Our Daikin ASHP
Hi Derek, thanks so much again for sharing your expertise.
You are quite correct I was confusing the terminology. I have put equilibrium temp back to the default of -4°C.
That makes complete sense, so we should expect to the ASHP running more given the higher pricing for gas and electricity. I will leave the curve at 45°C at -10°C and 25°C @ 18°C and with the lot max modulation now set at 10°C and monitor the cycling and overall COP.
Thanks,
Adam
Hi @adaml
When time allows, monitor how long the heat pump runs and then how long it is stopped before restarting. Also record the water flow and return temperatures, which may highlight any possible problems with your system. If your heat pump is running for short time periods then stopping for short time periods then it may be necessary to adjust some of the operating parameters.
Hi Derek,
I've been watching it run tonight and it is sometimes running for about 20 minutes and then stops and other times it is starting, running for only a couple of minutes and then stops. The required flow temp for tonight is showing as 31°C. The required was showing as 26°C and the lwt modulation seems to have increased this. The house is sitting at 21.7°C at the moment.
I think one potential problem could be that the Daikin thermostat/controller is situated in our downstairs hallway, with the kitchen door relatively close to it. This means that when we're cooking the temperature raises in the hall and trips the thermostat off, despite other parts of the house being cooler. I wonder if increasing the thermostat temp in the hall to say 22°C could be worth a shot?
Jan shows the compressor has been running for 4 hours with 42 starts at the moment. Other snapshots were 27 at 2 hours and 36 at 3 hours.
Stats from the controller tonight, couple of snapshots;
Outdoor temp. 9.0°C
Leaving water 26.8°C
Leaving water (PHE) 26.8°C
Inlet water temp. 25.3°C
Refrigerant temp. 26.0C
Flow rate 12.9l/min
Outdoor temp. 9.0°C
Leaving water 30.4°C
Leaving water (PHE) 30.0°C
Inlet water temp. 30.2°C
Refrigerant temp. 29.7C
Flow rate 12.6l/min
Hi @adaml
First of all let's clarify what is meant by running, do you mean that the compressor is actually running, or that it is just the water pump that is running?
The water pump is often started before the compressor is started, and continuous to run for a short period after the compressor has stopped. The water pump is also run for short periods of time to check the water temperature, so that the controller knows when to start the compressor to provide more heat energy.
Looking at your snapshots, I would say that the upper one has the water pump running but the compressor is stopped, and in the lower one both compressor and water pump appear to be running.
I think that you may find that the data relating to running and starts should be interpreted in the following manner.
'Jan shows the compressor has been running for 4 hours with 42 starts at the moment'.
I think that this actually means that since the start of January, the compressor has run for a total of 4 hours, and since the start of January the compressor has started 42 times. So it would appear that what has actually happened is that the compressor has started 42 times in approximately 42 hours, so has started on average once per hour, and has run for an average 5.77 minutes each time.
- 26 Forums
- 2,323 Topics
- 52.1 K Posts
- 451 Online
- 5,979 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Grant Aerona circulation/system pump staying on
@mikefl thank you, I've changed 4200 to 2 and now the m...
By damonc , 1 hour ago
-
RE: Solar panels on side of house to heat water
The original strategy behind the production of bi-facia...
By Transparent , 1 hour ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
@batpred I've had a bit of time to look into this to...
By Bash , 3 hours ago
-
RE: Flow rate discrepancy between ASHP and manifold
Air release valves dont always work! You are gonna ha...
By JamesPa , 3 hours ago
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
Fair enough. I recommend quizzing him to get your mone...
By JamesPa , 4 hours ago
-
RE: Havenwise App Help & Forum Support – Get the Most from Your Heat Pump
@simonwig Thanks for the bump. Not sure why I didn't se...
By HCas , 6 hours ago
-
RE: Are Water Companies Delivering Bricks?!
...which in turn reminds me of a Thelwell cartoon I onc...
By Majordennisbloodnok , 7 hours ago
-
RE: Our journey through Octopus tariffs 2020-2025
I mentioned above "2025 move to Intelligent Go meant ...
By Tim441 , 7 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — thank you, that is useful information you hav...
By cathodeRay , 9 hours ago
-
RE: Electricity price predictions
My apologies. I should've written "The number and dep...
By Transparent , 10 hours ago
-
RE: Help…my NIBE heat pump has faulted again!
If it happens only when it gets cold then it maybe that...
By JamesPa , 11 hours ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
Has anyone got past this screen to set up the integrati...
By AlanW1212 , 11 hours ago
-
RE: Heat Pump Training vs. Real-World Installation
@lucia have you discoveredfor how green each of our ene...
By Judith , 12 hours ago
-
RE: Diagnostic Data Needed for Repeatedly Failing Tesla Powerwall 3 System
You seem to be on the right track... Installers are rec...
By Batpred , 20 hours ago
-
RE: Should Our Water Circulation Pump Be Configured to Run All The Time?
there's a detect cycle setting (4200) on the old grant ...
By damonc , 22 hours ago
-
RE: Commencing on an ASHP Installation Process
@sheriff-fatman It's also worth highlighting that th...
By Lucia , 23 hours ago
-
RE: Hitachi Yutaki SCombi Heat Pump - Owners
. It does but, unless there has been a firmware updat...
By JamesPa , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
Yesterday it was chilly and the cosy6 had a Cop of 4.3 ...
By AgentGeorge , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Same here! This month 187kw.
By Andris , 1 day ago