Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
To ASHP, or not to ASHP, that is the question!!!!!!
Hi AmyFOD,
Welcome to the forum.
As both Julian and Kev have stated, get more quotes, since £14.5k does seem rather excessive for an ASHP system without radiators.
As far as the need to change your radiators, try to think back to the cold Winter days, how hot did your radiators need to get to keep your home warm? If they were not particularly hot then you may not need to change them.
Your particular problem is living in a Radon gas area. When you had the assessments carried out, did they state the Air Changes per Hour (ACH) rate and the subsequent heat demand due to having to heat the fresh air coming in. It could be quite high in your case.
Dependent upon the number and location of the air vents, in combination with the wind direction and strength, your heat loss due to ventilation requirements could vary quite considerably from one day to the next. This of course makes estimating maximum heat demand all the more difficult.
As somewhat of a solution, you could consider installing Mechanical Ventilation Heat Recover (MVHR), which basically uses the warm air going out to heat the fresh air coming in. The manufacturers claim up to 90% of the heat is recovered, but I don't know how accurate this figure may be. The systems are not particularly cheap, probably several thousands pounds, and require the installation of ducting, but may be cost effective in your case, since it would probably reduce your total heat demand, so a suitably sized ASHP would not need to work as hard and hence could operate at lower temperatures.
It is also possible to get MVHR systems which incorporate an ASHP, which makes them highly efficient, even in the cold days of Winter. The drawback is they do not produce hot water and are not eligible for RHI payments, but as I understand are considerably cheaper than a full ASHP system.
It may pay you to explore all the various options before your make any decisions.
@derek-m Hi Derek, currently we don't have solar pv or thermal, but we would consider it.
We only moved in a month ago so we don't have any experience of the depths of winter - it's been pretty chilly but we used to live in a wooden cabin with no central heating so I think we're quite hardy. I don't know what the ACH rate is, they didn't tell us that. I don't know anything about MVHR but it sounds like we ought to think about it.
We're looking to get a few more quotes and maybe consider a biomass boiler as my partner works in the woods, although there seem to be as many potential issues with that.
@julianc Ace, thank you, it does seem high to not include radiators and we also have to pay £250 to get them to come round and do a full assessment. It's non-refundable so it's making getting complete quotes look like an expensive business. Is it expected for us to have to pay for one of these every time we get a quote?
@amyfod I didn’t pay for any assessments. I got a free EPC through Eon who were offering a hybrid system. I decided not to proceed with that. I then got several full ASHP quotes. Most did basic assessments based on the EPC. Lots then said I had to change 10mm pipes to radiators. Nooo! Several did video walk around for more detailed quotes. Ecobubl, who were my final installers, did a full assessment to MCS standard. I compared this to the other quotes.
So steps are 1. Get an EPC, but you may have this if recently purchased 2. Seek quotes based on this 3. As questions. Don’t pay £250 or whatever for an assessment until you have finalised your installer and only then if it comes off your final bill
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and Volvo EX30 Ultra Twin Performance electric vehicles with Myenergi Zappi mk1 & Ohme chargers
@amyfod, our supplier used the EPC and did a home visit, where they measured the rooms and asked for some details about materials, insulation, etc. They produced quite a detailed quote with a parts and labour list. I then placed the order and paid a fully refundable 25% deposit, after which they did the MCS survey. There were a couple extra radiators which were covered by a variation notice. Another 25% before they started and the rest on completion. The cost of the MCS survey, calcs and admin was listed as an item on the quote.
An experienced supplier should be able to quote without doing the full survey. As @julianc says, don't pay for the survey up front, unless it's fully refundable.
@amyfod just fyi we've had two quotes 14k and 16k for ecodan 14w plus tank plus 300l cylinder, buffer tank and piping etc. No radiators. We already have underfloor heating. MMSP would cost more but you do get it back. Conscious this seems quite pricey - struggling to get others out to quote though.
Have discovered also that the 14kw ecodan is not the same style as the rest of the range which has been redesigned and labelled as 'ultra quiet'. Anyway, contacted our installers and have said want to see this model in action as trying to work out what they are like from quoted decibel range makes hard work of it. All being well going to see one in action tonight.
@kev-m just wondered what your experience of the ecodan 14kw has been like? My neighbours nearest room is about 12 metres away. I know it's a 'find out for yourself and make your own mind up' situation but since you've got the same model was interested?
@rv3 not trying to dissuade you, but have you looked at the Daikin Altherma 3H HT or the 3M? My 18kW is quiet single fan. Meets planning regs volume <0.63m3
My system £13.7k inc Mixergy 180L & buffer tank. Contact Daikin directly to get local approved installers.
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and Volvo EX30 Ultra Twin Performance electric vehicles with Myenergi Zappi mk1 & Ohme chargers
@RV3 our experience of the Ecodan has been good so far. Noise certainly isn't a problem in the house. Outside next to it, well obviously you can hear it. At the moment, when it's a bit warmer, it's very quiet and I don't think it would carry 12 metres. When it was colder at the start of April and it was working hard, it was definitely louder. However, noise nuisance is really subjective and depends on lots of external factors including ambient noise. It's nowhere near the level of the rattly old pub ACs you see; it's more the level of a modern car ticking over. See what you think when you see one in action but try and get to listen to it when it on full power (not sure how you'd do that though).
The other point worth making is that when it's cold and the ASHP is working hard, you are less likely to be outside or have windows open.
@rv3 I keep intending to record the noise level. But weather has warmed up so the ASHP isn’t running 😊
I think the different suppliers much have similarly competing products. My only thought was one fan vs two. The larger two fan boxes need planning permission whereas the Daikin single fan is within permitted development standards.
Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and Volvo EX30 Ultra Twin Performance electric vehicles with Myenergi Zappi mk1 & Ohme chargers
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 303 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
Recent daily electricity bills in kWh.
By bobflux , 3 minutes ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
I've been watching this with interest as I would like s...
By JohnnyB , 20 minutes ago
-
RE: Aerotherm 12+12kw cascade huge power utilisation
What the hell. There is exactly one reason to use a h...
By bobflux , 22 minutes ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Thanks for such a comprehensive response!!! ...
By errmm , 2 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 6 hours ago
-
As a full price electricity user (nae smart meter signa...
By Abernyte , 10 hours ago
-
Daikin high temperature heat pump
Hello, I have a DAIKIN ERSQ 016AAV1 16KW. I have a BRC2...
By gajolos , 11 hours ago
-
RE: Setback savings - fact or fiction?
I changed the pump power to the actual value to see if ...
By RobS , 13 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
Totally agree. However the manufacturers know that fe...
By JamesPa , 1 day ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 1 day ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 2 days ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 2 days ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 2 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 2 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 2 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 2 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 2 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 2 days ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 3 days ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 3 days ago