G99 application experience
Having decided on the PV and battery equipment that I wish to install, and after some prompting from various areas, I decided to submit my own G99 application while still to make a decision on the supplier/installer. As a retired electronics engineer, this shouldn't pose much of a challenge. The equipment I have chosen is by no means unusual and from reading various Internet forums it is clear that there are plenty of similar installations. I submitted my application, emphasised my lack of familiarity with the process and asked the DNO to contact me with any queries. After an appropriate delay, I expected - preferably sooner rather than later - to be advised what export limit would be applied.
Once I had selected my supplier/installer they offered to chase my application. I agreed, perhaps unwisely, on the basis that they should be more familiar with the process. I then sat back to wait for some queries.
Yesterday - more than two months after I submitted my application - the DNO has provided the following information to my installer:
Please see below voltage disturbance found on the study:
LV disturbance on the service existing = 0.36%
+ 5.124kW Photovoltaic = 2.13% - 0.36% = 1.77%
++6.0kW Battery Storage = 4.57% - 0.36% = 4.21%
G99 level of volt rise allowance = 1.7% max
G100 level of volt rise allowance = 2.4% max
Please note: voltage disturbance to other customers on the network can’t surpass 1.5%
Does anyone know what this means? My installer can't explain it to me and there is no narrative to show how these figures have been derived. It's not obvious to me why PV and battery are considered separately, either.
I'd be interested to hear of others' experiences of G99 applications and whether their applications have progressed more smoothly than mine. Also, what export limitations have been applied in your case - particularly in the case of separate PV and battery inverters. G100 export monitoring will surely be at the same point for both, so why not the same limit for each?
Regarding the 'disturbances' mentioned by the DNO, over the past week my grid supply has ranged from 230 - 244 V. Not a great excursion, but larger than 1.5%.
happen to know your are in MK same as me as per one of our other discussions. Western power were also concerned about voltage rise with my system as part of the application. They actually put a voltage logger on my house for a week as a precursor . I didn't see as much details as you did, it all went through my installer so I can't help you with meaning of the numbers. Their measurements proved there was no issue so they gave permission. In the last week, my voltage has varied from 222 (1am, battery and cars charging) to 245.8 (midday on a sunny day but not exporting all going into battery)
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank In the numbers above, there is no common relationship between disturbance and power for battery and PV, for example. Some context would be useful. I quickly scanned the G99 and G100 documents but nothing jumped out at me. Although we don't know what the figures relate to, I'm mildly amused at the accuracy and resolution given my grid voltage logs.
With your 3 Powerwalls (and, presumably, a large PV inverter) could I ask what export limits you have had applied.
- 26 Forums
- 2,129 Topics
- 46.8 K Posts
- 25 Online
- 5,654 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: ASHP heat output monitoring
@carlo I have a 16kw LG Therma V. Installed 2020 so eve...
By Tim441 , 5 minutes ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@morgan They may be good but cannot service the heat pu...
By dgclimatecontrol , 10 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@transparent Don’t know about other manufacturer’s offe...
By Toodles , 16 minutes ago
-
RE: Mitsu Wireless Controller and MelCloud
@davidalgarve If they are 'off' because of a timed s...
By Morgan , 2 hours ago
-
@toodles Of course. I've also used Tim and Kat's Gree...
By Old_Scientist , 1 day ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 2 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 2 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 2 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 3 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 3 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 3 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 3 days ago
-
RE: Who has a V2G EV installation
I agree, but a word of caution. V2X is also sometimes u...
By Majordennisbloodnok , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 4 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 6 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 6 days ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago
-
RE: Why do we need pressurised systems?
A good question @toodles. My old open thermal store and...
By AllyFish , 1 week ago