G99 application experience
Having decided on the PV and battery equipment that I wish to install, and after some prompting from various areas, I decided to submit my own G99 application while still to make a decision on the supplier/installer. As a retired electronics engineer, this shouldn't pose much of a challenge. The equipment I have chosen is by no means unusual and from reading various Internet forums it is clear that there are plenty of similar installations. I submitted my application, emphasised my lack of familiarity with the process and asked the DNO to contact me with any queries. After an appropriate delay, I expected - preferably sooner rather than later - to be advised what export limit would be applied.
Once I had selected my supplier/installer they offered to chase my application. I agreed, perhaps unwisely, on the basis that they should be more familiar with the process. I then sat back to wait for some queries.
Yesterday - more than two months after I submitted my application - the DNO has provided the following information to my installer:
Please see below voltage disturbance found on the study:
LV disturbance on the service existing = 0.36%
+ 5.124kW Photovoltaic = 2.13% - 0.36% = 1.77%
++6.0kW Battery Storage = 4.57% - 0.36% = 4.21%
G99 level of volt rise allowance = 1.7% max
G100 level of volt rise allowance = 2.4% max
Please note: voltage disturbance to other customers on the network can’t surpass 1.5%
Does anyone know what this means? My installer can't explain it to me and there is no narrative to show how these figures have been derived. It's not obvious to me why PV and battery are considered separately, either.
I'd be interested to hear of others' experiences of G99 applications and whether their applications have progressed more smoothly than mine. Also, what export limitations have been applied in your case - particularly in the case of separate PV and battery inverters. G100 export monitoring will surely be at the same point for both, so why not the same limit for each?
Regarding the 'disturbances' mentioned by the DNO, over the past week my grid supply has ranged from 230 - 244 V. Not a great excursion, but larger than 1.5%.
happen to know your are in MK same as me as per one of our other discussions. Western power were also concerned about voltage rise with my system as part of the application. They actually put a voltage logger on my house for a week as a precursor . I didn't see as much details as you did, it all went through my installer so I can't help you with meaning of the numbers. Their measurements proved there was no issue so they gave permission. In the last week, my voltage has varied from 222 (1am, battery and cars charging) to 245.8 (midday on a sunny day but not exporting all going into battery)
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank In the numbers above, there is no common relationship between disturbance and power for battery and PV, for example. Some context would be useful. I quickly scanned the G99 and G100 documents but nothing jumped out at me. Although we don't know what the figures relate to, I'm mildly amused at the accuracy and resolution given my grid voltage logs.
With your 3 Powerwalls (and, presumably, a large PV inverter) could I ask what export limits you have had applied.
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 60 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: What is the best strategy for operating a very oversized heat pump?
It makes sense, although shows a complete lack of thoug...
By JamesPa , 42 seconds ago
-
RE: Setback savings - fact or fiction?
And here in case any one wants it is the code I used in...
By cathodeRay , 4 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
No need for apologies, just cautioning about getting to...
By JamesPa , 21 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 22 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 2 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 4 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 7 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 18 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 21 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 22 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 7 hours ago
-
SolarPV tables / online calculator
By MichelleC 14 hours ago
-
By Toodles 2 days ago