AC vs DC Coupled Batteries (PV + Battery setup)
Just wondering if there is an accepted school of thought as to when it is best to go with AC or DC Coupled Batteries (I.e. is your battery charged from the AC or the DC side of your installation). Or is it just setup / cost driven (i.e. no solar just battery = AC coupled. Solar with microinverters = AC coupled. Otherwise DC coupled)?
As far as I gather (electricity is just magic to me though...) all batteries are DC and an inverter will always be needed as in domestic installations we consume/receive AC power.
I was wondering if there are advantages depending on where the predominant power source will be from (e.g. are you charging from grid in the winter, or always from your solar) whether this would make a difference. But charging from AC at any point will require inverting in and out of battery. So surely it is more efficient to run DC coupled, unless you're on microinverters or don't have solar PV (i.e. just battery).
Or is there a more complicated kit efficiency vs cost analysis angle?
My thinking was the same as yours - keep the battery on the DC side as there's one fewer AC/DC conversion loss.
In my experience, the one-way loss is around 5% and round trip loss of 10%. So you can add 10% to the cost of the DC kit for comparison I suppose. When I bought my system, I wasn't too fussed about the cost and there wasn't really much difference anyway. I just wanted the better, more efficient system, so got the DC version.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
There is an additional consideration if the DNO has to be consulted. An AC battery can discharge to the grid independently of the solar panels which could also be discharging to the grid. The combined export might be more than allowed by the DNO. This is not the case with DC batteries as I understand it and the DNO was happy for me to have DC battery but not AC with my second solar array.
As well as being more efficient, DC batteries have advantages when solar export is being clipped by the inverter, see below:
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody thank you - very much food for thought.
I had just about clocked onto the batteries charging in clipping situations but hadn't stumbled across the early and late tails part of the equation. Do you know if the presence of optimisers in a PV system materially changes this?
My line of thought over the last few days was starting to move towards microinverters and AC coupled battery storage (squaring of that in winter and/or if playing games with the likes of Agile) a good proportion of my battery charging would likely be from grid regardless.
I have a corner of the roof that will be regularly shaded by a tree until lunch / early afternoon in early/late summer and had read horror stories that, while modern solar panels are getting increasingly good at reacting to shading using bypass diodes, that regular shading increases the risk of diode and panel failure. In some cases manufacturers determining that known shading issues counts as an installation issue, therefore no warranty support, unless otherwise protected by microinverter/optimiser.
No one looks to be questioning the reliability of the Enphase microinverters. However, the same cannot be said for most of the optimiser manufacturers out there. Albeit the system I am otherwise considering is Huawei based and failure rates seem pretty low on their optimisers.
I do have concerns that microinverters would introduce an element of clipping (that an AC coupled battery obviously can't use) and (certainly US) installers seem to say that they size to ensure good generation at low light conditions (so I would worry that by upping the top end limit e.g. using IQ8H, I might be giving up some low end production - but I've struggled to find data I can interpret on this).
Another driver for this train of thought was microinverter lifespan closely matches panel lifespan and the AC battery choice is completely separate. The worrier in me has concerns that (on a DC coupled, hybrid inverter, setup) when the likes of the battery, BMS, or the string inverter requires replacement that you could end up stuck in a loop of potentially struggling to match parts into your existing ecosystem, or missing out on being able to make use of the latest innovations, or even having to commit to replacement of a whole suite of components once the first of the bundle fails.
Is there a general consensus that as long as sticking to well known/adopted brands that compatible kit will still be available 10-15 years down the line?
Also still looking for an answer to the question what happens when an optimiser fails? (assuming like Tigo or Huawei that the optimiser in question is one that doesn't need to be on all panels of an array) would this generally just be a loss in optimiser function rather than a complete loss of generation from the associated panel?
Happily I do keep swinging back to a position that the Huawei setup I've been quoted has been sensibly pieced together.
Posted by: @bontwoodyThere is an additional consideration if the DNO has to be consulted. An AC battery can discharge to the grid independently of the solar panels which could also be discharging to the grid. The combined export might be more than allowed by the DNO. This is not the case with DC batteries as I understand it and the DNO was happy for me to have DC battery but not AC with my second solar array.
As well as being more efficient, DC batteries have advantages when solar export is being clipped by the inverter, see below:
Please don't talk about AC Batteries - there is no such thing.
The article included concerns a grid size solar PV and Battery Storage system, in a domestic system you would probably be talking about a few watts of unharvested solar output, which is of little concern. Experience from my own 4kWp solar PV system would indicate that actual generation starts at only a few watts.
Of much greater concern is the need to ensure that there is minimum loss of generation due to panel shading or full output clipping.
@derek-m apologises I was in a rush and abbreviating. I will insert 'coupled' into the relevent paces in my post 🙂 Update seems I cant actual edit the offending post now
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @declan90@bontwoody thank you - very much food for thought.
I had just about clocked onto the batteries charging in clipping situations but hadn't stumbled across the early and late tails part of the equation. Do you know if the presence of optimisers in a PV system materially changes this?
My line of thought over the last few days was starting to move towards microinverters and AC coupled battery storage (squaring of that in winter and/or if playing games with the likes of Agile) a good proportion of my battery charging would likely be from grid regardless.
I have a corner of the roof that will be regularly shaded by a tree until lunch / early afternoon in early/late summer and had read horror stories that, while modern solar panels are getting increasingly good at reacting to shading using bypass diodes, that regular shading increases the risk of diode and panel failure. In some cases manufacturers determining that known shading issues counts as an installation issue, therefore no warranty support, unless otherwise protected by microinverter/optimiser.
No one looks to be questioning the reliability of the Enphase microinverters. However, the same cannot be said for most of the optimiser manufacturers out there. Albeit the system I am otherwise considering is Huawei based and failure rates seem pretty low on their optimisers.
I do have concerns that microinverters would introduce an element of clipping (that an AC coupled battery obviously can't use) and (certainly US) installers seem to say that they size to ensure good generation at low light conditions (so I would worry that by upping the top end limit e.g. using IQ8H, I might be giving up some low end production - but I've struggled to find data I can interpret on this).
Another driver for this train of thought was microinverter lifespan closely matches panel lifespan and the AC battery choice is completely separate. The worrier in me has concerns that (on a DC coupled, hybrid inverter, setup) when the likes of the battery, BMS, or the string inverter requires replacement that you could end up stuck in a loop of potentially struggling to match parts into your existing ecosystem, or missing out on being able to make use of the latest innovations, or even having to commit to replacement of a whole suite of components once the first of the bundle fails.
Is there a general consensus that as long as sticking to well known/adopted brands that compatible kit will still be available 10-15 years down the line?
Also still looking for an answer to the question what happens when an optimiser fails? (assuming like Tigo or Huawei that the optimiser in question is one that doesn't need to be on all panels of an array) would this generally just be a loss in optimiser function rather than a complete loss of generation from the associated panel?
Happily I do keep swinging back to a position that the Huawei setup I've been quoted has been sensibly pieced together.
Sorry Declan, those sorts of issues are beyond my level of expertise. I would hope that companies like Solaredge and Huawei would maintaince parts for 15 year old installations, but who knows!
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody I can also see the valid point that the DNO could understandably worry about independent discharge to grid.
Easy to accidentally start thinking the kW numbers we're talking about as 'small', i.e. comparable to a domestic EV charger or 'its a domestic array and a battery in my garage after all' but when 3.68 kWh is 16A I can see that a 6-7 kW array plus a battery with reasonable discharge rate soon adds up!
80A (my incoming fuse rating) is just over 18kW.
Would be quite conceivable to be asking to run 50A back to grid in an AC coupled scenario.
My gut says ask for too much and you risk getting limited back further than if you'd asked for a more reasonable amount in the first place ...
@declan90 Too true, balancing the grid must be a tricky job. My experience was that the DNO wasnt overly keen on getting into a conversation with me, although I did get an answer. The solar installer contacted him and agreed what was acceptable, which to be fair is working well. Im trying to get my tariff switched now so I can charge my battery at cheap times and export to the grid.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@derek-m apologises I was in a rush and abbreviating. I will insert 'coupled' into the relevent paces in my post 🙂 Update seems I cant actual edit the offending post now
Don't worry, I obviously knew what you meant, but I still think it is important that the correct terminology is used so that there is little room for confusion.
- 22 Forums
- 2,036 Topics
- 44.4 K Posts
- 40 Online
- 3,240 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: The Rise and Fall of Europe’s Most Generous Green Subsidy
@editor Attached images of external insulation. Think...
By Dwynwen , 56 seconds ago
-
RE: Air Source Heat Pump - Side Alley Suitability
@ad3628 I’ve seen loads of heat pumps successfully inst...
By Mars , 12 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Thermal Off's
@trebor12345 The Auto function is supposed to adapt au...
By Heatgeek , 14 hours ago
-
RE: In the middle of an ASHP installation - a few questions (and issues)
@jamespa they didn't provide any contract, or design pr...
By benson , 17 hours ago
-
RE: The Great British Heat Pump Quiz
@allyfish thanks for the feedback and glad it was fun! ...
By Mars , 19 hours ago
-
RE: help sizing rads based on room by room heat loss
If its 1988W at DT 50, which is how most radiators are ...
By JamesPa , 1 day ago
-
RE: Career change – entering the world of heating and heat pumps
@editor Mars, thank you. That's along the routes I was ...
By Lakey , 1 day ago
-
@editor thanks Mars, it's a rare occasion I'm looking f...
By big_si , 1 day ago
-
RE: Efficiency Concerns on newly installed Mitsubishi Ecodan 8.5kW
@ashp-bobba and @jamespa - thank you both for all your ...
By CBrenewable , 2 days ago
-
-
Win one of five "Heat Pumps 101" Courses
Heat pumps are gaining traction in the UK, but between ...
By Mars , 2 days ago
-
RE: Agile: average import cost vs other tariffs?
@toodles thanks for the analysis. I'll be really intere...
By Old_Scientist , 2 days ago
-
RE: ASHP Ecodan L9 error - No Heating but Hot Water
@phoenix15 I'm no plumber so please don't take this as ...
By dnagre , 3 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
@grantmethestrength Oh sorry to hear that, there should...
By ASHP-BOBBA , 3 days ago
-
@ashp-bobba TBH the ladies are rather disorganised, so ...
By Cathyem1 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
And for those of us without an automatic irrigation sys...
By Majordennisbloodnok , 3 days ago
-
Logically, the lower frequency = more gentle, yes, but ...
By SUNandAIR , 3 days ago
-
RE: Ideal Logic ASHP - change from 55°C to 35°C Heating?
Good point. I’ll keep my eye on the manifold temperatur...
By Tomdad , 3 days ago
-
RE: How hard and expensive would it be to change panel and add battery?
@transparent It is a setting that Octopus make via the ...
By Toodles , 3 days ago