Vaillant 10kw ASHP installation. Installer issues
Hi all,
Sharing my experience and current heat pump situation to potentially get some input and advice.
Had a 10kw vaillant installation which I am now concerned about due to the following issues;
The pump has been identified as oversized for my property
The installer recommended the 10kw heat pump based on my previous bills and did not carry out a heat loss calculation for the property. is this correct?
He originally suggested a 7.5kw but when I queried if the pump will provide sufficient hot water and heating, the installer recommended the 10kw saying it was a slight increase in price which will definitely provide the required heat. I later found out he should have advised otherwise using his professional knowledge but didn’t.
I was quoted for items that were not installed most importantly I was quoted and advised that a buffer tank will be installed however upon installation, a low loss header was installed. Upon review by another heat engineer at cost to me, I was advised that the system would perform better with the buffer tank due to the size of the heat pump especially given that it’s oversized for the property.
The pipes were not insulated leading to heat loss.
installer damaged property during installation and is yet to rectify the issues
The heat pump appears to require planning permission due to size but I was not advised of this by installer
The heat pump is noisy and also drains water into the drive which then freezes up.
The issues above have been identified however, I have been trying to get the installer to rectify these issues and they have been very bullish and a bit intimidating while also giving misleading information. Originally insisting they would not rectify the issues and involved vaillant.
Given their behaviour, I advised of my intention to raise a dispute with RECC which they claimed to be a member of. I have now found out that they are not a member of RECC, it is a different company with the same director that is RECC member. It is the director that I have been dealing with. I feel that I’ve been misled by this company and I could have serious issues in future in addition to the issue with their workmanship. I’m really not sure what to do. To escalate, I could raise the issue with RECC against the member company but my contract is in a different company name????
Quite honestly, this kind of installer behavior has to come to an end. It’s nuts.
There are clearly some basic issues, like drainage and damage. The buffer is a contentious subject, so one to avoid for now. And yes, a heat loss calculation should have been carried out to size the heat pump correctly.
The RECC angle is one worth pursuing, but I’ve yet to encounter an homeowner that has received a positive outcome. But I keep forwarding them cases, trying to add pressure.
Are any of the installers MCS certified? Also, have you paid them yet? If you haven’t, don’t pay until the matter is resolved.
Pre-order: The Ultimate Guide to Heat Pumps
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor thanks for this. Yes I will pursue the RECC and see what comes of it. Well the MCS certification is held by the sister company which is the same one with RECC registration. It’s the sister company that also applied for the BUS scheme .
I will explore raising with MCS too
How concerned should I be about the drainage? The reviewing heat engineer mentioned the drainage and I’ve also seen posts about the drainage here.
Well I am pursuing the buffer on two basis, one- that’s what I was quoted and it was changed without an approval or advise to me, two -the buffer is more suited to the pump size as explained to me. Although I was also advised that the pump is powerful enough to work without the buffer and llh, the buffer is the better of the two for the installation. The buffer can hold more volume of water to help the pump work efficiently without needing it to kickstart so frequently as it does now leading to high energy use. It will be marginally better but still better and I believe it will help the lifespan of the Heatpump too.
Thank you for confirming that a heat loss calc was necessary. When I asked the installer about this and the information they based the hp size recommendation on, they simply sent my bills and claimed that was enough to make the recommendation. I requested a heat loss report from another engineer and I know my installer definitely didn’t provide this. They seem unaware of the significance of this report . They did check the ECS of the building though. Could they claim this is enough and replaces the calculations?
There is an outstanding balance which I am currently using as leverage. If I had paid everything, I would be in a much worse situation right now. It is only leverage though as if they do not fix the issues, it will cost me potentially more than the balance to fix their mess. I intend to have all the issues resolved before paying the balance and I’ve informed the installer of this.
providing you have compensation controls (ie not heat miser, nest, hive, honeywell) from the heat pump manufacturer and providing system volume is within heat pump manufacturers specification the lack of buffer is not an issue.
Over sizing is disappointing, but what is the actual heat loss? How many radiators?
If MCS is behind this then how come a heat loss calculation was not undertaken? But you also need to appreciate heat loss calculations are only skilled guessing as you don’t know the building fabric and ventilation of an existing building in its entirety
At the end of the day a heat pump is just another heat source. It doesn’t really need a heat loss calculation to work effectively.
is the lack of insulation indoors or outdoors?
If you didn’t ask him to get planning permission specifically it’s not really his issue (MCS may suggest otherwise)
Professional installer
Posted by: @gemiar@editor thanks for this. Yes I will pursue the RECC and see what comes of it. Well the MCS certification is held by the sister company which is the same one with RECC registration. It’s the sister company that also applied for the BUS scheme .
I will explore raising with MCS too
How concerned should I be about the drainage? The reviewing heat engineer mentioned the drainage and I’ve also seen posts about the drainage here.
Well I am pursuing the buffer on two basis, one- that’s what I was quoted and it was changed without an approval or advise to me, two -the buffer is more suited to the pump size as explained to me. Although I was also advised that the pump is powerful enough to work without the buffer and llh, the buffer is the better of the two for the installation. The buffer can hold more volume of water to help the pump work efficiently without needing it to kickstart so frequently as it does now leading to high energy use. It will be marginally better but still better and I believe it will help the lifespan of the Heatpump too.
Thank you for confirming that a heat loss calc was necessary. When I asked the installer about this and the information they based the hp size recommendation on, they simply sent my bills and claimed that was enough to make the recommendation. I requested a heat loss report from another engineer and I know my installer definitely didn’t provide this. They seem unaware of the significance of this report . They did check the ECS of the building though. Could they claim this is enough and replaces the calculations?
There is an outstanding balance which I am currently using as leverage. If I had paid everything, I would be in a much worse situation right now. It is only leverage though as if they do not fix the issues, it will cost me potentially more than the balance to fix their mess. I intend to have all the issues resolved before paying the balance and I’ve informed the installer of this.
Vaillant produce schematics without a buffer, and are perfectly happy without one “ providing system volume is big enough” and you don’t use on off controls
Professional installer
Don’t pay them the balance, run them off the job, find someone else to fix this mess.
They seem like proper cowboys these ones.
You could find any competent plumber, give them the manufacturers installation schematic (not the one from the merchant, or from some third party) that suits your system and tell them to get in with it.
The manufacturers produce these for a reason. Choose the one without any hydraulic separation for the best system efficiency.
As for the planning issue… if anyone asks, tell them it’s an air conditioner 😉
A heat loss calc isn’t technically necessary if you know that the property is adequately heated by the current boiler. I’d argue that rad sizing to rooms at a lower flow rate is more important. For example, my place has an 11kW baxi Bermuda, installed when the property had no loft insulation and no double glazing, it managed to heat the place just fine back then, and still does now. So you could just say 11kW is fine and be done with it.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
Posted by: @gemiarHow concerned should I be about the drainage? The reviewing heat engineer mentioned the drainage and I’ve also seen posts about the drainage here.
I think it depends where your pump is. Our condensation drainpipe froze over in the cold and the pump slowly dribbled water across the paving from under it, which then froze, but we don't use that path much when it's that cold, there was space to step over it and it slopes away from the house, so I'm not bothered enough to change the drain (wider-diameter pipe or steeper fall).
Oversize unit: it may cycle in and off more on low output, as the heating load might be below the minimum turn down capacity of the unit. That will cost more in the longer run as cyclic operation consumes more power than steady state inverter control. If the ASHP is not massively oversized it won't be significant.
Drainage: it's not difficult to connect the unit drain to a soak-away under or adjacent to the unit. If the unit is on concrete pad or paving, core cut through this to the hardcore underneath, which is unlikely to ever have a penetrating ground frost. Condensate is pure water, so connection to either a permanent drain or a soakaway is possible. Drain pipe as short as possible and insulated, should not require trace heating that way.
Planning: Your personal choice, but planning responsibility is vested with the homeowner not the installer. I would seek retrospective planning permission as, if you ever want to sell your property, the lack of planning permission will surface in conveyancing and you may be obliged to either take indemnity out on behalf of the buyer or address the issue then. The Local Authority is very unlikely to refuse permission for ASHP if unit volume >0.6m3 is the only material planning issue. You might need to submit a completed MCS noise level assessment to prove noise level compliance 42.0dB(A) max at adjacent dwellings if relevant.
Heat Load Calculations: Essential? I would say so. Both to size the overall unit and, more importantly, to check individual room emitter sizing and capacities. For underfloor heating room emitter is less critical, because you have a very large surface area. But for retrofits where ASHP is married to wet radiators, the existing rads need to be checked and, often, increased in size to suit the lowest flow design temperature possible/practical for the room design temperature. Money spent increasing radiator sizes for lowest design flow temperature will be recouped several fold over the the life of the ASHP in lower electricity consumption due to higher SCOP.
@alec-morrow heat loss from subsequent survey is 5.35kw. Note that the installer originally suggested a 7kw heat pump but wasn’t confident about this recommendation when I queried if that’ll be sufficient for the property hence why he suggested 10kw.
I specifically didn’t want to change the radiators at the time so I’m not complaining about that as it was my choice.
The pipes without insulation are inside the building. The pipes outside are insulated although not very well but they are.
Posted by: @hughfDon’t pay them the balance, run them off the job, find someone else to fix this mess.
They seem like proper cowboys these ones.
You could find any competent plumber, give them the manufacturers installation schematic (not the one from the merchant, or from some third party) that suits your system and tell them to get in with it.
The manufacturers produce these for a reason. Choose the one without any hydraulic separation for the best system efficiency.
As for the planning issue… if anyone asks, tell them it’s an air conditioner 😉
A heat loss calc isn’t technically necessary if you know that the property is adequately heated by the current boiler. I’d argue that rad sizing to rooms at a lower flow rate is more important. For example, my place has an 11kW baxi Bermuda, installed when the property had no loft insulation and no double glazing, it managed to heat the place just fine back then, and still does now. So you could just say 11kW is fine and be done with it.
who is a competent plumber though? At this stage all plumbers are competent until things go wrong. Makes me want to stick to the devil I know and give them the opportunity to fix the issues plus it gets complicated with warranties etc
Posted by: @allyfishOversize unit: it may cycle in and off more on low output, as the heating load might be below the minimum turn down capacity of the unit. That will cost more in the longer run as cyclic operation consumes more power than steady state inverter control. If the ASHP is not massively oversized it won't be significant.
Drainage: it's not difficult to connect the unit drain to a soak-away under or adjacent to the unit. If the unit is on concrete pad or paving, core cut through this to the hardcore underneath, which is unlikely to ever have a penetrating ground frost. Condensate is pure water, so connection to either a permanent drain or a soakaway is possible. Drain pipe as short as possible and insulated, should not require trace heating that way.
Planning: Your personal choice, but planning responsibility is vested with the homeowner not the installer. I would seek retrospective planning permission as, if you ever want to sell your property, the lack of planning permission will surface in conveyancing and you may be obliged to either take indemnity out on behalf of the buyer or address the issue then. The Local Authority is very unlikely to refuse permission for ASHP if unit volume >0.6m3 is the only material planning issue. You might need to submit a completed MCS noise level assessment to prove noise level compliance 42.0dB(A) max at adjacent dwellings if relevant.
Heat Load Calculations: Essential? I would say so. Both to size the overall unit and, more importantly, to check individual room emitter sizing and capacities. For underfloor heating room emitter is less critical, because you have a very large surface area. But for retrofits where ASHP is married to wet radiators, the existing rads need to be checked and, often, increased in size to suit the lowest flow design temperature possible/practical for the room design temperature. Money spent increasing radiator sizes for lowest design flow temperature will be recouped several fold over the the life of the ASHP in lower electricity consumption due to higher SCOP.
You are right - the unit does cycle on and off frequently. The unit is definitely oversized and if that unit size is being installed in the appropriate house, a buffer will accompany to run efficiently
Thanks I will explore this option. The unit drains onto hard ground and we generally don’t walk there except to check the pump.
Understand that planning is a personal choice though the installer should have advised on this. I’m already getting in touch with the LPA to see what is required and they have asked for installation design which the installer has not provided. Also yes it’s the unit volume that seems to be the only issue. Unit runs quietly on normal days but was audible when temperatures dropped to -5
I will be changing the radiators at some point but need the unit to be installed and working as a 10kw vaillant should do first.
-
Is this ASHP install OK?
1 month ago
-
Rate the quality of your heat pump design and installation
4 months ago
-
Help needed in Essex
5 months ago
-
Vaillant arotherm plus heat pump frost protection
7 months ago
-
Air source heat pump problems - NIBE F 2040 ASHP
8 months ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 31 Online
- 5,736 Members
Podcast Picks
Latest Posts
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
Yes Octopus only have the £9 a month service plan for t...
By NJT , 2 minutes ago
-
RE: Are there any lawyers in the house???
Hi @jamespa, thanks again for all your thoughts, very u...
By GuydeB , 11 minutes ago
-
RE: Who’s Caved and Switched the Heating On Already?
@allyfish Dogs have owners - Cats keep staff. You are o...
By Toodles , 20 minutes ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 22 minutes ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 6 hours ago
-
RE: Midea ASHP – how to set weather compensation
I think it is a bug in the code, it comes on even when ...
By cathodeRay , 20 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 22 hours ago
-
RE: Buffers, hot water and cooling
@jamespa Your reasonably close! Especially with warmer ...
By dgclimatecontrol , 24 hours ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 1 day ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 2 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 2 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 2 days ago
-
RE: 300 Liter Tank - Do I have to heat it all?
The size of DHW tank affects the anti-legionella cycle....
By Transparent , 2 days ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
@scalextrix Name plate capacity
By HCas , 2 days ago
-
RE: Solar Thermal DHW and ASHP
I was originally contemplating a solar thermal installa...
By jamespetts , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
My system installed in July 2024 has produced 6.4mWh in...
By jamespetts , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@judith thanks for your suggestions. Starting from col...
By GrahamF , 3 days ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I switched to "fan coil mode" to be able to set water t...
By immunity , 3 days ago
-
RE: DESNZ doing a survey which asks the right questions!
Without a survey their only source of data is probably ...
By JamesPa , 3 days ago