Vaillant Arotherm Settings for New Installation
It is set on pure weather compensation at internal temperature of 22C. The unit runs 24hrs with a setback overnight. Theoretically that should be good for COP even if the electricity usage could be higher than running it for a shorter period.
I cant really drop the desired temperature or curve as the BIL's wife likes it warm. It was running at 20C initially but that didnt seem to help the COP greatly.
Your COP figure looks lovely. What sort of flow temperature are you using to get that high?
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Dropping the curve won’t drop the temp, it just adjusts the time it takes to get there. (Well in my simple mind lol).
Our present heat curve setting is 0.3. That’s been set by Vaillant using the adaptive heat curve setting. Next time the system fires up I’ll check what the flow temp is for you.
drew
Thanks Drew
that isn’t how I understand it. To me the curve sets the “gradient” on the weather compensation chart. The desired room temperature moves that gradient up or down the flow temperature axis.
I’ve put gradient in inverted comments as I know that it isn’t a straight line.
I might be wrong but coming from a system where I enter the min and max flow temps for different outside air temperatures, it makes sense in my mind.
In that case, if too low a curve is selected, a room might never reach the desired temperature.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
You are correct. I just tend to over simplify things. We’ve never had it not reach temperature; it seems to just take longer the lower the curve number is. With the Vaillant system there is no option to adjust the temps individually so the curve is the only option we have to play with. It may be worth trying to lower yours to 0.6 and seeing how it goes.
simplistically, with ours the higher the number the higher the electrical bill.
Drew
@drew-pa Ah thanks. Good to know I dont have a misconception about it.
On Energy Stats Uk ( https://energy-stats.uk/vaillant-arotherm-weather-curve-information/) Mick Wall gives a rough way of setting the correct curve.
A more detailed equation (TFlow = a * (HC * (Tset - Tout))b + Tset) is given on the Open Energy Monitor forum. ( https://community.openenergymonitor.org/t/vaillant-arotherm-owners-thread/21891/83?page=5)
Ive used that to reproduce a more accurate table of flow temperatures for curves at desired room temperatures at -3C OAT
I will paste it below for anyone interested in the future.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,122 Topics
- 46.6 K Posts
- 75 Online
- 4,529 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Are you sure the limit is not imposed by your emitters?...
By JamesPa , 13 seconds ago
-
RE: Why do we need pressurised systems?
@old_scientist If that were the case (and it might well...
By Toodles , 1 hour ago
-
OK... I'm here. But the amount of my time needed to add...
By Transparent , 3 hours ago
-
RE: 300 Liter Tank - Do I have to heat it all?
There’s no second hand market for DHW tanks (I was told...
By Judith , 8 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We had an excellent four months (11/3 to 15/7) generati...
By JulianC , 17 hours ago
-
RE: Is this just haze or something more?
I think the present somewhat cooler hazy days show the ...
By Judith , 22 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
All noted and accepted and as I say I am sorry that you...
By JamesPa , 24 hours ago
-
I think it is very much me that is sitting outside the ...
By Grantmethestrength , 1 day ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@davidalgarve It should just be recovered by both servi...
By dgclimatecontrol , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
Aggregators have been recognised for many years, and it...
By Transparent , 2 days ago
-
RE: Help me keep the faith with my air source heat pump installation
Great news I edited my previous post (probably af...
By JamesPa , 2 days ago
-
RE: Double or Triple Glazed Windows?
@toodles Glad to hear things are progressing well for y...
By TRBob , 2 days ago
-
How to waste energy (and time) playing with AI.
A friend of mine who subscribes to an AI service was ex...
By Toodles , 3 days ago
-
RE: Heat Pump Books For Beginners – Bodge Buster & From Zero To Heat Pump Hero
@topher you’re more than welcome to, yes. I’ll send you...
By Mars , 4 days ago
-
RE: Fitting new shower valve ..........
I’ve never taken a chance when fiddling and changing ou...
By Mars , 4 days ago
-
You should contact the council and report the unsatisfa...
By JamesPa , 4 days ago
-
RE: Benefits of an extra horizontal loop for GSHP
I would deffo install an additional slinky run, especia...
By Transparent , 4 days ago
-
RE: Say hello and introduce yourself
@editor fab - thanks Mars, and keep up the great work o...
By normpang , 4 days ago