AC vs DC Coupled Batteries (PV + Battery setup)
Just wondering if there is an accepted school of thought as to when it is best to go with AC or DC Coupled Batteries (I.e. is your battery charged from the AC or the DC side of your installation). Or is it just setup / cost driven (i.e. no solar just battery = AC coupled. Solar with microinverters = AC coupled. Otherwise DC coupled)?
As far as I gather (electricity is just magic to me though...) all batteries are DC and an inverter will always be needed as in domestic installations we consume/receive AC power.
I was wondering if there are advantages depending on where the predominant power source will be from (e.g. are you charging from grid in the winter, or always from your solar) whether this would make a difference. But charging from AC at any point will require inverting in and out of battery. So surely it is more efficient to run DC coupled, unless you're on microinverters or don't have solar PV (i.e. just battery).
Or is there a more complicated kit efficiency vs cost analysis angle?
My thinking was the same as yours - keep the battery on the DC side as there's one fewer AC/DC conversion loss.
In my experience, the one-way loss is around 5% and round trip loss of 10%. So you can add 10% to the cost of the DC kit for comparison I suppose. When I bought my system, I wasn't too fussed about the cost and there wasn't really much difference anyway. I just wanted the better, more efficient system, so got the DC version.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
There is an additional consideration if the DNO has to be consulted. An AC battery can discharge to the grid independently of the solar panels which could also be discharging to the grid. The combined export might be more than allowed by the DNO. This is not the case with DC batteries as I understand it and the DNO was happy for me to have DC battery but not AC with my second solar array.
As well as being more efficient, DC batteries have advantages when solar export is being clipped by the inverter, see below:
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody thank you - very much food for thought.
I had just about clocked onto the batteries charging in clipping situations but hadn't stumbled across the early and late tails part of the equation. Do you know if the presence of optimisers in a PV system materially changes this?
My line of thought over the last few days was starting to move towards microinverters and AC coupled battery storage (squaring of that in winter and/or if playing games with the likes of Agile) a good proportion of my battery charging would likely be from grid regardless.
I have a corner of the roof that will be regularly shaded by a tree until lunch / early afternoon in early/late summer and had read horror stories that, while modern solar panels are getting increasingly good at reacting to shading using bypass diodes, that regular shading increases the risk of diode and panel failure. In some cases manufacturers determining that known shading issues counts as an installation issue, therefore no warranty support, unless otherwise protected by microinverter/optimiser.
No one looks to be questioning the reliability of the Enphase microinverters. However, the same cannot be said for most of the optimiser manufacturers out there. Albeit the system I am otherwise considering is Huawei based and failure rates seem pretty low on their optimisers.
I do have concerns that microinverters would introduce an element of clipping (that an AC coupled battery obviously can't use) and (certainly US) installers seem to say that they size to ensure good generation at low light conditions (so I would worry that by upping the top end limit e.g. using IQ8H, I might be giving up some low end production - but I've struggled to find data I can interpret on this).
Another driver for this train of thought was microinverter lifespan closely matches panel lifespan and the AC battery choice is completely separate. The worrier in me has concerns that (on a DC coupled, hybrid inverter, setup) when the likes of the battery, BMS, or the string inverter requires replacement that you could end up stuck in a loop of potentially struggling to match parts into your existing ecosystem, or missing out on being able to make use of the latest innovations, or even having to commit to replacement of a whole suite of components once the first of the bundle fails.
Is there a general consensus that as long as sticking to well known/adopted brands that compatible kit will still be available 10-15 years down the line?
Also still looking for an answer to the question what happens when an optimiser fails? (assuming like Tigo or Huawei that the optimiser in question is one that doesn't need to be on all panels of an array) would this generally just be a loss in optimiser function rather than a complete loss of generation from the associated panel?
Happily I do keep swinging back to a position that the Huawei setup I've been quoted has been sensibly pieced together.
Posted by: @bontwoodyThere is an additional consideration if the DNO has to be consulted. An AC battery can discharge to the grid independently of the solar panels which could also be discharging to the grid. The combined export might be more than allowed by the DNO. This is not the case with DC batteries as I understand it and the DNO was happy for me to have DC battery but not AC with my second solar array.
As well as being more efficient, DC batteries have advantages when solar export is being clipped by the inverter, see below:
Please don't talk about AC Batteries - there is no such thing.
The article included concerns a grid size solar PV and Battery Storage system, in a domestic system you would probably be talking about a few watts of unharvested solar output, which is of little concern. Experience from my own 4kWp solar PV system would indicate that actual generation starts at only a few watts.
Of much greater concern is the need to ensure that there is minimum loss of generation due to panel shading or full output clipping.
@derek-m apologises I was in a rush and abbreviating. I will insert 'coupled' into the relevent paces in my post 🙂 Update seems I cant actual edit the offending post now
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @declan90@bontwoody thank you - very much food for thought.
I had just about clocked onto the batteries charging in clipping situations but hadn't stumbled across the early and late tails part of the equation. Do you know if the presence of optimisers in a PV system materially changes this?
My line of thought over the last few days was starting to move towards microinverters and AC coupled battery storage (squaring of that in winter and/or if playing games with the likes of Agile) a good proportion of my battery charging would likely be from grid regardless.
I have a corner of the roof that will be regularly shaded by a tree until lunch / early afternoon in early/late summer and had read horror stories that, while modern solar panels are getting increasingly good at reacting to shading using bypass diodes, that regular shading increases the risk of diode and panel failure. In some cases manufacturers determining that known shading issues counts as an installation issue, therefore no warranty support, unless otherwise protected by microinverter/optimiser.
No one looks to be questioning the reliability of the Enphase microinverters. However, the same cannot be said for most of the optimiser manufacturers out there. Albeit the system I am otherwise considering is Huawei based and failure rates seem pretty low on their optimisers.
I do have concerns that microinverters would introduce an element of clipping (that an AC coupled battery obviously can't use) and (certainly US) installers seem to say that they size to ensure good generation at low light conditions (so I would worry that by upping the top end limit e.g. using IQ8H, I might be giving up some low end production - but I've struggled to find data I can interpret on this).
Another driver for this train of thought was microinverter lifespan closely matches panel lifespan and the AC battery choice is completely separate. The worrier in me has concerns that (on a DC coupled, hybrid inverter, setup) when the likes of the battery, BMS, or the string inverter requires replacement that you could end up stuck in a loop of potentially struggling to match parts into your existing ecosystem, or missing out on being able to make use of the latest innovations, or even having to commit to replacement of a whole suite of components once the first of the bundle fails.
Is there a general consensus that as long as sticking to well known/adopted brands that compatible kit will still be available 10-15 years down the line?
Also still looking for an answer to the question what happens when an optimiser fails? (assuming like Tigo or Huawei that the optimiser in question is one that doesn't need to be on all panels of an array) would this generally just be a loss in optimiser function rather than a complete loss of generation from the associated panel?
Happily I do keep swinging back to a position that the Huawei setup I've been quoted has been sensibly pieced together.
Sorry Declan, those sorts of issues are beyond my level of expertise. I would hope that companies like Solaredge and Huawei would maintaince parts for 15 year old installations, but who knows!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I can also see the valid point that the DNO could understandably worry about independent discharge to grid.
Easy to accidentally start thinking the kW numbers we're talking about as 'small', i.e. comparable to a domestic EV charger or 'its a domestic array and a battery in my garage after all' but when 3.68 kWh is 16A I can see that a 6-7 kW array plus a battery with reasonable discharge rate soon adds up!
80A (my incoming fuse rating) is just over 18kW.
Would be quite conceivable to be asking to run 50A back to grid in an AC coupled scenario.
My gut says ask for too much and you risk getting limited back further than if you'd asked for a more reasonable amount in the first place ...
@declan90 Too true, balancing the grid must be a tricky job. My experience was that the DNO wasnt overly keen on getting into a conversation with me, although I did get an answer. The solar installer contacted him and agreed what was acceptable, which to be fair is working well. Im trying to get my tariff switched now so I can charge my battery at cheap times and export to the grid.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@derek-m apologises I was in a rush and abbreviating. I will insert 'coupled' into the relevent paces in my post 🙂 Update seems I cant actual edit the offending post now
Don't worry, I obviously knew what you meant, but I still think it is important that the correct terminology is used so that there is little room for confusion.
- 24 Forums
- 1,422 Topics
- 29.9 K Posts
- 25 Online
- 1,207 Members
Join Us!
Latest Posts
-
RE: Bivalent (or even trivalent!) system design options for a new GSHP installation
Wow! Huge amount of info. Thanks for taking the time. ...
By Algienon , 4 hours ago
-
It’s a bit nuts. May 4th today, and our central heating...
By Mars , 5 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
@cathoderay Are you dissing the Shipping Forecast ? It ...
By Jancold , 6 hours ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
Thanks for sharing Rachel, and it's commendable that yo...
By Mars , 17 hours ago
-
RE: Issues with Vaillant connectivity via the MyCONNECT gateway
@drew-pa I don't know about hard work! It is pretty cl...
By dr_dongle , 17 hours ago
-
RE: Are Solar Diverters Necessary for Homes with ASHPs and Solar PV?
@editor No, I made one 😀 Loft insulation all...
By Andris , 1 day ago
-
RE: Observations on my Ecodan's estimates of energy consumed and delivered
@hestia I haven't touched this setting. As I can't dete...
By glpinxit , 1 day ago
-
@hughf Thanks for that. Ah so they are talking about ...
By IRMartini , 2 days ago
-
RE: Ecodan software update. Real or scam?
@abernyte, hmm, must have been a major disruption if 40...
By Mars , 2 days ago
-
RE: Installing your own ASHP - DIY
I’m in the DIY camp, completed the install last Septemb...
By HughF , 2 days ago
-
Riello / Midea - modbus set flow temp
Hi, I’ve got a Riello NXHM 8kW HP with emonHP, all wo...
By stuartornum , 2 days ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
That could be the case, depending on where the triple r...
By AllyFish , 3 days ago
-
RE: Say hello and introduce yourself
@irmartini Oh! That’s a great shame.😳 Toodles.
By Toodles , 3 days ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@david999 On the subject of isolation after the battery...
By HughF , 3 days ago
-
RE: New Fogstar 15.5kWh upright solution
@robl I've added the screens. Li-Bms screen is accur...
By GGW , 3 days ago
-
RE: SCOP and seasonal variations
I’ve had a long chat with Aaron from Homely Technical S...
By Toodles , 3 days ago
-
RE: Gas Combi to ASHP - Making sense of survey results and proposal.
Many thanks to everyone who has helped with advice and ...
By IRMartini , 4 days ago
-
RE: What is Wrong with our Heat Pump Installation?
With BESS the ASHP is best. Charge battery for free fro...
By AllyFish , 4 days ago
-
@hubb84 Try looking at powerflushassociation.com. They ...
By Toodles , 4 days ago
-
Central heating inhibitor with ASHPs
Have you seen the Heat Geek article and video?
By ChickenBig , 5 days ago
Latest Topics
-
By IRMartini 2 days ago
-
Riello / Midea - modbus set flow temp
By stuartornum 2 days ago
-
Ecodan software update. Real or scam?
By Morgan 3 days ago
-
Noise problems with newly installed Samsung 8kW ASHP
By Lokisam 4 days ago
-
Central heating inhibitor with ASHPs
By IRMartini 5 days ago
-
Advice on potential HW Cylinder size
By JWilliams89 5 days ago
-
By Graeme 7 days ago