non-Mitsubishi owners - how much control do you have over your ASHP "freeze stat" function?

17 Posts
8 Users
3 Reactions
656 Views
(@ecodan-efficiency)
Trusted Member Member
191 kWhs
Joined: 5 months ago
Posts: 23
Topic starter  

On my ecodan the minimum temp I can set the freeze stat function to kick in is +3 degrees C. How does that compare with other manufacturers?


   
Quote
(@judith)
Honorable Member Member
2549 kWhs
Joined: 1 year ago
Posts: 298
 

Can you explain the freeze stat function please? What is it supposed to to do? It us certainly to be described/labelled differently on other makes but there might be the same function.

2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC


   
👍
1
ReplyQuote
(@jamespa)
Famed Member Moderator
10723 kWhs
Veteran
Joined: 2 years ago
Posts: 2020
 

So

Posted by: @ecodan-efficiency

On my ecodan the minimum temp I can set the freeze stat function to kick in is +3 degrees C. How does that compare with other manufacturers?

So far as I can tell absolutely no control available on my Vaillant, it kicks in at 4C

Posted by: @judith

Can you explain the freeze stat function please? What is it supposed to to do? It us certainly to be described/labelled differently on other makes but there might be the same function.

It switches on the heating (typically periodically or at a minimal value) - even if its switched 'off' - obviously provided the mains is connected - when the outdoor temperature falls below a certain value.  This function is also present in many boilers.  The idea is a fallback protection for pipes and equipment.  makes sense IMHO.

 

This post was modified 3 months ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
👍
2
ReplyQuote



(@ecodan-efficiency)
Trusted Member Member
191 kWhs
Joined: 5 months ago
Posts: 23
Topic starter  

@judith Hi, sorry, I should have been more informative. The "freeze stat" function will circulate the water traveling to and from the heat pump in the event of the outside temperature dropping below a set value - so that it does not freeze.

When I've had this function turned on I don't recall the pump itself operating, or indeed the radiators being warm at all, although there seems to be a suggestion that the ecodan system will keep the water at 20 degrees (based on the screen in the settings).


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26254 kWhs
Veteran
Joined: 4 years ago
Posts: 2979
 

Posted by: @jamespa

It switches on the heating (typically periodically or at a minimal value) - even if its switched 'off' - obviously provided the mains is connected - when the outdoor temperature falls below a certain value. 

I don't think I've ever seen this function/setting before on our control panel for our Global Energy Systems machine, but that's hardly surprising. 

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
Abernyte
(@abernyte)
Honorable Member Member
4154 kWhs
Joined: 2 years ago
Posts: 213
 

Mmmm...on my Ecodan it seems to operate at temperatures below +3C and when the system is not calling for heat. So during the overnight set back, if it is +3 or below,  it switches on the primary circulation pump to move the fluid but it does not switch on the heating. As the system has glycol added, the engineer switched it off at the last service as redundant. 

If the overnight temperatures are seriously sub zero, as in recently, then the auto adapt seems to bring on the heating to maintain the house at 16C regardless of set back until the next heating period hoves into view.


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10723 kWhs
Veteran
Joined: 2 years ago
Posts: 2020
 

Posted by: @abernyte

Mmmm...on my Ecodan it seems to operate at temperatures below +3C and when the system is not calling for heat. So during the overnight set back, if it is +3 or below,  it switches on the primary circulation pump to move the fluid but it does not switch on the heating. As the system has glycol added, the engineer switched it off at the last service as redundant. 

If the overnight temperatures are seriously sub zero, as in recently, then the auto adapt seems to bring on the heating to maintain the house at 16C regardless of set back until the next heating period hoves into view.

That all sounds plausible.  Neither heat pump nor boiler manufacturers seem to be particularly precise about what these sort of functions do.  The objective is clear however - to prevent freezing (of the unit itself and possibly the house pipework) during times when the heat source is otherwise off, such as vacation.  Its the sort of thing that modern electronics makes easy to do, but of course at the same time obscures the precise algorithm used!

My boiler system had an actual frost stat (a physical piece of hardware), which was wired basically to override pretty much all other controls if triggered, to switch the boiler on.  It was attached to the pipework so measured water temperature.  This could and did result in the boiler coming on in the middle of a very cold night even if I had it set to off.  That seems to me to be a very reasonable behaviour.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@ecodan-efficiency)
Trusted Member Member
191 kWhs
Joined: 5 months ago
Posts: 23
Topic starter  

Posted by: @abernyte

If the overnight temperatures are seriously sub zero, as in recently, then the auto adapt seems to bring on the heating to maintain the house at 16C regardless of set back until the next heating period hoves into view.

This sounds kind off odd. I run my ASHP on a room temp schedule, with a setback during the night to ensure it's off until morning (13 degrees because the house loses heat so quickly), and I've never witnessed this behaviour. Where would this figure of 16 be coming from? Have you activated Frost Protection on the melcloud app perhaps? (not to be confused with frost stat function).


   
ReplyQuote
Abernyte
(@abernyte)
Honorable Member Member
4154 kWhs
Joined: 2 years ago
Posts: 213
 

No..simply by observation. I can be found about in the early hours and I have noticed that the temperature seems to be kept around 16C if it is -4/5C OAT.  It could be Auto Adapt getting a head start on the morning warm up or some other magic dust that Mitsubishi have sprinkled as the Frost Protection setting is off. 


   
ReplyQuote



(@westkent)
Estimable Member Member
562 kWhs
Joined: 2 years ago
Posts: 48
 

Just checked my ecodan setting and mine is turned if so can only presume the system has antifreeze added 


   
ReplyQuote
(@harriup)
Reputable Member Member
1073 kWhs
Joined: 3 years ago
Posts: 107
 

Posted by: @ecodan-efficiency

Posted by: @abernyte

If the overnight temperatures are seriously sub zero, as in recently, then the auto adapt seems to bring on the heating to maintain the house at 16C regardless of set back until the next heating period hoves into view.

This sounds kind off odd. I run my ASHP on a room temp schedule, with a setback during the night to ensure it's off until morning (13 degrees because the house loses heat so quickly), and I've never witnessed this behaviour. Where would this figure of 16 be coming from? Have you activated Frost Protection on the melcloud app perhaps? (not to be confused with frost stat function).

I wonder if this related to the Holiday setting in the controller menu which sets a room temperature below which the heating will come on with a modest flow temp when the normal heating pattern has been turned off after Holiday Mode is activated. This has caught me out before when I expected the heating to remain off when I was on holiday only to see it running - I have lowered this temperature from its default setting of 15° since then.

Perhaps this particular setting also acts as a default lower room temperature even when the heating is following its day-to-day schedules?

 

This post was modified 3 months ago by HarriUp

Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV


   
ReplyQuote
(@judith)
Honorable Member Member
2549 kWhs
Joined: 1 year ago
Posts: 298
 

I spotted our value ages ago buried deep in a document/menu but now can’t re-find it!

It will be the same 4C as JamesPa’s value, assuming it’s the default. And I see no reason to change it.

That’s consistent with our old gas boiler inside the then unheated garage which kicked in at 7/8C (and did on cold nights). But the ashp has outside (no glycol but dump valves) pipes and it’s better that they don’t get to freezing and use the dump valves. As long as everything is working either the nighttime set back or holiday mode temperature will be much higher.

2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with it) open system operating on WC


   
ReplyQuote
Page 1 / 2



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security