Significance of delta betweeen flow and return temperature
Hi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Mitsubishi Ecodan 11.2kW ASHP
Posted by: @greekgoddjHi everyone,
I have been wondering about the following. Does the delta between the flow and return temperature have an impact on the efficiency/energy use of the ASHP? For example, assuming a ASHP that is focused on heating the flow to 40C, does it matter if what returns is 20C or 30C? In other words, if it is heating 1 room or 5 rooms, as long as the ASHP is aiming for a certain flow temperature (whether said temperature is manually set or driven by compensation curve), is the workload on the ASHP the same?
Thanks
Hi,
The simple answer is yes, the delta T of the flow and return water does impact the efficiency and energy use of a heat pump.
It takes a defined amount of energy to heat a specified amount of water by 1C. So if the water is entering the heat pump at 20C and exiting at 40C, then it will have required 4 times more energy to heat the water than if it was entering at 35C and exiting at 40C.
Picking up this significance of deltaT topic again but from the opposite side.
My system is an Daikin Altherma 11kw Monobloc, described in other threads. I have it working with weather comp, with the internal controller modulating the leaving water temperature. It's working alright, COP about 3.2, but I notice after the overnight setback, the pump runs nicely with a deltaT around 5C, and if I record the meters (fitted as part of a trial) the COP for this period is up above 3.6, but as the house reaches temperature a bit of modulation happens reducing the leaving water temperature gradually, but then leaving and return water temperatures end up being very similar, often the same for several hours, so no deltaT. The house is warm enough, so there is no heat demand in the property but the pump keeps running in this tick over state, and this drops the COP drastically because the ASHP is using electricity but not putting heat in to the property. So that's the scenario. Should I be trying to achieve a greater deltaT through the radiators? I could wind in the locksheilds on my rads, whilst keeping the system balanced, to reduce flow and allow a greater temperature drop across them? This is counter intuitive though as I've read that high flow rates are better for heat pumps.
Thoughts appreciated about whether I'm over thinking this one.
@adaml I don’t have the option to set a maximum modulation value, for some reason that menu option doesn’t show. It’s the 11kw Altherma monobloc, the last gen, not the latest one.
The curve is 44C/-5 and 23C/15
@adaml I worked it, I scrolled through the overview settings, I’d left this lot alone until now.
8-06 looks to be 3. Have I read that correctly? Is that a sensible number? I’m guessing it’s not enough. Today with the solar gain the house is up at nearly 23C, with the LWT at around 30C.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 259 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 13 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 23 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 2 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 18 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 23 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 24 hours ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago