Pressure drop Primary circuit
Hello !
I am having problems with my ASHP
Commisioned in 2016
When I had a reminder for the annual service, I said that the pressure in my primary circuit was low.
A day after the service the pressure was low again !
It was suspected that the pressure vessel was at fault , In consultation with the company i replaced the schrader valve in the vessel but the next day I was back to zero pressure.
Days later another engineer turned up and repressurised the system and a day later that escaped again.
I have replaced the expansion vessel myself since the company involved said there would be an expensive call out charge for further work on my system. My thinking is that there should be no further call out charges for an ongoing problem not fixed or notified at the time by the service.
I tested the old pressure vessel in water and it was leaking all around the seam. Problem solved I thought . Photos available of the unit after cutting it open.
After installing the new pressure vessel and priming it and the primary circuit to 1.5 bar the pressure still dropped out of the system.
I have looked at the Samsung unit outside and seen signs of slight fluid weeping under a valve. Photo can be supplied !
I have a inkling that one of my internal heat exchangers or the Samsung unit have sprung a leak for the pressure to keep dropping . How do I find where the problem lies and do I have any redress to the service / installation company if this is found to be the case ?
Many Thanks for your attention
Alistair
If your ASHP has both a pressure sensor internally and isolation valves and you also have a pressure sensor one on the expansion vessel then you can isolate your ASHP leave for 24-48 hours and see in which half of the system the pressure has been lost. Otherwise, you may be able to play similar games with any other bits of the system that can be isolated.
I dont see you have a redress against the service company, they appear to have taken reasonable action to fix an evident problem, its not really their fault that there appears to have been more than one problem.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hello James.
Thank you for your reply.
My AWHP is a Samsung AE090JXYDEH , 2 x SWEP ID2-1414 heat exchangers and a Gledhill ABL250HP thermal store. 5 rads 2 towel rails and 90m2 underfloor heating.
The house is a new build with high spec. insulation and themal efficiency , the heating system was specified as part of the whole design.
I can not find any valves on the Samsung unit, There are pressure gauges for the primary and heating circuits next to their prospective expansion vessels. Since these cicuits vary in capacity and along with the differances caused by temperature fluctuations it is hard to use these to diagnose the problem.
I suspect I might have to drain the primary circuit disconnect the ASHP and cap off the flow pipes to do a pressure test on the primary circuit and heat exchangers.
If that fails, I think that I should then remove the heat exchangers and test them individually.
If I drain my system what ratio of glycol to water should I put back in ( I will measure the volume that comes out )
I know I am asking alot, but from experience , the warranty is as useless as the person who causes you to claim off it !
Cheers
Alistair
If you have heat exchangers between primary and secondary the two circuits are isolated so a leak in one wont affect the other. So whichever pressure gauge is dropping tells you which circuit to test. If there are no isolation valves then yes you will need to drain and pressure test, but there isn't much between ashp and heat exchanger so im not sure that, if the leak is in the primary, a pressure test will tell you much that you can't determine buy visual observation.
Have I misunderstood how your system is plumbed?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The primary circuit from the Samsung unit transfers its heat to the secoundry / heating circuit through 2 metal plate heat exchangers.
Do these fail and would that cause wierd pressure events across both circuits .
I am hoping this because they are cheap to replace compared to the heat pump or digging holes in the plaster to find a leak.
It is the primary that drops its pressure.
I Will switch system off and top both systems up and pressure vessels and get result overnight !
Primary at 20psi 1.4 bar
Secondary at 15psi 1.0 bar
I am hoping that by doing this i can find the area of fault and then hand it over to an engineer.
PHE s can fail, I'm not sure what the most common failure mode is. If a plate separating the two circuits failed pressures will presumably equalise, if a plate between one circuit and the air fails presumably only that circuit is affected.
Results overnight may clarify!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Good morning !
I am writing this as I am dealing with the Samsung help line !
Two days ago I posted about losing pressure in my heating systems primary circuit.
Many thanks To James for replying!
Since then I have had the system turned off . After the initiall cool down of the system I checked all pressures and topped up as required.
I deliberately had the two circuits at different pressures .
Over night there has been a slight drop in pressure (1 to 2 psi) evenly in both circuits this I think is down to residual cooling.
Given that the system lost its Pressure over night when operating, would I be right in thinking the fault lies in the outside unit ?
Given that it has no warranty. Can and is it worth repairing these things ?
Are there people who would take it on ?
If I have to replace the unit will the wiring and pipes be of the same standard ?
I know It is a big ask, but my faith in tradesmen is very low , I have a self build and have learnt that I can live with my own mistakes, but find it hard to come to terms with paying other people, to muck it up or not provide support .
Many regards
Alistair
P.s heating not on the Samsung phone options.
I have just been given a diferent number from the one on my paper work 0330 7262677 . I am going in !
Hi Alistair. I’m not an engineer but it sounds as if your analysis is correct to me. Perhaps others will be able to confirm.
A replacement like for like should be a straight swap. I’ve fitted my own Samsung if that’s the route you want to take.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Whoo hoo A number that worked , option 5 !
An engineer is going to call me back !!
Nick from Samsung has called me back .
He has said that the system has had major trauma, and possibly for a long term, due to failure of the pressure vessel , and that it may take a while to expell all the air in the primary circuit !
Will keep the fill loop attached and top it up as needed for a week , and then report back !
I will hope for the best, and admit that this help has quelled some of my cynacism ! Thanks Nick !
If only I had recieved similar attention from my service / installers !
Thankyou to all
Alistair
Just to update you all.
I made up my own fill loop as my installers had not left one for the primary circuit and used a special pump. Eventually after many small top ups and bleeds over 5 weeks the system eventually held a constant pressure !
It was hard to be positive, thinking they were going to charge me a call out fee for every time the system needed topping up.
I have now found a local company who are much more reasonable on their charging structure !
Many thanks to those who helped !
Alistair
Posted by: @ohdearismJust to update you all.
I made up my own fill loop as my installers had not left one for the primary circuit and used a special pump. Eventually after many small top ups and bleeds over 5 weeks the system eventually held a constant pressure !
It was hard to be positive, thinking they were going to charge me a call out fee for every time the system needed topping up.
I have now found a local company who are much more reasonable on their charging structure !
Many thanks to those who helped !
Alistair
I've always regarded topping up heating systems as my job not a plumbers. My gas system needed topping up about twice per year and no way was I going to pay someone else to do this given that it takes less than five minutes and they would have to travel whereas I am already on site. Likewise cleaning filters.
Perhaps I'm just too mean!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,378 Topics
- 53.9 K Posts
- 171 Online
- 6,060 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Radiator sizing sanity check
No chance! Largely, hence my suggestion to do some...
By JamesPa , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
As it turns out this is correct! All I needed to do was...
By benson , 5 hours ago
-
Here is an update of the setback we operate on our syst...
By SUNandAIR , 7 hours ago
-
RE: Grant ASHP 17.5 kw. weather curve
@chinkoa Sorry there are two separate thoug...
By JamesPa , 7 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@transparent As easy as putting sparklers in champag...
By Papahuhu , 8 hours ago
-
@f1p Looks good, and will likely be something I use whe...
By Sheriff Fatman , 11 hours ago
-
RE: Cascade 2x Grant Areona 10kw ASHP - Ongoing setup issues
Either complete Bow Locks or at best a marginal effect....
By JamesPa , 13 hours ago
-
Hi all I’m looking to get some insight on what others...
By Renewables345 , 14 hours ago
-
RE: The Great British Heat Pump Owner Persona Survey: Let's Build Our Archetype!
@mosibi, go on then, complete the survey. Let's get the...
By Mars , 14 hours ago
-
RE: Water Hammer After Heat Pump Install
@jaynieq I wish you luck with this one. I think the ma...
By JamesPa , 16 hours ago
-
RE: Optimum new build house design for Heat Pump
From first principles I would say: Definitel...
By JamesPa , 1 day ago
-
RE: Weather compensation- why you should use it
As good a place as any to drop this video:/p>
By Mars , 1 day ago
-
RE: Forum updates, announcements & issues
@transparent D'Oh - I did look before I posted but I mi...
By dr_dongle , 2 days ago
-
Compatibility with Samsung AE080RXYDEH
I am new to all this. We have a SamsungAE080RXYDEH that...
By John999 , 2 days ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Maybe you should buy your additional batter...
By Bash , 2 days ago
-
RE: Data Accuracy Problem: Daikin 8kW Heat Pump's Onecta App vs MMI Power Consumption
@nursethescreens Yes, comfort and happiness of the fami...
By Toodles , 2 days ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
Thanks folks. I had tried googling an ethernet lab adap...
By z8lccda , 2 days ago
-
RE: Changing from 4-port buffer to volumizer
@toodles I'm not concerned that the behaviour is not no...
By Andy1618 , 2 days ago
-
-
RE: Setback savings - fact or fiction?
I agree, and I think there are two things in play here....
By cathodeRay , 2 days ago