Hi Derek, thanks so much again for sharing your expertise.
You are quite correct I was confusing the terminology. I have put equilibrium temp back to the default of -4°C.
That makes complete sense, so we should expect to the ASHP running more given the higher pricing for gas and electricity. I will leave the curve at 45°C at -10°C and 25°C @ 18°C and with the lot max modulation now set at 10°C and monitor the cycling and overall COP.
Thanks,
Adam
Hi @adaml
When time allows, monitor how long the heat pump runs and then how long it is stopped before restarting. Also record the water flow and return temperatures, which may highlight any possible problems with your system. If your heat pump is running for short time periods then stopping for short time periods then it may be necessary to adjust some of the operating parameters.
Hi Derek,
I've been watching it run tonight and it is sometimes running for about 20 minutes and then stops and other times it is starting, running for only a couple of minutes and then stops. The required flow temp for tonight is showing as 31°C. The required was showing as 26°C and the lwt modulation seems to have increased this. The house is sitting at 21.7°C at the moment.
I think one potential problem could be that the Daikin thermostat/controller is situated in our downstairs hallway, with the kitchen door relatively close to it. This means that when we're cooking the temperature raises in the hall and trips the thermostat off, despite other parts of the house being cooler. I wonder if increasing the thermostat temp in the hall to say 22°C could be worth a shot?
Jan shows the compressor has been running for 4 hours with 42 starts at the moment. Other snapshots were 27 at 2 hours and 36 at 3 hours.
Stats from the controller tonight, couple of snapshots;
Outdoor temp. 9.0°C
Leaving water 26.8°C
Leaving water (PHE) 26.8°C
Inlet water temp. 25.3°C
Refrigerant temp. 26.0C
Flow rate 12.9l/min
Outdoor temp. 9.0°C
Leaving water 30.4°C
Leaving water (PHE) 30.0°C
Inlet water temp. 30.2°C
Refrigerant temp. 29.7C
Flow rate 12.6l/min
Hi @adaml
First of all let's clarify what is meant by running, do you mean that the compressor is actually running, or that it is just the water pump that is running?
The water pump is often started before the compressor is started, and continuous to run for a short period after the compressor has stopped. The water pump is also run for short periods of time to check the water temperature, so that the controller knows when to start the compressor to provide more heat energy.
Looking at your snapshots, I would say that the upper one has the water pump running but the compressor is stopped, and in the lower one both compressor and water pump appear to be running.
I think that you may find that the data relating to running and starts should be interpreted in the following manner.
'Jan shows the compressor has been running for 4 hours with 42 starts at the moment'.
I think that this actually means that since the start of January, the compressor has run for a total of 4 hours, and since the start of January the compressor has started 42 times. So it would appear that what has actually happened is that the compressor has started 42 times in approximately 42 hours, so has started on average once per hour, and has run for an average 5.77 minutes each time.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 17 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Boiling Mad: Exposing Radiatorgate
Actually they do. My case is a prime example. Catalo...
By DREI , 7 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
Blunt answer? The 20-year-old gas system was f...
By DREI , 7 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
You can even go as low as 40c flow temp, if you want a ...
By DREI , 7 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 8 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 9 hours ago
-
RE: Midea ASHP – how to set weather compensation
I'm guessing these are the mcs defaults which are likel...
By JamesPa , 10 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 10 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 12 hours ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 14 hours ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 19 hours ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 20 hours ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 1 day ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 1 day ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 2 days ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 3 days ago
-
RE: Help me keep the faith with my air source heat pump installation
@adamk, interesting point. I’ve not focused much on Hea...
By Mars , 2 days ago
-
Intelligent Octopus Flux (IOF) Review
I promised @toodles that I would provide an update and ...
By Old_Scientist , 2 days ago
-
RE: Who's your electricity provider and what's your tariff?
I am pleased to see the change. We definitely need t...
By Jeff , 3 days ago