Removing a Low Loss Header from Samsung Gen6 System
also its worth saying, the PWM pump is not the enabler to run at low flow temps. That comes from having big enough emitters, properly balanced, etc.
what the PWM does is control the flow rate up/down to maintain the DT , at lower output levels when running in a steady state for a long period. For a given lower output, you can have either the flow rate staying the same (Fixed speed pump) and DT reduced, or the DT can stay the same and the flow rate reduces (variable speed pump).
there is an FSV , can't remember the number of the top of my head, for Target DT. with a PWM pump in the system, the samsung will vary the flow rate to try to maintain this DT but only when its in the stable part of a heating cycle. It has no effect when doing DHW, or when in the initial startup part of a heating cycle (Which is 30-60 mins , at least on my system). This FSV for DT control method has no function if you don't have a PWM pump (this is a common misconception), and is of little use in a system with primary/secondary seperation.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank Thanks for that explanation Ian, very interesting and useful
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@iancalderbank Ah okay, thats interesting. I have to say deciphering the user manual and FSV values is one of the most difficult parts of owning a samsung heat pump.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker You should see a Mitsubishi! 🤣
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 22 Forums
- 2,096 Topics
- 46.2 K Posts
- 61 Online
- 3,383 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
Did you manage to reduce power requirement for DHW? G...
By Bart , 18 minutes ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 9 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 10 hours ago
-
RE: Mitsubishi cycling while on chilled water output
I absolutely wouldn't remove the buffer altogether, I'd...
By JamesPa , 17 hours ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 19 hours ago
-
@jamespa Thanks for the advice - very helpful. I had al...
By abam48 , 2 days ago
-
RE: Weather compensated secondary circuits with Biomass
Hi @andycoo we do an LK 110 standalone weather compensa...
By Sune , 2 days ago
-
RE: Adding battery storage to SolarEdge PV system
@chandykris No need to apologise at all! I forgot to ad...
By Toodles , 3 days ago
-
RE: Say hello and introduce yourself
Yes please do Suggesting a loss in the region...
By JamesPa , 3 days ago
-
As I have reported elsewhere we turned on the cooling o...
By downfield , 4 days ago
-
-
@el3b Hi, sorry to hear that, it is advisable to instal...
By ASHP-BOBBA , 4 days ago
-
RE: Difficult positioning of air source heat pump
@rikiarn Out of intrigue, the thread reads as though Ai...
By Sheriff Fatman , 5 days ago