@rusty any power company will look at peak amps when sizing a system. If you have 100amps on single phase, you have 24kw to play with. 18kw taken up from the ASHP does not leave a lot of wiggle room. In reality you wont get anywhere near this, but it COULD happen and that's the power companies issue.
Posted by: @batalto@rusty any power company will look at peak amps when sizing a system. If you have 100amps on single phase, you have 24kw to play with. 18kw taken up from the ASHP does not leave a lot of wiggle room. In reality you wont get anywhere near this, but it COULD happen and that's the power companies issue.
Thanks for the explanation. I’m also in the early stages of looking at ASHP sizing and expect a largish unit, similar to @timh. I am finding the preliminary information available from manufacturers data sheets to be rather poor. Peak current requirements being one factor. I’ve got two 100A circuits to the house (or at least the fuses say 100A on the label), legacy of it previously being divided into a dependent relative annex, now removed, and the original circuit. The down side being two standing charges for the meters. I was going to have one removed, but perhaps I’ll keep it.
Posted by: @timh@rusty that is a good point. A 7kW car charger will use 7kW, but if the heat pump is 300% efficient, then if the output is 18kW, the input would only need to be 6kW, which makes a big difference. Thank you!
Sorry, I didn’t mean to imply that the supply should be sized by the typical power requirements. I’m aware that there will be a large start up current due to the compressor and fans starting up, etc, however I was under the impression that modern HPs used mitigation strategies, soft start, inverter control etc. I was a bit spooked by the thought of requesting a supply upgrade. See also the response from @batalto.
@rusty I can 100% tell you they have all of those features and I would never expect to see that kind of draw unless incredibly exceptional circumstances. I can also tell you a power company couldn't care less and will take the rated power as it's use when doing their calculations.
Posted by: @batalto@rusty I can 100% tell you they have all of those features and I would never expect to see that kind of draw unless incredibly exceptional circumstances. I can also tell you a power company couldn't care less and will take the rated power as it's use when doing their calculations.
@batalto, thanks again. Just out of interest I asked my DNO (Western Power), how they would treat this size installation. The website has some information on connecting HPs, but it’s rather vague. The response was basically to check with the installer/manufacturer ... not all that helpful.
The solution seems very easy to me. Ditch the EV 😂. Just my opinion but they aren’t good enough yet, they aren’t saving the planet, the infrastructure isn’t capable of mass ownership/charging, they cost a fortune to buy, naff all residual value and that value declines very rapidly, cost of replacing and recycling the batteries……… etc etc. Going to cop some flack for this opinion, and it’s probably an argument for a different thread, but I care not a jot. Hey ho 😘
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
75A is definitely over the top.
For context, we have a 12 kW heat pump, a 7 kW EV charger, a hot tub, and a background house load of around 1kWh, and everything is absolutely fine with an 80amp main house fuse.
Posted by: @rustyPosted by: @batalto@rusty I can 100% tell you they have all of those features and I would never expect to see that kind of draw unless incredibly exceptional circumstances. I can also tell you a power company couldn't care less and will take the rated power as it's use when doing their calculations.
@batalto, thanks again. Just out of interest I asked my DNO (Western Power), how they would treat this size installation. The website has some information on connecting HPs, but it’s rather vague. The response was basically to check with the installer/manufacturer ... not all that helpful.
I'm with Western Power and found them really helpful. Called the main office and they gave me the number of the local depot (South Wales) who came out and upgraded my main fuse within days (from 65 to 80amp). Didn't charge either which surprised me (said it was part of their statutory duty).
They said an 80amp fuse would handle a heat pump of up to 18kw - but I don't have solar or EV.
The one I'm planning to install is only 7kw so will be notification only.
The only other thing they said was to make sure the pump complies with BS EN6100-3-2/3
I guess any new heat pump from a reputable manufacturer would do that....but there's some details here if you're technically minded. https://www.westernpower.co.uk/downloads/3379
All way over my head... but the chap at the local depot was happy to talk through the details if needed. Maybe worth trying them again if you're not sure of anything.
Posted by: @morganThe solution seems very easy to me. Ditch the EV 😂. Just my opinion but they aren’t good enough yet, they aren’t saving the planet, the infrastructure isn’t capable of mass ownership/charging, they cost a fortune to buy, naff all residual value and that value declines very rapidly, cost of replacing and recycling the batteries……… etc etc. Going to cop some flack for this opinion, and it’s probably an argument for a different thread, but I care not a jot. Hey ho 😘
I won't be getting an EV either. I already have one expensive, not good enough yet, incapable of mass ownership piece of technology that will cost a fortune to replace and don't need another.
@kev-m tut
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and new Hyundai Ioniq 5 N electric vehicles with Myenergi Zappi mk1 charger
Posted by: @andygoPosted by: @rustyPosted by: @batalto@rusty I can 100% tell you they have all of those features and I would never expect to see that kind of draw unless incredibly exceptional circumstances. I can also tell you a power company couldn't care less and will take the rated power as it's use when doing their calculations.
@batalto, thanks again. Just out of interest I asked my DNO (Western Power), how they would treat this size installation. The website has some information on connecting HPs, but it’s rather vague. The response was basically to check with the installer/manufacturer ... not all that helpful.
I'm with Western Power and found them really helpful. Called the main office and they gave me the number of the local depot (South Wales) who came out and upgraded my main fuse within days (from 65 to 80amp). Didn't charge either which surprised me (said it was part of their statutory duty).
They said an 80amp fuse would handle a heat pump of up to 18kw - but I don't have solar or EV.
The one I'm planning to install is only 7kw so will be notification only.
The only other thing they said was to make sure the pump complies with BS EN6100-3-2/3
I guess any new heat pump from a reputable manufacturer would do that....but there's some details here if you're technically minded. https://www.westernpower.co.uk/downloads/3379
All way over my head... but the chap at the local depot was happy to talk through the details if needed. Maybe worth trying them again if you're not sure of anything.
Probably the way I phrased the question, I have found WPD helpful in the past also.
Some of the fog is clearing a bit, if I understand correctly. I guess in the absence of any other info, the DNO will probably assume that the HP can become a purely electrical heater, hence the high assumed current demand based on the rated power. There will also be voltage drops in the cabling to the network from the pump start up transients and steady state load, which must remain within some tolerance of nominal. Switching in large transient loads makes the lights flicker.
Hi @rusty
I don't know for certain, since I haven't seen it stated in any of the manuals, but I suspect that the compressor motor, and probably also the fan and water pump motors, may all have inverter drives, which would mean that could have a soft start capability, and hence would not create an inrush current surge when they start.
- 26 Forums
- 2,283 Topics
- 51.1 K Posts
- 209 Online
- 5,944 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
Hello, Question on how Havenwise works with a Samsung...
By nickhorne , 21 minutes ago
-
Extend the colder range of the weather compensation curve?
In theory everyone has a heatpump designed to deliver t...
By TheBinMan , 38 minutes ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@jamespa thank you. The unit is a EDLA09DA3V3. Refriger...
By MairiA , 54 minutes ago
-
RE: Faulty Clivet heat pump out of the box
@steveimpey I’m always watching 👀My Clivet cont...
By Mars , 4 hours ago
-
RE: When to use Octopus Intelligent Go tariff with my heat pump and battery
@treewizard That's probably fine, provided as you say...
By GrahamF , 5 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
16Kw AIROSD Manufacturer: Foshan Model: QBKFXFC-...
By Polar bear , 5 hours ago
-
Just a suggestion but upload your images to an AI agent...
By RadWhisperer , 7 hours ago
-
RE: Daikin Wireless Thermostat
The switch from WDC to LWT i.e. pure WC is fairly strai...
By RadWhisperer , 7 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Thank you for your continuous research, and posts. As y...
By ectoplasmosis , 15 hours ago
-
RE: Trying to understand my Nibe F1245
@barry-sharp, is this something you could help with?
By Mars , 16 hours ago
-
I signed up for this, I think it will be a good one. Al...
By ASHP-BOBBA , 20 hours ago
-
RE: Heat Loss v Outside Air Temperature
Ideal conditions to collect the data! Although the left...
By cathodeRay , 21 hours ago
-
RE: My DIY Heat Pump installation
@majordennisbloodnok The 'more' button takes me to ...
By Polar bear , 21 hours ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
@vsmith1 If you have access to Home Assistant then you ...
By Gmuzz , 22 hours ago
-
Aira Intelligence: integrated home energy system
Aira has just announced a new integrated home energy sy...
By Mars , 24 hours ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
i cant trace it. Near the pumps in the basement it seem...
By bonobo , 1 day ago
-
Daikin Altherma Heating Controls using Onecta Integration via Home Assistant
Ok so likely not setting the world on fire here for rev...
By phil bell , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
So I’m still with E.ON Next, and I received a pretty sn...
By Mars , 2 days ago
-
RE: First time wall mounting an ASHP
what you need to do is everything you can to remove the...
By ASHP-BOBBA , 2 days ago