Significance of delta betweeen flow and return temperature
Hi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Mitsubishi Ecodan 11.2kW ASHP
Posted by: @greekgoddjHi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Hi,
The simple answer is yes, the delta T of the flow and return water does impact the efficiency and energy use of a heat pump.
It takes a defined amount of energy to heat a specified amount of water by 1C. So if the water is entering the heat pump at 20C and exiting at 40C, then it will have required 4 times more energy to heat the water than if it was entering at 35C and exiting at 40C.
Picking up this significance of deltaT topic again but from the opposite side.
My system is an Daikin Altherma 11kw Monobloc, described in other threads. I have it working with weather comp, with the internal controller modulating the leaving water temperature. It's working alright, COP about 3.2, but I notice after the overnight setback, the pump runs nicely with a deltaT around 5C, and if I record the meters (fitted as part of a trial) the COP for this period is up above 3.6, but as the house reaches temperature a bit of modulation happens reducing the leaving water temperature gradually, but then leaving and return water temperatures end up being very similar, often the same for several hours, so no deltaT. The house is warm enough, so there is no heat demand in the property but the pump keeps running in this tick over state, and this drops the COP drastically because the ASHP is using electricity but not putting heat in to the property. So that's the scenario. Should I be trying to achieve a greater deltaT through the radiators? I could wind in the locksheilds on my rads, whilst keeping the system balanced, to reduce flow and allow a greater temperature drop across them? This is counter intuitive though as I've read that high flow rates are better for heat pumps.
Thoughts appreciated about whether I'm over thinking this one.
@adaml I don’t have the option to set a maximum modulation value, for some reason that menu option doesn’t show. It’s the 11kw Altherma monobloc, the last gen, not the latest one.
The curve is 44C/-5 and 23C/15
@adaml I worked it, I scrolled through the overview settings, I’d left this lot alone until now.
8-06 looks to be 3. Have I read that correctly? Is that a sensible number? I’m guessing it’s not enough. Today with the solar gain the house is up at nearly 23C, with the LWT at around 30C.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 43 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
Thanks. No buffer. Def controlled by the Samsung. Therm...
By Profzarkov , 56 minutes ago
-
RE: Boiling Mad: Exposing Radiatorgate
Hi @Rob, I’d be more than happy to contribute. I have ...
By DREI , 1 hour ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@andris a great year - very happy with our system
By Profzarkov , 3 hours ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
A bit of a follow up on the progress of the Ecodan pump...
By ThunderMink , 4 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
After our rather lengthy meander off piste, I thought I...
By GrahamF , 5 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump - to collect the IAT/OAT data, can I sugges...
By cathodeRay , 6 hours ago
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 16 hours ago
-
My Samsung Gen6 (probably same controller as yours) onl...
By Old_Scientist , 1 day ago
-
@drei When I was in local government we were of cours...
By JamesPa , 1 day ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 1 day ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 2 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 2 days ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 2 days ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 3 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 3 days ago