We had a 14kW twin fan Ecodan fitted about 6 years ago. At the time the house was rather cold and lots of stone walls
we’ve just finished completely stripping back 3 of the coldest rooms. So about 1/3 -1/2 of the house. These rooms are now very high insulation. Almost to passivhaus standards.
weve also replaced 3 big of radiators which were plumbed in microbore with a big 5 loop UFH circuit
the knock on effect is its nice and warm but we’ve noticed more cycling from the Ecodan. Nothing major maybe 4x hour currently but that might increase as we hit warmer weather.
Any tips on mitigating the oversized heat pump?
it’s an FTC5 so no quiet mode. We have 3rd party pumps so they aren’t controlled by the HP but we could manually turn them up/down.
is it worth timing an off period each day?
here’s some stats from melpump
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
I have an oversized (for my property) Samsung unit. I can only run constantly when the temp drops below 5C, and even then it gets too warm in the bedroom overnight so I tend to turn off between midnight and 4am, and reheat in the cheap 4-7am slot on my Cosy tariff. I'd need ambient temps close to zero to be able to run constantly. I also turn off between the 4-7pm peak.
I run my system such that the room thermostat controls the heat pump through call for heat, and as long as the room stat is calling for heat, the heat pump will stay on. If it can't dissipate all of the heat it's producing due to the radiators being too small/LWT is set too low, the flow temps just rise until the system reaches equilibrium. Flow temps of ~32C is about as low as I can reasonably go, but I can reduce to 30C overnight if it's really cold.
Our digital room stat has adjustable hysteresis of 0.2-1.0C, and I find a setting of 0.5C is a good compromise between comfort and achieving reasonably long heating runs. the heating may stay on for 45-60mins and then be off for 60mins as the room stat goes between 19.5-20.0C, or whatever I care to set it at.
The trick is to try to ensure reasonably long runs to achieve good efficiency. Cycling 4 times an hour probably isn't great. Reduce the flow temps as low as possible, and try to maximise run times within what is comfortable (obviously you don't want large temperature swings making things too uncomfortable).
Make observations / take measurements to see what works well for your system. Some systems are happier than others when cycling.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
See I’m hoping to keep my flow temps lower. It’s 7c outside and I’m on 29c flow.
im similar in that everything is open. We tend to like around 19c but stats set to 21c. House it’s around 19-20 currently.
so it’s working it’s just cycling too much really.
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
If you are concerned about cycling all you can do is run it a few degrees warmer till you either get no cycling or reduce it to a level you are happy with. I find 32C and I get no cycling, at some point the thermostat will hit its limit and HP will turn off till house drops 0.5C and thermostat turns it on again that can be several hours.
Posted by: @bensebSee I’m hoping to keep my flow temps lower. It’s 7c outside and I’m on 29c flow.
im similar in that everything is open. We tend to like around 19c but stats set to 21c. House it’s around 19-20 currently.
so it’s working it’s just cycling too much really.
Are your emitters capable of emitting the heat being produced at a flow temp of 29C? If they are not, then the return temp will rise and narrow the dT as the heat being produced cannot be dissipated into the room, and the heat pump will cycle. If that is the issue, the solution is larger emitters or higher flow temps (the heat has to go somewhere).
For any given ambient temperature, you can find your minimum flow temp by running the heat pump constantly and with room stats set high, and see where the flow temps settle (you will need to set the ASHP to always on though so it cannot cycle). For my system (rads only, no UFH), in milder weather (above 10C), the minimum flow temp I can achieve is around 32-33C, and as the outside temp falls (along with the COP), my minimum flow temp reduces to around 30C as less heat is being produced due to the lower COP.
You likely have two choices - run with a lower flow temp (29C) and the unit cycles, or run with a higher flow temp without cycling and allow the room stat to turn off for periods when the house is at temperature. The former is more efficient due to lower flow temps but excessive cycling reduces the efficiency, whereas the latter benefits from potentially longer runs without cycling but efficiency is reduced due to the higher flow temps. You may want to run some comparisons to determine which works better for you (for your definition of better). You will likely find there is a sweet spot for flow temps, below which it is not worth venturing.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
Posted by: @bensebWe had a 14kW twin fan Ecodan fitted about 6 years ago. At the time the house was rather cold and lots of stone walls
we’ve just finished completely stripping back 3 of the coldest rooms. So about 1/3 -1/2 of the house. These rooms are now very high insulation. Almost to passivhaus standards.
weve also replaced 3 big of radiators which were plumbed in microbore with a big 5 loop UFH circuit
If your UFH is a high mass construction you may be able to store quite a bit of heat so you can run the heating above the cycling temperature or to a less extreme cycling count and live with long off times. So is your UFH a screed construction? What other emitters do you have? Are you thinking of screeding the other half of your floor area?
And as @old_scientist said there might be issues if your return temps aren’t keeping low.
The 14kw ecodan will have a minimum output of somewhere around 4.5kw which will challenge your emitter setup to lose enough heat at low flow temps.
Our ecodan is an 8.5 in a 180 sqM old house and we can’t quite get down to 32c flow temps (rads only) but we are fine at 34c with one cycle sometimes two cycles per hour. Our return temps are pretty much horizontal on the MELCloud graphs at that flow temp.
Hmm lots to think about.
the house is about 250 m² roughly half of that is UFH. Ie most of downstairs. but only one large room (lounge) is proper UfH with screed the rest is retro fit so doesn’t have the same thermal mass. so still good output but we can’t charge it up the way we can with screed
we’re also on Octopus cozy I did experiment with over running the heating during the cheaper periods and let it cool down a bit on the peak periods but it wasn’t running very efficiently and as our battery tends to keep everything off peak anyway it wasn’t making much sense
I’ll have to keep an eye on the cost of running either with a lower temperature and more cycles versus slightly high temperature less cycles
one thing I need to consider is due to the shape of the house We have quite a few pumps. There’s two on the primaries for the Heatpump and then another three for the internal distribution so I think we have about 400 W of pumps when the system is running that can be about 50% of the heat pump usage.
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Posted by: @bensebwe’re also on Octopus cozy I did experiment with over running the heating during the cheaper periods and let it cool down a bit on the peak periods but it wasn’t running very efficiently and as our battery tends to keep everything off peak anyway it wasn’t making much sense
Yes, if you have battery storage and can flatten the import price, then ramping up in cheap slots and set back or switching off at more expensive times makes little sense - it will be more efficient to just run constantly (or as constantly as you can) at as low a flow temp as reasonable. Without battery storage, it absolutely makes sense to leverage the price differential between cheap, day rate and peak rate times, even when it means giving up a little efficiency to do so (half price electricity for 8 hours a day gives substantial usage if you can shift half or more of your usage into that 1/3rd of the day) by 'charging up' your DHW and UFH screed.
There are advantages to an oversized heat pump too, which rarely get discussed, so it's not all doom and gloom. As you are not working it flat out in the coldest weather, it's likely to frost up less and you are operating it within it's most efficient range (generally between 30-70%), outside of which efficiency rolls off. After a winter holiday (or extended power cut) where the heating has been turned off or down to minimum, you have the extra capacity to reheat the home quicker rather than merely being able to maintain an exiting comfortable temperature.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
I've been experimenting with flow temperature, now the house doesn't have windows open for builders, etc.
Managed to push our WC curve down -7c from where it was. This is great except if the heating goes off for any period, then it's slow to recover, but fine for maintenance.
Settled on about -5, so means currently at 6c outside, we're on 29c flow temp. Using about 20kwH of power a day. Not bad for a 200+ year old, 250sqm house eh!
Will start to look at cycling next week now I have a starting point for what flow temp it 'needs'
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
@benseb that sounds a good point from which to start. Since our battery is just a third of your size I would be heating in just the low cosy period and then mostly off and take the efficiency hit. But you don’t need to do that. Happy fiddling to get the cycling better!
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
16 hours ago
-
Ecodan Zone 2 Mitshibishi thermostat Auto Adapt
1 month ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
2 months ago
-
New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
2 months ago
-
Ecodan with FTC7 - True Weather Compensation
2 months ago
- 27 Forums
- 2,523 Topics
- 58.7 K Posts
- 582 Online
- 6,802 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Underfloor Heating Installation Issues with Heat Pump
This looks like a practical solution 👍
By bobflux , 1 hour ago
-
It's a detached house with a fairly large split-level e...
By petch , 2 hours ago
-
Your installer may well be right. If the WC curve isnt...
By JamesPa , 3 hours ago
-
RE: Our 10 year old Grant heat pump failed
Same as many boilers, ovens washing machines and other ...
By JamesPa , 5 hours ago
-
RE: Home energy storage & battery register
3 X Pylontech US2000 Plus @ 2.4 Kw each = 7.2 Kw SoFa...
By vzm56n , 6 hours ago
-
RE: Daikin Altherma 3 LT compressor longevity question
So on this question of compressor longevity, I have a D...
By Optimistic Optimiser , 6 hours ago
-
Horizontal Hot Water Cylinders for ASHP with Energy Efficiency Rating 'A'
I looking to Have an ASHP installed in the near future....
By vzm56n , 6 hours ago
-
RE: Noisy Grant Aerona 3 13kW ASHP question
Here's a LibreOffice spreadsheet. I put the formula f...
By bobflux , 12 hours ago
-
RE: Electricity price predictions
I assumed you were joking here. Hence my joke about ...
By Batpred , 12 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Photos of cylinder cupboard and UFH manifold would be u...
By Travellingwave , 16 hours ago
-
RE: My misgivings about installing ASHP and solar panels via the ECO4 scheme...
It has been some time since I posted comments about Eco...
By Dwynwen , 1 day ago
-
RE: Forum updates, announcements & issues
Something big is coming to Renewable Heating Hub! Ove...
By Mars , 1 day ago
-
RE: A Single Voice for Heat Pumps, But Will It Finally Raise Industry Standards?
From what I’ve read, the Heat Pump Association UK is me...
By Jonatan , 1 day ago
-
RE: Tell us about your Solar (PV) setup
Pylontech US5000 stores about 4.3 kWh accounting for in...
By bobflux , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Hi all, Just an update on where we are with the "Consta...
By DEdwards , 2 days ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
Well I've had an interesting few days and would like to...
By giganto , 2 days ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
Yes, here's mine. From the service manual parts numbers...
By bobflux , 2 days ago
-
Had to learn the hard way 🤣 now I'm sharing T...
By bobflux , 2 days ago
-
RE: Issue with a Grant Air Source Heat Pump & Tado Smart Thermostat
Im assuming from your original post that hysterisis ref...
By JamesPa , 2 days ago
-
RE: Heat Pump vs New Gas Boiler for Inherited House - Worth the Extra Cost?
Hi @fretless6 Mike, I have experience with Taggas (Re...
By Old_Scientist , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Now seems a good time to summarise the costs and effici...
By benson , 3 days ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 3 days ago