Significance of delta betweeen flow and return temperature
Hi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Mitsubishi Ecodan 11.2kW ASHP
Posted by: @greekgoddjHi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Hi,
The simple answer is yes, the delta T of the flow and return water does impact the efficiency and energy use of a heat pump.
It takes a defined amount of energy to heat a specified amount of water by 1C. So if the water is entering the heat pump at 20C and exiting at 40C, then it will have required 4 times more energy to heat the water than if it was entering at 35C and exiting at 40C.
Picking up this significance of deltaT topic again but from the opposite side.
My system is an Daikin Altherma 11kw Monobloc, described in other threads. I have it working with weather comp, with the internal controller modulating the leaving water temperature. It's working alright, COP about 3.2, but I notice after the overnight setback, the pump runs nicely with a deltaT around 5C, and if I record the meters (fitted as part of a trial) the COP for this period is up above 3.6, but as the house reaches temperature a bit of modulation happens reducing the leaving water temperature gradually, but then leaving and return water temperatures end up being very similar, often the same for several hours, so no deltaT. The house is warm enough, so there is no heat demand in the property but the pump keeps running in this tick over state, and this drops the COP drastically because the ASHP is using electricity but not putting heat in to the property. So that's the scenario. Should I be trying to achieve a greater deltaT through the radiators? I could wind in the locksheilds on my rads, whilst keeping the system balanced, to reduce flow and allow a greater temperature drop across them? This is counter intuitive though as I've read that high flow rates are better for heat pumps.
Thoughts appreciated about whether I'm over thinking this one.
@adaml I don’t have the option to set a maximum modulation value, for some reason that menu option doesn’t show. It’s the 11kw Altherma monobloc, the last gen, not the latest one.
The curve is 44C/-5 and 23C/15
@adaml I worked it, I scrolled through the overview settings, I’d left this lot alone until now.
8-06 looks to be 3. Have I read that correctly? Is that a sensible number? I’m guessing it’s not enough. Today with the solar gain the house is up at nearly 23C, with the LWT at around 30C.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 191 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Electricity price predictions
@lucia Absolutely. And all this talk about being rea...
By Batpred , 5 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
And I thought I was the one with the taxi on speed dial...
By Majordennisbloodnok , 7 hours ago
-
RE: Solar panels on side of house to heat water
@paultheheating We are looking into PV panels at the...
By Batpred , 10 hours ago
-
@jamespa They are indeed mysterious devices!!! I have o...
By Toodles , 12 hours ago
-
RE: Heat Pump Training vs. Real-World Installation
Congratulations on passing the course. The observation...
By Max Abbey , 13 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
@sim0n0 Here's a reply to help you out. As a owner ...
By trebor12345 , 15 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
The engineer came yesterday and as the rooms were ok te...
By AdamK , 15 hours ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
@jamespa Can I check something that I done some weeks a...
By trebor12345 , 16 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
The problem I see with A2A (and I'm interested if there...
By Temperature_Gradient , 17 hours ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
@temperature_gradient I specifically explained to my po...
By Toodles , 17 hours ago
-
RE: Grant Aerona Short Cycling
@damonc I was refering to the 'standard' energy sticker...
By MikeFl , 20 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@hcas where do I find Havenwise Support? On...
By Morgan , 21 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
We recently (Aug 25) had a Grant Aeorana 3 installed un...
By GA3_USR , 1 day ago
-
RE: Grant Aerona circulation/system pump staying on
My AERONA 3 circulation pump runs constantly whatever t...
By damonc , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Thanks, @sheriff-fatman. Happy for you to search any po...
By Majordennisbloodnok , 2 days ago
-
Thanks, @cathoderay. I was aware of some changes to ...
By Majordennisbloodnok , 2 days ago
-
RE: Trying to understand my Nibe F1245
@greenlight Many thanks for the information, it's set m...
By Chris12 , 2 days ago
-
This is what I answered, I really have no hope: "......
By Batpred , 2 days ago
-