Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Significance of delta betweeen flow and return temperature
Hi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Mitsubishi Ecodan 11.2kW ASHP
Posted by: @greekgoddjHi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Hi,
The simple answer is yes, the delta T of the flow and return water does impact the efficiency and energy use of a heat pump.
It takes a defined amount of energy to heat a specified amount of water by 1C. So if the water is entering the heat pump at 20C and exiting at 40C, then it will have required 4 times more energy to heat the water than if it was entering at 35C and exiting at 40C.
Picking up this significance of deltaT topic again but from the opposite side.
My system is an Daikin Altherma 11kw Monobloc, described in other threads. I have it working with weather comp, with the internal controller modulating the leaving water temperature. It's working alright, COP about 3.2, but I notice after the overnight setback, the pump runs nicely with a deltaT around 5C, and if I record the meters (fitted as part of a trial) the COP for this period is up above 3.6, but as the house reaches temperature a bit of modulation happens reducing the leaving water temperature gradually, but then leaving and return water temperatures end up being very similar, often the same for several hours, so no deltaT. The house is warm enough, so there is no heat demand in the property but the pump keeps running in this tick over state, and this drops the COP drastically because the ASHP is using electricity but not putting heat in to the property. So that's the scenario. Should I be trying to achieve a greater deltaT through the radiators? I could wind in the locksheilds on my rads, whilst keeping the system balanced, to reduce flow and allow a greater temperature drop across them? This is counter intuitive though as I've read that high flow rates are better for heat pumps.
Thoughts appreciated about whether I'm over thinking this one.
@adaml I don’t have the option to set a maximum modulation value, for some reason that menu option doesn’t show. It’s the 11kw Altherma monobloc, the last gen, not the latest one.
The curve is 44C/-5 and 23C/15
@adaml I worked it, I scrolled through the overview settings, I’d left this lot alone until now.
8-06 looks to be 3. Have I read that correctly? Is that a sensible number? I’m guessing it’s not enough. Today with the solar gain the house is up at nearly 23C, with the LWT at around 30C.
- 27 Forums
- 2,539 Topics
- 59.1 K Posts
- 287 Online
- 6,818 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Balancing is a long process and its possible to mess th...
By JamesPa , 4 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 5 hours ago
-
Thanks everyone for the help, Havenwise now diasbled. q...
By Boycey , 7 hours ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli Depending on whether you can get an EV tariff, I...
By ChandyKris , 8 hours ago
-
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 10 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@technogeek I think you are correct, but, it didn’t inf...
By Papahuhu , 10 hours ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 10 hours ago
-
@Mars at the time of writing heating oil is £1.28 / ltr...
By TechnoGeek , 11 hours ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 14 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 14 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
The setup for this is a Samsung Modbus card. Connected ...
By antonical , 15 hours ago
-
RE: Forum updates, announcements & issues
@davidalgarve, if the emails are more than roughly a mo...
By Mars , 16 hours ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 16 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 17 hours ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 1 day ago
-
RE: Setback savings - fact or fiction?
The answer was in two parts in my reply, the second par...
By RobS , 1 day ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 1 day ago
-
Ecodan control return to Melpump from Havenwise trial. settings check
Hi, Just got control back after being on the hav...
By Boycey , 1 day ago
-
RE: Refrigerant R32, is it now banned in the EU from 1st Jan 2027 for monobloc ASHPs?
I wonder if heat pump manufacturers will tone these sit...
By JamesPa , 1 day ago
-
RE: Who’s Caved and Switched the Heating On Already?
@editor yesterday we used 12kW of electricity for heat,...
By Judith , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
Loss assessments can be a very serious case of GIGO. I...
By JamesPa , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
@jamespa Just bizarre. This is our data. I really don't...
By antonical , 2 days ago
-
RE: Mitsubishi Ecodan 11.2kW review
I think you said its an 11.2kW model and your house is ...
By JamesPa , 2 days ago