Zilmet 110 ultra pro 18 (type 19) expansion vessel - Horizontal installation
This has been installed horizontally on top of a kitchen cabinet which houses the hot water tank. At the time of install I challenged the plumber on the orientation and he said that these types can be horizontal and all is fine.
I have looked on the Zilmet website and their documentation states:
"Expansion vessels should always be installed in a vertical orientation with the water
connection at the bottom.
Our requirements are simply that the vessel be installed in a way that allows future access,
and ideally be in the coolest available part of the system to assist with longevity of the
membrane. At no time can a vertical vessel be mounted horizontally, or be mounted to a
wall or framework suspended by itʼs legs."
Now, the exact model number 1100001955 is not listed in the manual and they do have "vertical and Horizontal" models. But to me this one looks like it should be Vertical as it has a wall brace.
Anyone else have this installed or experience of these?
I have sent an email to the manufacturer to confirm, hopefully i get an official reply.
Posted by: @saf1973the exact model number 1100001955 is not listed in the manual and they do have "vertical and Horizontal" models. But to me this one looks like it should be Vertical as it has a wall brace.
Anyone else have this installed or experience of these?
Thanks for including a photo @saf1973
I have five expansion vessels of differing sizes and orientations.
But it has much to do with me having a well and no mains water supply! 😎
All of these are self-installed, and I've had to replace one due to a failed membrane.
Three are for potable (treated) water, and the others for expansion in heating circuits.
The good news is that I therefore have the experience you're looking for!
The quote from the Zilmet site "Expansion vessels should always be installed in a vertical orientation with the water connection at the bottom" needs context.
It is not always the case.
Domestic well-pumps are often supplied with a horizontal expansion vessel beneath them - for which Zilmet is one of the manufacturers!
Nor is a welded bracket an indication of the preferred orientation.
Different models of expansion vessel are required depending on the 'type of water' in the system they are connected to.
Potable water, suitable for drinking, is usually connected to a vessel painted blue if it is made with cast mild steel.
But it can be left unpainted if stainless steel is chosen.
If the fluid contains system inhibitor chemicals, such as that which runs through radiators, then the vessel manufacturer may recommend that the internal rubber diaphragm is evenly in contact with that fluid.
That would occur in a vertical orientation such as you describe.
Each vessel is different, which is why it's important to select the correct one for the application.
Over time (years) there will be 'leakage' of air across the membrane.
That which enters a heating circuit will be eradicated through the air-release valves.
But the slow migration of air (gas) molecules will reduce the pressure in the expansion vessel.
This pressure is restored by using a car foot-pump to add air through the schrader valve beneath the black cap at the opposite end to the water connection.
It's tricky to do that whilst squeezing yourself into a kitchen cupboard!
Moreover, to obtain the required pressure, it's usual to have a shut-off valve on the water connection.
Otherwise you're pushing the foot-pump against the entire water circuit!
In tight situations I have two shut-off valves on the flexible connection to the expansion vessel.
By shutting both, I can remove the entire vessel from the circuit, whether it has any pressurised water inside it or not.
I can then take it outside and re-pressurise it with ease.
In most cases a pressure vessel should be oscillating around the half-full position.
If it's completely full of water then the pre-pressurised air part of the vessel needs pumping up.
You can deduce this by placing the vessel on a set of bathroom weighing scales.
1 litre of water has a mass of 1Kg.
Does that help?
Save energy... recycle electrons!
@transparent thanks for the post!
Mine is connected to the combination valve which sipplies the cold feed to the DHW tank and balanced cold to the house, so from your post it would see that it does not matter it's orientation so much? Also, this is a white vessel so is it the wrong type?
I am thinking that if it is on its side any sediment would build up under the membrane and potentially rub against it with the friction eventually bursting it. If it is vertical the sediment would remain at the bottom of the vessel and not touch the membrane. Fortunately I do have a whole house filter so sediment should be minimal.
I had a similar unit in my previous property where I maintained it, i had to release the water pressure in the system to be able to pump up the diaphram. In one instance i replaced it as the diaphram had burst. It was wall mounted but i cannot remember if that was for Potable water or the heating system.
i've just found this good YT video that explains a lot and shows a vessel in horizonal orientation...
Posted by: @saf1973... from your post it would see that it does not matter it's orientation so much? Also, this is a white vessel so is it the wrong type?
I don't think you can deduce that much from what I've said!
Zilmet will specify the orientation for each design which they offer.
It depends on a number of factors, including the composition of the butyl-rubber membrane, and the type of lacquer which may have been applied to the internal walls.
There are more combinations of features than can possibly be described by the colour which is used to paint the outside.
It is no longer the case that all manufacturers use blue to identify suitability for potable water.
As that YT video demonstrates, the new vessel chosen by the presenter is coloured white, but he introduces it as suitable for potable water!
I too have had difficulty finding the Zilmet specification sheet for your particular vessel.
However Advanced Water's site does have a document you can download which allows you to calculate the pre-charge pressure and the required total capacity you need.
Save energy... recycle electrons!
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 347 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: What determines the SOC of a battery?
@batpred I didn't write the Seplos BMS software, I a...
By Bash , 13 minutes ago
-
RE: Electricity price predictions
Sorry to derail this thread ‘slightly?’ but back to the...
By Toodles , 22 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
Without knowing it, @andrewj, you've laid down the gaun...
By Majordennisbloodnok , 41 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 46 minutes ago
-
I am having my existing heat pump changed to a Vaillant...
By trebor12345 , 1 hour ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 2 hours ago
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 4 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 4 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 10 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 20 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 22 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago