Rethinking the mindset for mass retrofit - a provocative idea

68 Posts
10 Users
17 Reactions
6,849 Views
(@iancalderbank)
Noble Member Contributor
3665 kWhs
Joined: 2 years ago
Posts: 643
 

@jamespa a few thoughts

heatpumpmonitor.org is great , but in the nicest possible way something of an echo chamber - the people who've made the effort to put their systems on there are (generally speaking) the same people who've made the time and effort to make their systems work really well, because if their data shows poor performance, they'll have done something about it! So whilst they show what is achievable in practice over a decent sample size, they show the upper end of that. I'm trying to get my system on there at the mo. I'll drag their figures down ;-). Its not that easy to get your system on there, you have to be a geek and get a bunch of stuff installed and configured, as I'm sure you're aware, and is so not "joe public" suitable. data from the rest of the country's installs - those have not been tweaked and optimised by heating enthusiasts - is what you'd need to see, but that would have to come a different way.

early adopter - I disagree, we are in early adopter. NOT from a tech point of view - I accept it is mature. I mean from a people (% of users who've got one, % of the installer pool who can fit / have fitted one) and process (are installs and systems reliable and consistent) point of view.

flow rates and distribution pipework - I've a lot of respect for heatgeek so no doubt their figures are good, but there are some of the dreaded assumptions in there which won't be the case for all houses. some people's distribution pipework won't be great or as per those assumptions. almost every house is different. back to having to know whether the house is suitable or not for your "straight swap".

having done my own install and 1 month in, and followed all the best practices that I could ( single loop, no buffer, modulating pump, volumiser, replace emitters, long run times) I don't know yet how one gets these super high COPs. I've had at best 3.5 when its been around 7-9C. This morning, outside temps hovering around zero, I got 2.0 (see pic below) and that is not with high flow T's , I'm at  42 or 43. and I gave a damn about my install.

image

this thread isn't a discussion about my system but my point is that I will put the effort in to improve my system. In the "straight swap" situation that won't happen. So, IMO, the mfr claimed / spec sheet COPS will be a complete pipe dream.

My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
👍
1
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
3397 kWhs
Joined: 2 years ago
Posts: 463
 

Posted by: @jamespa

userid="4643"]

the difference is that with a gas boiler, the biggest issue is the safety risk.

 

Quite, so less regulation not more is required!

Sorry I have to disagree- the HP installation industry needs to be completely re- configured with powerful measures centred on performance penalties. 

The central objective to the HP rollout is energy efficiency on a massive scale. If an MCS installer company installs a “Designed” system delivering a COP of only 1.5 (when it should be 4) and fails to document an energy strategy which is intelligible to the home owner then there must be heavy and ruthless penalties to the installer for failure to deliver the design performance.

In the same way that Gas Safety cannot be compromised... Today energy efficiency cannot and must not be treated as a secondary ambition.

Many other publicly funded businesses need to meet standards requiring penalty tests, why not the lucrative BUS scheme. 

 


   
ReplyQuote
(@chickenbig)
Honorable Member Member
2388 kWhs
Joined: 3 years ago
Posts: 292
 

Posted by: @iancalderbank

some people's distribution pipework won't be great or as per those assumptions. almost every house is different. back to having to know whether the house is suitable or not for your "straight swap".

This rather suggests the industry is missing a system for characterising the flow network. I can't help but feel that with some level of "plugging in a pump into the existing system" and "manually turning the existing radiators off and on" one can fairly non-intrusively assess the flow properties. I guess that some more sophisticated boilers may even allow you to control the pump level and see the flow rate. In addition, injecting slugs of warm water into the pipes (a delta) one might be able characterise how insulated the pipes are as well as the length of pipe runs by observing when each radiator starts to heat up.

Perhaps there is a business case for some kind of a product, especially if one can shoe-horn magic pixie-dust AI in there to recognise standard system layouts to reduce the number of manual operations required. Installation risks need to be managed.

 

   
ReplyQuote



(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@jamespa

I too try to think outside the box, and have spent much of my career educating the 'but this is the way we have always done it' clan. Methods and processes can often be improved, and at the end of the day it will invariably come down to 'is it cost effective to do so'.

We both share the same desire, to help reduce greenhouse gas production by lowering fossil fuel consumption, and hopefully encouraging others to do the same. There are a number of options that could be used to try to achieve this goal.

For me, the starting point should always be to reduce demand, be that energy efficient appliances, modified lifestyle, or in the case of home heating, improved insulation. Reducing demand for most would be a win - win, since it would not only help reduce ones energy bills, but by reducing demand, can help reduce the amount of generating capacity required to be built and operated to meet that demand. Reduced generating capacity should help keep down costs for the benefit of the consumers.

A further way to reduce demand is to try to ensure that ones heating system is operating at maximum efficiency, be that gas fired, oil fired, or by means of a heat pump. This is where our thinking differs slightly, though we still champion optimum efficiency.

The redeeming factor for heat pumps, is their higher efficiency by harvesting energy from a free external source, in most cases the outside air. This unfortunately is also their Achilles Heal, since unlike other heating systems, the fuel source for an ASHP is not consistent, and reduces with falling outside air temperature. This of course occurs at the time of peak heating demand.

Even using average daily temperatures in ASHP calculations does not work well, since it is quite possible for the outside temperature to change from a low of -2C overnight, to a peak of 10C during daytime. This can have a dramatic effect not only on the heat loss experienced by a property, but also the energy source for an ASHP being used to heat that property. Making calculations based upon an average temperature of 4C, will I suspect indicate a higher efficiency than the true value achieved. The higher the required LWT, the lower the overall efficiency achieved.

At the end of the day it is down to individuals to decide what improvements they can make in their efforts to reduce energy consumption in the most efficient manner.

I attached a copy of a spreadsheet I produced quite some time ago for an Ecodan 14kW ASHP. It can be used to explore how a system is likely to respond to varying insulation levels, heat emitter capacity and indoor temperature setting. If you have any questions then please feel free to ask.


   
ReplyQuote
(@iancalderbank)
Noble Member Contributor
3665 kWhs
Joined: 2 years ago
Posts: 643
 

Posted by: @chickenbig

This rather suggests the industry is missing a system for characterising the flow network. I can't help but feel that with some level of "plugging in a pump into the existing system" and "manually turning the existing radiators off and on" one can fairly non-intrusively assess the flow properties. 

I tried to do this with my existing system. But: my primaries to the boiler were undersized (they were replaced for the heatpump), my existing circulating pump was undersized (Arguably even for the boiler system) and certainly couldn't generate the head/flow rates needed for a heat pump circulation rates. I contemplated just replacing the circulating pump with the HP spec one , but concluded it wouldn't be worthwhile (Because any result would be invalid due to the aforementioned too-small primaries) and I literally couldn't buy the pump that I wanted to without actually buying a heat pump with it. real world houses will have any manner of similar foibles.

I think you might be able to prove a definite positive: if you set existing circulation pump to max, can you get the flow rates the HP needs (without huge noise etc), if yes, observe and measure behaviour with rads on/off one by one, but if the result is anything other than that , I think you're back to intrusive "find the pipes" assessment.

 

My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
ReplyQuote
(@iancalderbank)
Noble Member Contributor
3665 kWhs
Joined: 2 years ago
Posts: 643
 

Posted by: @sunandair

Sorry I have to disagree- the HP installation industry needs to be completely re- configured with powerful measures centred on performance penalties. 

The central objective to the HP rollout is energy efficiency on a massive scale. If an MCS installer company installs a “Designed” system delivering a COP of only 1.5 (when it should be 4) and fails to document an energy strategy which is intelligible to the home owner then there must be heavy and ruthless penalties to the installer for failure to deliver the design performance.

In the same way that Gas Safety cannot be compromised... Today energy efficiency cannot and must not be treated as a secondary ambition.

Many other publicly funded businesses need to meet standards requiring penalty tests, why not the lucrative BUS scheme. 

I'm halfway between the two of you.

If a system installed under the current MCS regime, only delivers COP 1.5 and it was specified as 4, and/or it just doesn't heat the house properly, then the installer must rectify or be penalised. There I agree with sunandair. But, I think we all know that doesn't work very well in practice, right?

But there's another objective to HP rollout which is arguably higher priority than "energy efficiency": Get Off Gas. here I agree with JamesPa, and why I said what I said several post back.

If heat pumps can be made to COST the same as gas (to run and to install) even for low efficiency run costs (thus requiring HP specific electricity pricing or a major price shift),  that then means those installs are more acceptable to the mass user base and the take up goes up. then IMO this is still of benefit for the climate. Those less efficient installs (perhaps not under MCS ) could be still of value to the climate and the user, providing they still work (and by work I simply mean "heats the house to the user's comfort"). There's always the option then for the user to invest a little more (or be given a interest free loan to do so) to up-spec the system to make it more efficient.

note that I am not advocating that all installs should be low efficiency - far from it - I'm just saying that accepting that some will have to be - providing the joe public customer is not left financially disadvantaged or Cold -  is a potential way to Get Off Gas more quickly.

 

My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs


   
ReplyQuote
(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@iancalderbank

At the present time installing more heat pumps will not necessarily 'get off gas', it will just move the location where the gas is being burned.

Combined Cycle Gas Turbine (CCGT) power stations are approximately 50% efficient, so it takes 2kW of gas to produce 1kW of electrical energy. If a heat pump only has a COP of 1.5, then to operate it will entail burning more gas.

When operating in open cycle, a CCGT is only 33% efficient. I will leave you to do the maths.

Installing inefficient heating systems is therefore not the answer, and will not encourage homeowners to go through the trauma and expense of installing such a system, that will then probably cost more to run.

I feel that it is rather pointless for the Government to throw our money at the heat pump manufacturers and installers, without there being an agreed design philosophy of how to correctly install a heat pump in the different properties, correctly trained staff to install and configure such systems, and a regulator 'with teeth' who can ensure that systems are correctly installed, configured and commissioned for optimum efficiency, and take action with those companies who fail to provide an adequate service.

I'm not holding my breath. 🙄 


   
👍
1
ReplyQuote
 robl
(@robl)
Honorable Member Member
2570 kWhs
Joined: 3 years ago
Posts: 199
 

Posted by: @iancalderbank

If a system installed under the current MCS regime, only delivers COP 1.5 and it was specified as 4, and/or it just doesn't heat the house properly, then the installer must rectify or be penalised. There I agree with sunandair. But, I think we all know that doesn't work very well in practice, right?

 

@iancalderbank 

I'd love to see MID certified meters installed under MCS, and then a guaranteed SCOP performance from it!  I appreciate the meters cost money, but I think are well worth the extra and should be installed as standard.  As a bare minimum a MID certified electrical meter should always be installed, they're only £50.  So far as I'm aware, electrical and thermal meters inside heatpumps are of unknown (and poor) tolerance, so cannot be used as part of a guarantee. 

 


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10857 kWhs
Veteran
Joined: 2 years ago
Posts: 2054
Topic starter  

Thanks for all the comments.  As a group we aren't currently 'converging', which is a disappointment given that this group seems to be considerate of others views and generally positively minded.

From some of the comments above I realise that I made the classic rookie error (even though I should know better) of leaping to a strawman partial solution before being certain we agree on what the objective, constraints and assumptions are.  So lets take a step back and check we agree on those.  We can then return to the comments above

 

I would suggest the following

 

Objective

the objective is to reduce, eventually eliminate carbon emissions while heating our houses, with a degree of urgency commensurate with the ambition to be carbon neutral by 2050.  

This is subtly but importantly different to 

Posted by: @sunandair

The central objective to the HP rollout is energy efficiency on a massive scale.

In this context it is worth noting (to give a scale to the problem) that we currently retrofit 1.4M gas boilers each year, and have about 23M houses.  So roughtly we need to do about 1M-1.5M per year.

Constraints

the primary constraint is that it has to be affordable, not just to the few, but to the many.  I would also suggest that making the assumption that it will be made affordable by ongoing taxpayer subsidies (at any material level) is dangerous, possibly foolhardy

the timescale objective means that any solution needs to be based largely on technology we have, or can be confident we will have shortly

Assumptions

I think we have to assume that an ASHP run on electricity is cleaner, and will continue to be cleaner, than gas ever can be.  We further have to assume that the cleanliness of electricity will, at worst, keep pace with the demand, contrary to this comment:

Posted by: @derek-m

At the present time installing more heat pumps will not necessarily 'get off gas', it will just move the location where the gas is being burned.

The fact is that the proportion of renewables in electricity has grown every year recently.  If we want to take a snapshot then the Government publishes greenhouse gas conversion factors, currently 0.18 (Kg(e) per kWH) for Gas, 0.19 for electricity.  The figure for electricity has been improving year on year and, even at the current figure, an ASHP COP of 1.1 would outperform electricity in terms of carbon emissions.

For the purposes of the discussion about ASHPs we also should assume that insulation is a parallel activity, not alternative but parallel.  However there will always remain a requirement to heat homes

 

Can we at least agree on these, and are there any which need to be modified or added?

 

Once we agree on these, or alternatives, I suggest we try to agree on the current state of the industry.

 

 

 

 

 

 

This post was modified 2 years ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
2
ReplyQuote



(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

@jamespa

I think that many on the forum would agree that there is not a simple solution, but that all reasonable options should be considered and investigated. I am not convinced that many of our politicians and their advisors fully understand the scale of the problems. Voting into law net zero requirements is not going to make it happen.

I would suggest that we consider the problems and possible solutions, and then try to convince others of the need for action.

Here is my list of suggestions.

1) Problem :- It is my understanding that many of the condensing gas boilers installed in homes throughout the land are not actually condensing. Possible Solutions :- Educate homeowners to lower the temperature setting so that condensing actually occurs, thereby reducing consumption and saving them money. Ensure Gas Engineers who install and service gas boilers are adequately trained, and ensure that gas boilers are correctly adjusted and that the homeowner knows the reason why. Savings of up to 10% may be possible, and possibly would be the simplest and cheapest to achieve.

2) Problem :- Many homes have poor energy efficiency, due to poor levels of insulation. Possible Solutions :- Encourage those that can afford to do so, to improve insulation levels whatever their heating system, financial support should be provided for those that cannot afford to do so. Highlight the energy saving and long term financial benefit of improved insulation.

3) Problem :- There would appear to be a lack of knowledge within Government, the varies ministries and regulators, about heat pumps and heating systems, which may be affecting decision making. Possible Solutions :- Insist that they have one installed in their own home, at their expense, and see if they enjoy the upheaval and fun and games getting it to work, or getting someone back to fix it when it doesn't.

I will see if I can think of more tomorrow.


   
ReplyQuote
(@chickenbig)
Honorable Member Member
2388 kWhs
Joined: 3 years ago
Posts: 292
 

Posted by: @jamespa

Constraints

I would certainly add that the heat source needs to be simple to fit, probably opportunistically when the existing heat source breaks. This implies it should be quick (and low risk) to install, with a broad-base of installers trained and willing to do so.


   
ReplyQuote
SUNandAIR
(@sunandair)
Noble Member Member
3397 kWhs
Joined: 2 years ago
Posts: 463
 

hi @jamespa

The issue of uptake has loomed large lately and I’m sure there’s many and varied reasons. I guess inflation and the economy wouldn’t have helped. 

Reputation of the HP industry and conversations over the garden wall would certainly have fuelled a lot of resistance to what is often perceived as over-complicated, unreliable and very temperamental. 

You put the word “Mindset” in the title. 
But who’s mindset?

Customer’s still crave NEST or HIVE type thermostats. So the industry gives them pseudo smart thermostats which don’t work. 

What we need is a genuine customer lead solution to heat pump installation. One that recognises “Efficiency is King” and HPs are a delicate instrument that needs to be tailored to the property and fully commissioned… And that the End User, with their own set of limitations and knowledge is the one having to operate it.

Whereas, instead of trying trying to demistify the way a heat pump works the operatives and sales teams appear to languish in the complexity. 

Step One: stop fitting the main controller in the attic, spare room or in the cellar. 😅😂

There are other steps of course…. But this is not just a science issue the “human/machine interface” is totally missing from the MCS guidelines and all most installers handbooks. 
IMHO
  


   
ReplyQuote
Page 4 / 6



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security