Time to seriously consider the Homely System perhaps?
My current heating setup is a Samsung 12Kw High Temperature Quiet heat pump fitted in parallel with a Grant Votex Blue flame oil boiler, all controlled using a Honeywell Resideo TR6_HW smart thermostat.
As the HP was fitted in June of this year I have been going through the process of fine tuning the weather compensation control, now that the outside environment is getting to proper winter temperatures and through testing, finding out the capabilities of my old 1970's / 80's rads, as these were an unknown in the initial calculations.
Following the HeatGeeks procedure and using little Govee thermometers to verify the temperatures in various parts of the house, I was confident that the system was now functioning optimally, house reaching 21C, Good Lady happy until... I reintroduced the smart thermostat into the control loop... Good Lady no longer as happy due to feeling colder than before.
Hmmm I thought, so I placed one of my Govee thermometers right next to the thermostat to monitor what was going on and have now learnt something new!
Smart thermostats, from what I know, have algorithms in their programming to avoid temperature overshoot which is a waste of energy when these devices are being used with fossil fuel systems. As fossil fuel systems push a large amount of heat energy into the building during each cycle, the thermostat compensates for this (in my case) by shortening the cycle time the closer the room temperature gets to the target temperature.
So the result is, when the room temperature reaches approximately 1C to 1.5C within range of the target temperature, the thermostat changes its behaviour by reducing the cycle time.
Now this has the effect on my oil boiler of slowing the heating rate to 0.5C / hour for the final 3 hours of heating, meaning the room finally gets to 21C within 30 minutes of going to bed, so I have now adjusted the start time to enable most of the evening to be 21C.
However as we know HP's are not so great at producing large quantities of heat quickly per cycle and need to run for longer times per cycle to achieve the required flow temperatures. This was not so in my case, the thermostat throttles back the HP to the point the flow temperatures only get within 4 to 5 degrees of the required temperature on each cycle, resulting in less heat to the room and a cold Wife.
Two options were open to me at this point, increase the weather compensation curve to hopefully cater for this but completely ruin the COP or make the thermostat think its colder than it is. Opting for option 2 I adjusted the temperature offset to -1C to see how that helped which I am pleased to say, as a temporary work around, has the desired effect. The thermostat keeps the longer cycle times until the room gets to within 0.5C before slowing the rate meaning the final stage now only takes 2 hours not the 6 hours I was experiencing with the HP.
This leaves me with the question, are current smart thermostats on the market actually suitable for HP's? Is it time to seriously consider a control system such as the Homely?
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
Posted by: @technogeekMy current heating setup is a Samsung 12Kw High Temperature Quiet heat pump fitted in parallel with a Grant Votex Blue flame oil boiler, all controlled using a Honeywell Resideo TR6_HW smart thermostat.
As the HP was fitted in June of this year I have been going through the process of fine tuning the weather compensation control, now that the outside environment is getting to proper winter temperatures and through testing, finding out the capabilities of my old 1970's / 80's rads, as these were an unknown in the initial calculations.
Following the HeatGeeks procedure and using little Govee thermometers to verify the temperatures in various parts of the house, I was confident that the system was now functioning optimally, house reaching 21C, Good Lady happy until... I reintroduced the smart thermostat into the control loop... Good Lady no longer as happy due to feeling colder than before.
Hmmm I thought, so I placed one of my Govee thermometers right next to the thermostat to monitor what was going on and have now learnt something new!
Smart thermostats, from what I know, have algorithms in their programming to avoid temperature overshoot which is a waste of energy when these devices are being used with fossil fuel systems. As fossil fuel systems push a large amount of heat energy into the building during each cycle, the thermostat compensates for this (in my case) by shortening the cycle time the closer the room temperature gets to the target temperature.
So the result is, when the room temperature reaches approximately 1C to 1.5C within range of the target temperature, the thermostat changes its behaviour by reducing the cycle time.Now this has the effect on my oil boiler of slowing the heating rate to 0.5C / hour for the final 3 hours of heating, meaning the room finally gets to 21C within 30 minutes of going to bed, so I have now adjusted the start time to enable most of the evening to be 21C.
However as we know HP's are not so great at producing large quantities of heat quickly per cycle and need to run for longer times per cycle to achieve the required flow temperatures. This was not so in my case, the thermostat throttles back the HP to the point the flow temperatures only get within 4 to 5 degrees of the required temperature on each cycle, resulting in less heat to the room and a cold Wife.Two options were open to me at this point, increase the weather compensation curve to hopefully cater for this but completely ruin the COP or make the thermostat think its colder than it is. Opting for option 2 I adjusted the temperature offset to -1C to see how that helped which I am pleased to say, as a temporary work around, has the desired effect. The thermostat keeps the longer cycle times until the room gets to within 0.5C before slowing the rate meaning the final stage now only takes 2 hours not the 6 hours I was experiencing with the HP.
This leaves me with the question, are current smart thermostats on the market actually suitable for HP's? Is it time to seriously consider a control system such as the Homely?
Or you could just use the controller that was designed to control the heat pump. Simples. 😎
@derek-m I wish it was! 🤣 Sadly due to the HP and controller being located within the outside boiler room, running the data cable for the built in thermostat to the lounge was not an option plus the Resideo is still needed when I use the oil boiler 🙁
5 Bedroom House in Cambridgeshire, double glazing, 300mm loft insulation and cavity wall insulation
Design temperature 21C @ OAT -2C = 10.2Kw heat loss
Bivalent system containing:
12Kw Samsung High Temperature Quiet (Gen 6) heat pump
26Kw Grant Blue Flame Oil Boiler
All controlled with Honeywell Home smart thermostat
@Technogeek I've recently been attempting to characterise my gas-fired central heating and radiators prior to a possible transition to an ASHP and stumbled across the same problem with my 'smart' thermostat. I had turned down the boiler output - which has control algorithms of its own - removed the overnight temperature setback and found we were variously throwing on extra clothes or ripping them off once the outside temperature started going low. The situation varied from room to room, probably not helped by unbalanced radiators and the odd 30 year old TRV deciding to stick again. I suppose it may help convince my good lady that we really do need to replace what we have 😉 .
@derek-m Admittedly, we have only had the Homely smart controller for a few weeks but it seems to have settled down now and is keeping the house at the temperatures we require at different times - without any problems; the radiators seem to be warm most of the time now and our consumption now when the temp. has dropped to 1 - 3 degrees most days is lower than when we were at 8 - 9 degrees and using the Heatmiser Neo on/off stat. I had spent some time carefully tweeking the LWT and WC settings on our Daikin EDL08 hp to get the best out of the system - but Homely has improved on this considerably! Well worth considering I think. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
- 26 Forums
- 2,204 Topics
- 48.6 K Posts
- 20 Online
- 5,859 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Help me keep the faith with my air source heat pump installation
@jamespa the flexis have been in a horizontal position ...
By AdamK , 7 hours ago
-
From the consumer's viewpoint, he's still going to cons...
By Transparent , 7 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Hi, thanks for the reply. The air is from the domestic ...
By Get , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Perhaps they didn't significantly rewrite the algorithm...
By JamesPa , 8 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick maybe pickup this ChatGPT conversation an...
By Tim441 , 10 hours ago
-
RE: How can I programme a setback for my Samsung Gen6 8kW heat pump?
Yes, and probably also Adia although the latter has a m...
By JamesPa , 10 hours ago
-
@editor I am all in favour of provocati...
By GrahamF , 14 hours ago
-
@editor lol. I wish. They told me to switch everything ...
By bontwoody , 15 hours ago
-
RE: How to Understand Wiring Up a Heat Pump
Morning, On top of what everyone else I would deffo loo...
By Grantmethestrength , 20 hours ago
-
RE: Sizing a heat pump: Save me from my headache
Got the results back from the one we’re ...
By Mikeatthezoo , 1 day ago
-
RE: Renewables & Heat Pumps in the News
Thanks Lucia. I'll set aside some time to go through th...
By Transparent , 3 days ago
-
RE: Do I just go with the lowest quote for my heat pump?
Seems to be settling better now I'll leave it alone
By Jancold , 3 days ago
-
RE: Bosch CS5800i 5kW - Experience So Far
We do like the exhaust air heat pump as a centralised M...
By Steelbadger , 3 days ago
-
RE: Solar Thermal DHW and ASHP
@kenbone how is your battery holding up Ken? Still goin...
By Mars , 3 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Old Samsung R410a unit 9kw, modbused controlled, let Ha...
By KenBone , 3 days ago
-
RE: Replacement Inverter for old FIT system
@bontwoody I have a single string 3kW solar AC inverter...
By Old_Scientist , 3 days ago
-
Octopus removed our gas meter for free a couple of year...
By robl , 3 days ago