Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Scottish Borders ASHP
Hello,
We are currently upgrading windows and insulation as well as improving draughtproofing on our 100 year old stone semi detached house. Meanwhile we are getting quotes for an ASHP with UFH downstairs.
Reading this forum I'm pretty sold on getting a Mixergy tank. Can anyone advise on what size a Mixergy tank would be required when a 200l normal tank would be usually specified? We are a family of 4 with one shower/bath. Some installers seems reserved about fitting a third party tank.
We need some electrical work done as well. Has anyone had their main fuse upgraded to accommodate an ASHP? What other electrical stumbling blocks might we encounter?
We currently have a mains gas combi which is very underwhelming in the cold months. The radiators throughout the house don't cut it either. Very small bore pipes leading off main pipes from the boiler.
The majority of the ground floor is suspended timber floor which we intend to insulate and then have the UFH installed, board and tile/engineered wood over. Reading this forum, Stelrad K3 compact rads seem like a good choice upstairs.
I'm thinking we will need lots of new pipe work to reduce the work on the pump as the current feed to the rads is so small. Did you use mostly plastic or copper pipe on your system? This seems to be fairly important due to the difference in internal diameter. What diameter pipe did you have installed?
Our EPC report says that our demand is 25,665kWh for space heating and 2,000KWh for hot water per year.
The goal is to eliminate gas from our home and hopefully generate some of our own electricity through solar. We hope to drive down energy costs in the long run. Is there further heat loss calculations you would recommend?
Thank you to all who contribute to this forum, its a wealth of knowledge and ideas.
@Gordonville, it sounds like you're going to end up with a completely new system, which it what we had. We started with no central heating at all. UFH works well with an ASHP but you don't need it. It is a different sort of heating and is also quite expensive to install so don't discount radiators. We used all standard 15mm copper pipes in our system.
Our fuse was OK as it was, because our supply was previously running 8 storage heaters. You do need to ask your Distribution Network Operator (DNO) before you install a ASHP; they will tell you whether the incoming supply is up to it (it probably will be). Upgrading the fuse is then not a big job if needed.
That's quite a high heat demand for a semi but hopefully your insulation work will reduce it. You will end up paying more than with gas but I'm sure you know that.
You can download the MCS heat loss calculator here.
https://mcscertified.com/mcs-launch-new-improved-heat-pump-calculator/
Do check the permitted development rules for ASHPs as the Scottish ones are a little more restrictive on where you can site the ASHP.
Good luck and keep us up to date with progress.
@gordonville, the one thing that I can comment on, and that you've already highlighted, is the bore and rad size. It took us a while to get the bottom of why the southern end of the house wasn't coming to temperature and we finally ascertained that the reduced pipework work from the utility room where our tank is to the southern portion of the house was causing the issues, so the upgrade to K3 rads from Stelrad was a game changer. The true test is still coming, but I'm confident we'll be far warmer this winter.
Have you received any quotes yet, and do you have a brand preference at this stage?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Thank you for the replies. That MCS heat loss calculator looks like a really powerful tool. I’m kind of concerned that neither of the quotes we have had go in to such detail.
We had one quote for a Vaillent 12kW high temp unit and tank with UFH.
Another quote was for a Nibe F2040 12kW with Telford tank and UFH.
Both came in at just over 20K. Seems like too much. We are learning as we go and this forum really helps with that.
I used the EST search bar to fire out loads of further quote requests and have had a couple of replies. It has helped me get the appropriate information together. Lots of companies seem very busy. There is probably a shortage of parts at the moment too.
In terms of brands I do like the idea of Nibe but they seem much more expensive and I wonder what you really get for that extra cash.
I like that they are heat pump specialists and have been in business for a good amount of time. Being Scandinavian made also appeals to me.
I am wary of standard boiler manufacturers coming out with heat pumps. This is perhaps in justified. Honestly, I don’t know which brand would be the best balance of cost/performance/warrenty etc. What is your views on this? Most installers probably have a preferred brand and most customers probably prefer their own install i guess.
I have an electrician coming round soon to look at a rewire so hopefully he will help with the DNO. I’ll attach a picture of the incomer here. Nothing on it to say what the rating currently is.
As for the UFH, I do like our floorboards. To properly insulate the house I think these will have to be lifted anyway. I’m not totally against the rads idea though. The worry is that they will have to huge but maybe that is an old way of looking at it.
@gordonville Both are good units, the Valiant controller is very complicated whilst the Nibe unit is much easier to operate and has a built-in online connected through Wi-Fi. I have installed both, but prefer the Nibe unit. (they are similar in price at source and both have excellent backup)
The installers should, according to MCS supply you with full room by room heat loss calculations with an emitter schedule (under floor or radiators) stating the flow temperature at the design temperature (around -3 or -4 for you), It must also include evidence that the heat pump will supply sufficient energy at this temperature without assistance as air source heat pumps loose performance and output at lower temperatures.
If the installers cannot supply this, look for another one.
Correctly sized radiators can supply excellent performance and comfort, but the design temperature should not be greater than 45 Deg C. Under floor should have a design flow temperature of 35 Deg C, a pipe spacing of 100mm usually suffices.
We are very busy at the moment, there is generally not a problem with supply, but people are tying to get the installations done before the RHI finishes in March next year, we have customers that we quoted 3 years ago now requesting installations.
I hope this helps.
@gordonville I posted the heat loss calculator and ASHP selector from freedom heat pumps on here a while ago. Have a look, it should help you in cross checking any quotes
-
How to Understand Wiring Up a Heat Pump
5 months ago
-
How to Zone with a Single Room with UFH
6 months ago
-
UFH and ASHPs
10 months ago
-
Heat Pump, DHW, UFH and Radiator Install
1 year ago
-
Retrofitting UFH with a heat pump already installed
2 years ago
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 311 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Indeed we don’t! Much though I wish to be loy...
By Toodles , 52 minutes ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 2 hours ago
-
As a full price electricity user (nae smart meter signa...
By Abernyte , 6 hours ago
-
Aerotherm 12+12kw cascade huge power utilisation
Looking for a little bit of advice. new inst...
By Hamish_mckay , 7 hours ago
-
Daikin high temperature heat pump
Hello, I have a DAIKIN ERSQ 016AAV1 16KW. I have a BRC2...
By gajolos , 7 hours ago
-
RE: Setback savings - fact or fiction?
I changed the pump power to the actual value to see if ...
By RobS , 9 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
@majordennisbloodnok Thanks I hope it helps someone. St...
By antonical , 21 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
Totally agree. However the manufacturers know that fe...
By JamesPa , 22 hours ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 1 day ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 1 day ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 1 day ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 1 day ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 1 day ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 2 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 2 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 2 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 2 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 2 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 2 days ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Sorry to hear that but I'm not surprised TBH. Stratifi...
By JamesPa , 2 days ago
-
RE: Say hello and introduce yourself
@pt151 welcome to the forums, and looking forward to he...
By Mars , 3 days ago
-
Samsung Gen 7 16kW Integrated unit Modbus monitoring
Looking for some assistance to get modbus monitoring wo...
By antonical , 3 days ago