Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
We designed and built our own house around a GSHP in 2011, because we wanted to do the right thing, even though we had mains gas. This year it has developed many issues and alarms and has finally now stopped working. With sub-zero outside weather I'm rather desperate!
No one seems to know anything about it, I'm over £500 down just having 3 separate 'expert' heating engineers stand there and let me shown them how it works and them to scratch their heads and walk away and send me a bill. On top of this it took me a while just to get someone to come and look at it, we had no heating in November.
Is there anyone out there that can help?
The main issue seems to be a HTF alarm (GT8/GT9) and then a HTF max which trips the unit out. I'm told there should be a particulate filter but cannot find it, I know it's not in the inside of this model, so it might never have been fitted.
I increased the alarm threshold and lowered the water temperature to force the pump to drop into rad heat in order to get heating into the house. This was in November, and it's limped through to now, but the GT8 temp has increased to over 70 with a GT9 at sub 30, and with water temperature of only 40. Now cannot get it to jump to rad heat. If I try add heat to get it to cycle the water temp to over 60, then a electrical cassette alarm triggers.
Alto Energy have been quite helpful and have told me to drain the system and check the flexible hoses below the electrical cassette, but this is beyond my abilities and when I have suggested this to the heating engineers, then don't seem keen either?
I have been given a quote to install a Worcester Bosch gas boiler and HW tank, it's quite eye watering after spending £25k on a system I thought we would get 20-30 years out of, however, it's a lot cheaper than a replacement GSHP.
Its a fact that there are more engineers out their that understand gas boilers, and very few that are either interested or have knowledge of heat pumps.
On top of this the increase in electricity/kWhr has really also enforced my belief that we are just not ready to heat our homes with this technology.
Do you know what the alarm means.
From what you 'have been told' it sounds like a 'low flow' alarm. If it wasnt there initially then something has changed to increase the system resistance and thus reduce the flow. The most likely candidate is a blocked filter (Im basically agreeing with the advice you have received).
Both gas and heat pump central heating systems have filters to take out the crud (technical term!) that accumulates from the inside of the radiators. They need to be cleaned out every so often and if they aren't you can get a low flow alarm (or the consequences of low flow) with either. The recommendation is often to clean them out annually, but in practice they may last years (depending on your emitters) before they become a problem. That's just how it is with central heating systems.
They are typically roughly cylindrical about 10cm diameter and 20cm high. Google "Magnaclean" which is one example, or "Spirotech" which is another. It will be most likely be fitted close to the main unit in the main pipework which is the 'return' ie is bringing water from your emitters to the heat pump, or less likely it maybe just inside the unit (check the manual). If there isnt one, then the likely consequence is a blocked heat exchanger in the heat pump, which is not good news. A gas boiler suffers from exactly the same problem.
The next most likely problem is a water pump fault, but if you haven't cleaned the filter then everything points to the filter.
Since these filters are used in most central heating systems any plumber worthy of the title should be able both to find and fix it (or if you can find it then its a simple DiY job). Of course not all plumbers are worthy of the title. Feel free to post some pictures in case I or someone else can spot it.
On the matter of running cost do you know what COP you are getting and have you explored alternative electricity tariffs. There is no reason, with a half decent heat pump set up and an appropriate tariff, why you should be paying anything significantly more than you would pay for a gas fired system, and you might well be able to pay less.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Further to the above I found the manual here
Page 37 describes the alarm and possible reasons, of which a blocked filter is one.
Page 29 describes the particle filter which is, it seems, integral to the pump (but may nevertheless be fitted externally depending on your model - see page 29). It also describes how to clear it which does not require draining the system (but does require a pair of 'supplied' circlip pliers, probably now discarded but obtainable from eg Halfords)
You may in addition have a third party Magnaclean/Spirotech filter a blockage in which would have the same consequences and cause the same alarm so far as I can tell. So its worth looking for this as well.
Hopefully that helps.
This really should be an annual maintenance action, but I guess many people (including me) don't actually bother with annual maintenance of heating systems.
PS, for transparency I'm neither a plumber nor a heating engineer. I have a physics degree and spent 30 years in engineering, so have a bit of a 'nose' for this sort of problem, but essentially zero specialist knowledge. (This may or may not be a disadvantage, because I know essentially nothing I am forced to work almost everything out from first principles, which generally turn out to be extremely simple and common to multiple systems. However please note that this means I can also get caught out!)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Many thanks for taking the time to reply. There is a Magnaclean on the return from the rads/UFH, which I have cleaned myself, is this just the white plastic filter and actual magnets that you clean and there is no other cleaning necessary? I have tried to upload a pic, but for some reason won't let me.
There should be a particle filter on both the cold feed and the hot flow and return, as mine is the C line with the hot water tank inside the unit, both are external to the pump, however, I think my installer, who was pretty useless maybe forgot to put them in.
I'm also a mechanical engineer by apprenticeship and degree, which is why I probably know more than the heating engineers that visited. Unfortunately, it's a matter of confidence of not screwing it up completely at this time, as I've managed to get the pump into limp mode by lowering the water temp to 35 and also bring the heat curves down, this way the GT8 temp remains below the cut out temp and I get a little heat into the house. However, the anti-legionnaires function, ie heating the water to 65 will not work.
Thanks for the manual too. I will check if this is the same as the one I have.
Posted by: @abboteThere is a Magnaclean on the return from the rads/UFH, which I have cleaned myself, is this just the white plastic filter and actual magnets that you clean and there is no other cleaning necessary? I have tried to upload a pic, but for some reason won't let me.
I can see the magnaclean. I cant remember whats inside TBH but that sounds about right.
Posted by: @abboteThere should be a particle filter on both the cold feed and the hot flow and return, as mine is the C line with the hot water tank inside the unit, both are external to the pump, however, I think my installer, who was pretty useless maybe forgot to put them in.
Oh dear - its just possible that the heat exchanger could be blocked then if these aren't present and you have a flow problem. Is there any way you could flush it through? Of course there are other possible explanations for a flow problem but filter blockage this is definitely the most likely.
Posted by: @abboteI'm also a mechanical engineer by apprenticeship and degree, which is why I probably know more than the heating engineers that visited. Unfortunately, it's a matter of confidence of not screwing it up completely at this time, as I've managed to get the pump into limp mode by lowering the water temp to 35 and also bring the heat curves down, this way the GT8 temp remains below the cut out temp and I get a little heat into the house. However, the anti-legionnaires function, ie heating the water to 65 will not work.
I think you have put your finger on why this might be better as a DiY job!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
As I thought I've been told that the most likely cause if the internal flexible pipes below the electrical cassette and flow pump. It's great that the price of these pipes is only £146 inc' VAT but so far the best cost I have for their replacement is £1,000 ex VAT, and that's only for 0.5 days labour. I'm still leaning towards ripping it out. Is there a market for second hand spares or repairs IVT GSHPs?
Posted by: @abboteI'm still leaning towards ripping it out. Is there a market for second hand spares or repairs IVT GSHPs?
That's a pity, the most expensive part of a GSHP is, SOFAIK, the underground bit by some margin, which you already have!
Unfortunately we live in a throwaway society where nobody wants to (or knows how to) repair anything, and if they do wants to rip us off big time. Its true across the whole spectrum of 'consumer' goods.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


@abbote Hi there,
Well done with all the fault-diagnosing you have done so far and sorry to hear that you have been having such issues with your system.
Did you manage to locate the particle filter and get it cleaned?
Heat pump consultant and designer at Cirrus Energy.
Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Book a one-to-one session with Rob to discuss things here.
-
Ground Source Heat Pump Systems and Their Design
12 months ago
-
Depths for GSHP slinkys
1 year ago
- 21 Forums
- 1,961 Topics
- 42.5 K Posts
- 61 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
Heat Pump Sizing & Installation Costs
I’m doing some research for an upcoming article and pod...
By Mars , 2 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
@johnr Hadn't thought about secondary glazing - definit...
By BAMi , 22 minutes ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 52 minutes ago
-
RE: SolarPV tables / online calculator
By Gary , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 12 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 12 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 14 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 16 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 18 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 19 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 21 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 24 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 2 minutes ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 52 minutes ago
-
SolarPV tables / online calculator
By MichelleC 8 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 20 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 22 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago