Posted by: @adaml@derek-m Thank you! This manual did not match my controller, however, this one does;
The link doesn't seem to work, sorry - if you Google this you should find it though.
Bivalent activation temp is currently set at the default of 0°C and bivalent hysteresis temp is currently set at the default of 3°C.
Please let me know if you have any suggestions?
Hi Adam,
You need to look at pages 68 and 69.
@derek-m Got it - thank you! I think me reading it, understanding and knowing what is sensible are all different things. I can see though that @editor advice earlier is down to this setting to prevent the ASHP activating when it is not beneficial to do so.
Do I understand correctly that as set the ASHP will not activate below 0° and will not activate until the ambient temp is above 3°C?
Hi Adam,
The way I interpret the instructions, is that as the ambient air temperature falls to 0C, the ASHP will be switched off, and the controller will send a permission signal to the gas boiler to switch on. The reverse happens when the ambient air temperature rises to 3C.
A more economical option would be to input the tariff values for both gas and electricity into your controller, and let the controller decide when to change from ASHP to gas. Based on your present tariffs, your ASHP would require a COP of 5.11 or higher, to make it economically viable to run your ASHP in preference to your gas boiler.
Hi Derek,
That makes complete sense, sorry I think I had become too focussed on Possibility 1 and negated to spot the other option. I have my current tariffs setup already.
I have noted it states;
To have an optimal operation when choosing possibility 2, it is for [C‐04] recommended to choose a higher value than the default value.
[C-04] is Range: 2°C~10°C (default: 3°C) (step: 1°C). I have increased this to 6°C - a guesstimate, so if any input please let me know?
Depending on the used boiler, the boiler efficiency should be chosen as follows:
|
# |
Code |
Description |
|
[A.6.A] |
[7‐05] |
|
The option of 0: Very high is already selected.
Hi Adam,
Do you know what COP you are getting from your ASHP at the moment?
I suspect it will be less than 5.11, in which case your gas boiler should be running.
You should be able to get operational data from the controller.
I've been playing around with the weather dependent curve;
45°C flow at -1°C and 30°C flow at 15°C
then
50°C flow at -5°C and 30°C flow at 20°C
then
50°C flow at -7°C and 31°C flow at 14°C
I am also running the system for longer, so unfortuntely lots has changed and I wonder if I'd be better reverting it all with the exception of lowering the DHW temp.
The trouble being I am not sure what impact this will be having on my COP as I cannot get granular data from the controller.
Hi Adam,
Given the difference in the tariff rates for electricity and gas, I would expect your ASHP to only be operating when the ambient air temperature is in the range of possibly 15C and above.
The other thing that I discovered, is that when used with radiators, the ASHP is set for a delta T of 8C between flow and return temperatures. This is probably why you cannot set the weather compensation curve below 30C.
I am still trying to get my head around how the system will work on weather compensation, when for most of the time the gas boiler will be on and the ASHP will be off. You can correct me if I am wrong, but I suspect the controller will be acting more like a thermostat, and just switching the gas boiler on and off to control the temperature.
Could you monitor and report back on the system operation, whilst I have a read through the correct manual.
Hi Adam,
One thing that I forgot to ask, did you have any optional equipment installed?
Hi Derek,
Yes I would say you are correct, the ASHP was operating more in November when the outside temps were around 11-15°C and we could bring the house up to 21°C without the gas boiler.
The outdoor temp tonight is 2.5°C and the desired water temp is showing as 42°C - which is based on the weather comp curve. The gas boiler is firing and on the LED for the boiler it is showing as 48, if I raise the DHW temp to 49 and run the hot tap this display shows 49 so would appear to be degrees Celsius. I wonder where the 48°C is coming from for the gas boiler water temp for the radiators?
That is also correct, it's acting more like a thermostat at the moment switching the gas boiler on and off to maintain the house temp of 21°C. I suppose that is in part what triggered my curiosity to explore what was going on with the ASHP side of things. The ASHP was last active a couple of days ago early one evening for perhaps an hour and then the gas boiler took over.
Thanks for all your help so far, really do appreciate it!
Adam
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 259 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 30 minutes ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@editor, this is now an example of greenwashing in the ...
By Majordennisbloodnok , 41 minutes ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 2 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 2 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 3 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 3 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 4 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@benson — as @tasos suggests, plotting multiple variabl...
By cathodeRay , 6 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 8 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 19 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 20 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 24 hours ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 24 hours ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@majordennisbloodnok Daikin, take note! (In fact, I hav...
By Toodles , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
@mk4 — good work! First, I agree, no evidence of cycl...
By cathodeRay , 2 days ago