Pressure drop Primary circuit
Hello !
I am having problems with my ASHP
Commisioned in 2016
When I had a reminder for the annual service, I said that the pressure in my primary circuit was low.
A day after the service the pressure was low again !
It was suspected that the pressure vessel was at fault , In consultation with the company i replaced the schrader valve in the vessel but the next day I was back to zero pressure.
Days later another engineer turned up and repressurised the system and a day later that escaped again.
I have replaced the expansion vessel myself since the company involved said there would be an expensive call out charge for further work on my system. My thinking is that there should be no further call out charges for an ongoing problem not fixed or notified at the time by the service.
I tested the old pressure vessel in water and it was leaking all around the seam. Problem solved I thought . Photos available of the unit after cutting it open.
After installing the new pressure vessel and priming it and the primary circuit to 1.5 bar the pressure still dropped out of the system.
I have looked at the Samsung unit outside and seen signs of slight fluid weeping under a valve. Photo can be supplied !
I have a inkling that one of my internal heat exchangers or the Samsung unit have sprung a leak for the pressure to keep dropping . How do I find where the problem lies and do I have any redress to the service / installation company if this is found to be the case ?
Many Thanks for your attention
Alistair
Posted by: @ohdearismHello !
I am having problems with my ASHP
Commisioned in 2016
When I had a reminder for the annual service, I said that the pressure in my primary circuit was low.
A day after the service the pressure was low again !
It was suspected that the pressure vessel was at fault , In consultation with the company i replaced the schrader valve in the vessel but the next day I was back to zero pressure.
Days later another engineer turned up and repressurised the system and a day later that escaped again.
I have replaced the expansion vessel myself since the company involved said there would be an expensive call out charge for further work on my system. My thinking is that there should be no further call out charges for an ongoing problem not fixed or notified at the time by the service.
I tested the old pressure vessel in water and it was leaking all around the seam. Problem solved I thought . Photos available of the unit after cutting it open.
After installing the new pressure vessel and priming it and the primary circuit to 1.5 bar the pressure still dropped out of the system.
I have looked at the Samsung unit outside and seen signs of slight fluid weeping under a valve. Photo can be supplied !
I have a inkling that one of my internal heat exchangers or the Samsung unit have sprung a leak for the pressure to keep dropping . How do I find where the problem lies and do I have any redress to the service / installation company if this is found to be the case ?
Many Thanks for your attention
Alistair
If your ASHP has both a pressure sensor internally and isolation valves and you also have a pressure sensor one on the expansion vessel then you can isolate your ashp leave for 24-48 hours and see in which half of the system the pressure has been lost. Otherwise, you may be able to play similar games with any other bits of the system that can be isolated.
I dont see you have a redress against the service company, they appear to have taken reasonable action to fix an evident problem, its not really their fault that there appears to have been more than one problem.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hello James.
Thank you for your reply.
My AWHP is a Samsung AE090JXYDEH , 2 x SWEP ID2-1414 heat exchangers and a Gledhill ABL250HP thermal store. 5 rads 2 towel rails and 90m2 underfloor heating.
The house is a new build with high spec. insulation and themal efficiency , the heating system was specified as part of the whole design.
I can not find any valves on the Samsung unit, There are pressure gauges for the primary and heating circuits next to their prospective expansion vessels. Since these cicuits vary in capacity and along with the differances caused by temperature fluctuations it is hard to use these to diagnose the problem.
I suspect I might have to drain the primary circuit disconnect the ASHP and cap off the flow pipes to do a pressure test on the primary circuit and heat exchangers.
If that fails, I think that I should then remove the heat exchangers and test them individually.
If I drain my system what ratio of glycol to water should I put back in ( I will measure the volume that comes out )
I know I am asking alot, but from experience , the warranty is as useless as the person who causes you to claim off it !
Cheers
Alistair
If you have heat exchangers between primary and secondary the two circuits are isolated so a leak in one wont affect the other. So whichever pressure gauge is dropping tells you which circuit to test. If there are no isolation valves then yes you will need to drain and pressure test, but there isn't much between ashp and heat exchanger so im not sure that, if the leak is in the primary, a pressure test will tell you much that you can't determine buy visual observation.
Have I misunderstood how your system is plumbed?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
The primary circuit from the Samsung unit transfers its heat to the secoundry / heating circuit through 2 metal plate heat exchangers.
Do these fail and would that cause wierd pressure events across both circuits .
I am hoping this because they are cheap to replace compared to the heat pump or digging holes in the plaster to find a leak.
It is the primary that drops its pressure.
I Will switch system off and top both systems up and pressure vessels and get result overnight !
Primary at 20psi 1.4 bar
Secondary at 15psi 1.0 bar
I am hoping that by doing this i can find the area of fault and then hand it over to an engineer.
PHE s can fail, I'm not sure what the most common failure mode is. If a plate separating the two circuits failed pressures will presumably equalise, if a plate between one circuit and the air fails presumably only that circuit is affected.
Results overnight may clarify!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 22 Forums
- 2,082 Topics
- 45.7 K Posts
- 41 Online
- 3,370 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: DHW SET UP with Samsung gen 5
So I go to Daily and 1 slot enter time and on choice an...
By Alfapat , 22 minutes ago
-
@bart Best of luck moving forward, I look forward to he...
By ASHP-BOBBA , 13 hours ago
-
RE: Renewables & Heat Pumps in the News
By Morgan , 13 hours ago
-
RE: Ecodan EMP2 kit - is it any good?
Please note: heat meter accuracy at 95+% is as long as ...
By ASHP-BOBBA , 1 day ago
-
RE: Air Changes per Hour - ACH and the MCS requirement
@jamespa I love going on the tools, I did it yesterday,...
By ASHP-BOBBA , 1 day ago
-
RE: Flow Rate & Low Loss Headers
Houses with reasonably low loss aren't going to require...
By JamesPa , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
If it's running on WC then at night it's quite likely t...
By JamesPa , 1 day ago
-
RE: Jokes and fun posts about heat pumps and renewables
@majordennisbloodnok That’s OK as long as the ‘Terminol...
By Toodles , 2 days ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@aaron All features were in place for the last several ...
By AF1 , 2 days ago
-
RE: To relocate or add extra PV panels..advice required
The situation you are currently experiencing is represe...
By apollogrid , 3 days ago
-
RE: I don't need any heating in the summer. How do I turn my Samsung heat pump off?
SmartThings indeed allows remote control over the heat ...
By HCas , 3 days ago
-
RE: Remaining hot water/hot water flow meter
@lakey Hi, I had a quick read through and wanted to see...
By ASHP-BOBBA , 3 days ago
-
RE: I worry I've messed my Samsung settings up somehow
@ecobaker I missed this, sorry So 3031 was set to...
By Joshua , 3 days ago
-
RE: Forum updates, announcements & issues
@old_scientist thank you, and thank you to @Morgan for ...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
I am a UK based product manager for an energy storage s...
By shawnlee , 4 days ago
-
RE: Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
That's great and in principle I wouldn't disagree, but ...
By JamesPa , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Mitsubishi 8.5 kW Ecodan Standalone (PUZ-WM85VAA)
By Nell , 4 days ago
-