Samsung Launches the EHS Mono HT Quiet – A High Temperature, Low Noise Heat Pump Ideal for Home and Building Renovations
@heacol thanks . I read your recent article on here with great interest, and also your linkedin post about your conference presentation, I'm waiting with bated breath for your full write up. given that you don't use buffers or plates or any form of separation, that implies to me you may have accepted a lower flow rate than that implied by (say) 16kw@DT5 (for a large older house), in which case you may be running a wider DT? I'm also really interested in your detailed thoughts on control. Do you site the heat pump's controller in a location where there is always demand? or am I leaping too far ahead and should just wait for your write up? my system is still a single loop gas boiler right now so I've all these decisions to take.
@hughf thanks, I had been zeroing in on daikin as a likely candidate as those DT settings are indeed there in the manual, and I find it one of the better written manuals. annoying that the new samsung still doesn't have a published set of manuals yet.
I really appreciate the help, any of you guys fancy installing a system in milton keynes? I'm really struggling to find an installer that I'm comfortable to give the work to. Met plenty of "plumbers" who know less about heat engineering than I do (but are far better pipework fitters) and so run away once a conversation about system design is initiated...
PWM pumps, I've been wanting to change my heat-only gas boiler's pump (grundfos alpha2) to a PWM one for ages. at fixed max speed it heats the house but is really noisy , and when demand is low the pipes resonate due to the TRV small openings. in PP3 mode its super quiet but not enough flow for the whole house on a cold day. I do manual PWM by running up there and pressing the button if its below zero...:(. I have the means of generating a PWM control signal based on heating load - evohome radiator heads running into home-assistant through ramses-RF gives me the number for % heat demand for the house (and/or for every single room) which can be mapped to a PWM level, an ESP32 board will do the hardware part - but tracking down a PWM pump (with control cable) in the uk domestic market is proving challenging for me (as far as I can tell the commonly available grundfos UPS3 is PWM capable, but no-one uses or sells the PWM parts in the UK...)
cheers
Ian
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank all you need is a pwm cable. As long as the pump has two sockets on it, it’s pwm capable.
You could even just jam 3 crimp connectors in there if you can’t get a cable.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@iancalderbank PM me and I will see if I can help.
Director at Heacol | Expert Heat Pump Consultant | Book a one-to-one consultation for pre- and post-installation advice, troubleshooting and system optimisation.
Posted by: @iancalderbank@heacol thanks . I read your recent article on here with great interest, and also your linkedin post about your conference presentation, I'm waiting with bated breath for your full write up. given that you don't use buffers or plates or any form of separation, that implies to me you may have accepted a lower flow rate than that implied by (say) 16kw@DT5 (for a large older house), in which case you may be running a wider DT? I'm also really interested in your detailed thoughts on control. Do you site the heat pump's controller in a location where there is always demand? or am I leaping too far ahead and should just wait for your write up? my system is still a single loop gas boiler right now so I've all these decisions to take.
@hughf thanks, I had been zeroing in on daikin as a likely candidate as those DT settings are indeed there in the manual, and I find it one of the better written manuals. annoying that the new samsung still doesn't have a published set of manuals yet.
I really appreciate the help, any of you guys fancy installing a system in milton keynes? I'm really struggling to find an installer that I'm comfortable to give the work to. Met plenty of "plumbers" who know less about heat engineering than I do (but are far better pipework fitters) and so run away once a conversation about system design is initiated...
PWM pumps, I've been wanting to change my heat-only gas boiler's pump (grundfos alpha2) to a PWM one for ages. at fixed max speed it heats the house but is really noisy , and when demand is low the pipes resonate due to the TRV small openings. in PP3 mode its super quiet but not enough flow for the whole house on a cold day. I do manual PWM by running up there and pressing the button if its below zero...:(. I have the means of generating a PWM control signal based on heating load - evohome radiator heads running into home-assistant through ramses-RF gives me the number for % heat demand for the house (and/or for every single room) which can be mapped to a PWM level, an ESP32 board will do the hardware part - but tracking down a PWM pump (with control cable) in the uk domestic market is proving challenging for me (as far as I can tell the commonly available grundfos UPS3 is PWM capable, but no-one uses or sells the PWM parts in the UK...)
cheers
Ian
Just Google 'pwm cable for grundfos pumps' and you will find a selection of suitable cables on offer.
Thanks very much all! Just found the MCS link for the unit sold by Midsummer....link below for anyone else interested.
Product directory - MCS (mcscertified.com)
Gen6 SCOPs:
@35°C | 4.55 |
@40°C | 4.25 |
@45°C | 3.95 |
@50°C | 3.68 |
@55°C | 3.40 |
New HT SCOPS:
35°C | 4.75 |
36°C | 4.69 |
37°C | 4.64 |
38°C | 4.58 |
39°C | 4.53 |
40°C | 4.47 |
41°C | 4.42 |
42°C | 4.36 |
43°C | 4.31 |
44°C | 4.25 |
45°C | 4.2 |
46°C | 4.14 |
47°C | 4.09 |
48°C | 4.03 |
49°C | 3.97 |
50°C | 3.92 |
@iancalderbank - I'm in a similar position to you in many ways: a (now retired electronics) engineer in Milton Keynes looking to replace a gas boiler in a large unconventional property. The property was built in 1990 but the boiler was subsequently replaced by a BG gas safe trained plumber. Although the system as originally installed appears to have had some weather compensation, that went out of the window along with all idea of a coherent system design. The present boiler is, I believe, over-specified, grossly inefficient and is ageing before it's time (it is ten years old). Now seems to be a good time to consider all replacement options. It's a large system comprising 18 radiators and a complex blend of pipe gauges. I'm not keen on learning another skill myself so I really need to involve a professional heating engineer who knows their onions. Have you been able to identify anyone locally who could fit the bill? I'm happy for you to message privately if you prefer.
Ian
- 26 Forums
- 2,158 Topics
- 47.4 K Posts
- 36 Online
- 5,736 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
@pash44pump Referring to the problem of rooms with diff...
By Tasos , 1 hour ago
-
RE: Help me keep the faith with my air source heat pump installation
Er true, it should have read l/hr!
By JamesPa , 2 hours ago
-
RE: Big Changes Coming to Our Heat Pump System
@old_scientist, our system was royally bodged six years...
By Mars , 2 hours ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
@scalextrix You're assuming that the source of the comm...
By Transparent , 2 hours ago
-
@jamespa thanks, I appreciate the offer. For n...
By DREI , 16 hours ago
-
RE: Who’s Caved and Switched the Heating On Already?
I have 3 women in the house, 2 little ones, so my heati...
By DREI , 21 hours ago
-
@damon thanks. I will do as you suggest. Hopefully I wi...
By bontwoody , 22 hours ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@dgclimatecontrol I attach the responses from 2 potenti...
By pash44pump , 2 days ago
-
RE: Buffers, hot water and cooling
@dgclimatecontrol thanks, that's helpful.
By JamesPa , 3 days ago
-
RE: Failing heat pump system - seeking thoughts on a rebuild
I realise im overdue an update on my situation. first...
By Cleardene-ashp , 3 days ago
-
RE: Replacing Worcester oil boiler with an ASHP
@toodles thanks. I was told by the engineer that this h...
By JulianC , 3 days ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
A week later, I'm finally picking up this comment... ...
By Transparent , 3 days ago
-
RE: COP is not the only measure of efficiency
We keep all our TRVs fully open using the whole house a...
By Old_Scientist , 3 days ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
I am pleased to say at 4pm today we have added another ...
By ASHP-BOBBA , 4 days ago
-
RE: Renewables & Heat Pumps in the News
To unpack this a little.... 1) how many of us in this...
By Lucia , 4 days ago
-
RE: Vaillant aroTherm Plus 10kW thoughts?
@realevil the fans and fan speed / coil size (height, w...
By ASHP-BOBBA , 5 days ago
-
RE: Mitsubishi Ecodan 11kw Defrosting Issue.
@morgan this can just be done by your sepecilist when t...
By ASHP-BOBBA , 5 days ago
-
RE: Anyone still weathering it out with Agile?
@toodles I guess it all comes down to import averages. ...
By Tim441 , 5 days ago