Significance of delta betweeen flow and return temperature
Hi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Mitsubishi Ecodan 11.2kW ASHP
Posted by: @greekgoddjHi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Hi,
The simple answer is yes, the delta T of the flow and return water does impact the efficiency and energy use of a heat pump.
It takes a defined amount of energy to heat a specified amount of water by 1C. So if the water is entering the heat pump at 20C and exiting at 40C, then it will have required 4 times more energy to heat the water than if it was entering at 35C and exiting at 40C.
Picking up this significance of deltaT topic again but from the opposite side.
My system is an Daikin Altherma 11kw Monobloc, described in other threads. I have it working with weather comp, with the internal controller modulating the leaving water temperature. It's working alright, COP about 3.2, but I notice after the overnight setback, the pump runs nicely with a deltaT around 5C, and if I record the meters (fitted as part of a trial) the COP for this period is up above 3.6, but as the house reaches temperature a bit of modulation happens reducing the leaving water temperature gradually, but then leaving and return water temperatures end up being very similar, often the same for several hours, so no deltaT. The house is warm enough, so there is no heat demand in the property but the pump keeps running in this tick over state, and this drops the COP drastically because the ASHP is using electricity but not putting heat in to the property. So that's the scenario. Should I be trying to achieve a greater deltaT through the radiators? I could wind in the locksheilds on my rads, whilst keeping the system balanced, to reduce flow and allow a greater temperature drop across them? This is counter intuitive though as I've read that high flow rates are better for heat pumps.
Thoughts appreciated about whether I'm over thinking this one.
@adaml I don’t have the option to set a maximum modulation value, for some reason that menu option doesn’t show. It’s the 11kw Altherma monobloc, the last gen, not the latest one.
The curve is 44C/-5 and 23C/15
@adaml I worked it, I scrolled through the overview settings, I’d left this lot alone until now.
8-06 looks to be 3. Have I read that correctly? Is that a sensible number? I’m guessing it’s not enough. Today with the solar gain the house is up at nearly 23C, with the LWT at around 30C.
- 26 Forums
- 2,265 Topics
- 50.6 K Posts
- 129 Online
- 5,924 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
@benson I checked the last week of data and i must say ...
By Mosibi , 38 minutes ago
-
RE: My DIY Heat Pump installation
Its what ive used. I know some people choose ones which...
By bontwoody , 4 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Did @mark-hall really just say that?! 🤯 He drop...
By Mars , 5 hours ago
-
RE: Grant 13kW Aerona3 - issues getting zones to temp
Oh completely, he even said without the hydrau...
By Crimson , 5 hours ago
-
We privatised electricity (back in the 80s I think) so ...
By JamesPa , 6 hours ago
-
RE: Electricity price predictions
So he must have a good team helping him in this.. ...
By Batpred , 9 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
There is no such thing as a silly question! @toodles ...
By JamesPa , 12 hours ago
-
RE: UFH downstairs and radiators upstairs balancing question
Isn't this a great example of KISS!
By JamesPa , 12 hours ago
-
RE: Who has a V2G EV installation
Would that be a Chint RCD perhaps? Have a look at thi...
By Transparent , 13 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
11.2kW Ecodan Manufacturer: Misubishi Model: PUZ-WM...
By DRB01 , 1 day ago
-
RE: Homely asking about Solar Panels.
@majordennisbloodnok I will report back with any develo...
By Toodles , 1 day ago
-
RE: Mediation with RECC, what's your experience?
@editor Thank you, I really appreciate it! I've made ...
By TreeWizard , 1 day ago
-
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
Are you able to post a photo of that 180-litre cylinder...
By Transparent , 1 day ago
-
Renewable heating and renewable energy are very jargon ...
By Majordennisbloodnok , 1 day ago
-
Agreed. It doesn't take all that much maintenance to ke...
By Majordennisbloodnok , 1 day ago
-
RE: Oil Boiler & Heat Pump Hybrid System
OK. Got it. As a fellow rural West Country resident, ...
By Transparent , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
Ok so that seems to be the key point namely only mcs ca...
By JamesPa , 2 days ago