycle electrons!
- 26 Forums
- 2,220 Topics
- 49.2 K Posts
- 102 Online
- 5,880 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
Having joined the Aira owners group on Facebook (for so...
By Pirate Rich , 8 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
Interesting. So if you set blocade it can't know the c...
By JamesPa , 10 hours ago
-
RE: Widespread failure of insulation installation
@jeff Along with a phone-in on BBC Radio Four today, mu...
By Toodles , 10 hours ago
-
RE: What is the Heat Geek Guarantee?
@editor Thanks Mars, it is encouraging that Heat Geek a...
By colinc , 10 hours ago
-
RE: 5 Star Service from Havenwise
Ok…a bit tumbleweed. From our own experience we were ...
By benson , 11 hours ago
-
RE: Renewables & Heat Pumps in the News
Love the thought of it! simplification and sometimes me...
By Batpred , 11 hours ago
-
RE: New Fogstar 15.5kWh upright solution
That's good news for the moment anyway. Can we try to...
By Transparent , 11 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
Hi, I've always found Henri to be super helpful. From ...
By davidnolan22 , 11 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk Will not even get started... The power of the ...
By Batpred , 12 hours ago
-
Sounds like you got it working for monitoring! With wel...
By Batpred , 13 hours ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
Thank you Aadil. We appreciate you taking the time to r...
By Mars , 13 hours ago
-
RE: Say hello and introduce yourself
@chris12 Let us hope that next year will be a bumper so...
By Toodles , 16 hours ago
-
RE: Isolating the system for a planned power cut
@batpred - that Solis installation page is too vague. ...
By Transparent , 16 hours ago
-
RE: Heating Turned Off but Radiators Still Warm
I love Necromancy... but to follow James, heat pumps WI...
By DREI , 17 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
12kW Gen 6 AE120BXYDEG (currently NOT performing well a...
By DREI , 17 hours ago
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
Buffer tanks can best be thought of as part of a 'produ...
By JamesPa , 19 hours ago
-
Very Much Awake – Renewing the Heating Industry One Step at a Time
Like any industry that touches so many lives, and is so...
By Aadil Qureshi , 20 hours ago
-
Ah.... I'd like to make a couple of observations: &nb...
By Transparent , 20 hours ago
-
RE: Battery storage to run Heat Pump.
Hats off to the ones that persist, @Transparent ! ...
By Batpred , 21 hours ago