Undersized Vaillant ASHP and abandoned by installer
Hello everyone !
I am a newbe to this site but have spoken to Mars some years ago and I am very happy to see this site prospering.
My installer specified and installed a 7 Kw/hr Vaillant ASHP. The installer also removed a 400 Ltr tank and replaced it with a 300 Ltr tank. Both were suitable for solar thermal but neither were suitable for an ASHP.
There were many installation errors highlighted by Vaillant engineers and highlighted by a recent a report that I commissioned from a Vaillant approved fitter.
During the first few months I had a number of visits from mobile Vaillant engineers. I had asked them to attend due to the heat pump was not heating the house and was very expensive to run.
Recently, I had the pump serviced. The engineer told me that the pump was too small and according to my original SAP report should be a 12 Kw/hr ASHP, also confirmed by Vaillant.
When challenged, an engineer told me that the tradesman is their customer, and they do not wish to upset them !
I must say that I found the Vaillant engineers to be pleasant and competent.
Every tradesman has to be a member of an accredited body (Napit, Recc, or MCS) but they all consider the tradesman to be their customer !
My case is currently being examined by NAPIT.
If I change the size of my ASHP I will probably loose my Ofgem payment.
My installer is not responding to calls.
Any advice would be welcome. Thanks
What was the heat loss calculation for your home?
Do you have a buffer tank or plate heat exchanger installed?
How is your heat pump being controlled, by thermostats and or TRV's?
Posted by: @jonathanoriginal SAP report should be a 12 Kw/hr ASHP,
Should that read kW. kW is power and kWh is unit of energy used over time. 12kW used for a hour is 12kWh, also 4kW used for 3 hours is also 12kWh.
The SAP report will mention W, if you are reading kWh you are looking at the wrong thing.
Prospective of the SAP report you should have a heat loss calculation, done by the supplier.
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
Welcome to the forums @jonathan.
There’s a lot to unpack with your case. First up, can you please remind us when your system was installed?
I must say, I’ve been battling the installer “customer” angle you’ve alluded to with the powers that be, and it’s a ridiculously frustrating situation homeowners find themselves in. In 2025, with MCS 2.0, some of this is apparently going to be addressed, but currently, consumer protections are undermined by the relationship between the installer and the consumer codes or MCS.
Do you also have an open case with MCS?
If possible, please can you give me an approximate timeline of the events you’ve mentioned above. Once I have more info, I’ll take this to MCS and other bodies for comment.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
@johnmo subject to correction, I think Jonathan is saying their installer initially fitted a 7kW heat pump, but it should have been a 12kW unit.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Follow our sustainability journey at My Home Farm: https://myhomefarm.co.uk
@editor Hello Mars,
Thank you for your prompt reply.
The installer is a member of NAPIT, so I made my complaint to them on 3rd July 24. They aim to respond in
10 working days (2 weeks). My case is being handled by Rebecca Riley who is currently on annual leave until
Monday 12th. She is waiting for a response from their Technical department.
I did start a complaint with MCS on 16/6/24 but did not proceed further. (Case # 110340)
My system was commissioned in March 21. Over the next year I had a number of visits from Vaillant mobile
engineers who all failed to mention that the ASHP was too small. The latest engineer pointed out that the
water tank was suitable for solar thermal but not solar thermal and ASHP. The installer took out a 400 ltr tank
and replaced it with 300 ltr with the same spec.
I have asked Ofgem whether I would loose my RHI payments if I change to a suitable size of pump and they
are unable to tell me. Their one object in life is to withdraw payments for RHI as often as possible with no
cause.
Regards
Jonathan
Posted by: @jonathanaccording to my original SAP repor
So how Watts does that specify you need in December or January?
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
@editor Hello
I am attaching the report from Amber Heating.
I am intending to install approx 35 KW/hr of battery storage, which will be charged overnight at a cost of 7p
per Kw/hr. These will power the ASHP to heat supply energy to the house during the day and evening. This
tariff is available for
EV users. I will pay 70% less for my energy.
Regards
Jonathan
@jonathan Regarding the battery storage enabling you to use grid supply when at the cheapest tariff rate, I do something very similar with 27 kWh of Tesla Powerwalls.
For anyone in my situation (EV tariff not available as we don’t drive due to both of us having a visual handicap) Octopus Energy Cosy works very well as they recently increased the amount of hours at the cheapest rate to 8 hours over 3 intervals in a day. They now charge approx. 11.2 pence per kWh during these 8 hours thus allowing for ‘topping up’ at more frequent intervals. My aim has been to only use the grid during these 8 hours and always have charge to power the domestic needs including an 8 kW Daikin ASHP. Regards, Toodles.
Toodles, 76 years young and hoping to see 100 and make some ROI on my renewable energy investment!
Hello Derek
I have a 45L Vaillant buffer tank and sensoCOMFORT vaillant controlls plus 3 manifolds (one on each floor) controlled by time clocks (one each floor) plus room thermostats for each zone Kitchen hall office drawing room on ground floor, 4 bedrooms 1st floor, and bedroom and ensuite on top floor.
Regards
Jonathan
Do yourself a favour and give the heat pump some some chance of working well.
Time clocks delete
Buffer delete
Room thermostats delete or set high they they only work to limit stop
Set up loops by balancing to get the room temps correct, more flow if you need warmer, less flow to make rooms cooler
Assume you have pumps & mixers on each UFH manifold? If so look to delete those.
Run pure weather compensation 24/7.
Required flow temp will drop considerably giving an automatic upping of heat pump output, make your radiator dual fuel to get higher output if needed.
Buy a couple of panel heater to backfill heat demand if needed
Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.
- 25 Forums
- 1,576 Topics
- 33.6 K Posts
- 39 Online
- 1,853 Members
Join Us!
Latest Posts
-
RE: Is the Grant controller a thermostat?
@derek-m I had tried just turning off at the display po...
By Marvinator80 , 5 hours ago
-
No, 2nd was not a one-off. No, the carbon intensity doe...
By Majordennisbloodnok , 6 hours ago
-
RE: Say hello and introduce yourself
@transparent Thank you. My aim is firstly to heat my ho...
By Jancold , 6 hours ago
-
RE: Are you planning to use a wood burner to supplement your central heating this winter?
The option of supplementing the heat in shoulder season...
By Judith , 7 hours ago
-
RE: Two possible heat pump routes - how to evaluate them?
@johnmo @heacol @derek-m Perhaps it would help to dis...
By JamesPa , 8 hours ago
-
Ask why you need it? You should be running an open syst...
By Johnmo , 9 hours ago
-
RE: ASHP added to Biomass System?
My view Make sure you heating system can run at a low...
By Johnmo , 9 hours ago
-
RE: Determining correct flow rate?
Optimising flow rate for DHW heating is something I'd b...
By Old_Scientist , 11 hours ago
-
RE: My horrific Samsung heat pump installation and experience
@iantelescope Good. Why are you expecting the ...
By JamesPa , 11 hours ago
-
RE: 6 Red Flags to Avoid When Considering a Heat Pump Installation
Please keep us posted with any progress and if there is...
By Toodles , 12 hours ago
-
-
RE: Gravel trays and flexible pipes
@mike-patrick I don’t know how much condensate drains a...
By Toodles , 14 hours ago
-
RE: Heat pump monitoring - what are you using?
@njt As the Cosy peak rate (4-7pm) immediately follows ...
By Old_Scientist , 16 hours ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Hi. Unfortunately on-going. Mitsubishi agreed that th...
By Richard24738 , 16 hours ago
-
RE: Will heat pump heat hot water without increasing the temp in my home?
@ellyse I’m on octopus and initially flux because I had...
By David999 , 17 hours ago
-
RE: Energy tariffs and consumption fiddling to make my heat pump more cost efficient.
Would not bother wasting your time, every house is diff...
By Johnmo , 17 hours ago
-
@transparent it’s a 20 tube panel and at least 4 tubes ...
By David999 , 1 day ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Hi, You would need the MIM-H04EN in order to use ...
By NetDonkey , 1 day ago
-
RE: VDI 2035 heating water specification
Your water looks to in a similar place to mine, after I...
By Johnmo , 2 days ago
-
RE: Single vs. three phase for heat pump, EV and appliances
@transparent no they were a concept in America but went...
By David999 , 2 days ago
Latest Topics
-
Determining correct flow rate?
By rhh2348 18 hours ago
-
By VincePrince 18 hours ago
-
By bontwoody 2 days ago
-
By David999 2 days ago
-
Recommendation for natural herbicide
By Mars 3 days ago
-
Powerwall 3 - is it worth the outlay?
By Profzarkov 3 days ago