No heat in radiators since heat pump failure
I have an Ecodan system that was working fine for the last 4 years until it failed in the cold spell back in December and promptly froze. After defrosting I had a company come out and repair which seemed to go fine and it heats water no problem but only get heat in about the bottom 2 inch's of all the radiators. They have been out and checked the system and say it is working fine !! All statistics and traces from Mitsubishi say it is working fine. Last recommendation from them was to replace the pump which I have done with the one they recommended and still no improvements. Getting to the end of my tether with them. Does anybody have any suggestions on what the problem could be and how to resolve? All rads have been bleed and all full
Weird that the pump is working (as per the latest team to visit) but you're not getting heat to the rads @tony-clarke. My first thought was distribution pump, but that's been replaced. Have you checked your expansion vessel? Is that pressurised and maintaining pressure?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Presume you've bled the radiators? Air might have got into the system during the service?
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
If the heat pump is producing warm water, then I would suggest tracing along the pipework from where it enters your home, measuring the pipework temperature to see where the warm water is going. Ensure any manual valves located on the way are fully open and any actuated valves are functioning correctly.
Has the system been drained down and refilled? If so you may possibly have an airlock somewhere, try opening the filling valve to increase the heating system pressure slightly then bleed the radiators again.
@tony-clarke , Derek’s reply prompted me to remember something that occurred to us a couple of years ago. Our heat pump was working fine, rads were hot, but the UFH stopped working.
We followed the pipework out of the heat pump to the UFH circuit and when we hit the Honeywell valve the water getting to it was hot, but the pipes after the valve were cold. As it turned out, the motor in the valve has died - we replaced it, and everything worked again.
So follow the pipes and see where that leads. Hopefully it’s something simple like a faulty valve.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Radiators that are only getting warm at the bottom only sounds like they are full of air. Easy to check that one. Has the Ecodan got either a manual flow gauge or automatic flow measurement? With all manual valves open, radiator TRVs open and zones calling for heat, easy to check if you have correct flow.
Pumps can cavitate if they are working against closed valves, when that happens their flow drastically reduces and air bubbles will be generated in the system as the pump suction tries to pull water that simply isn't there because something is stopping the flow, but the cause is usually quite obvious. Check all circuit isolation and service valves are open.
Hope it gets resolved soon!
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 402 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
Without knowing it, @andrewj, you've laid down the gaun...
By Majordennisbloodnok , 2 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@tasos and @cathoderay thanks. I have some history grap...
By benson , 6 minutes ago
-
I am having my existing heat pump changed to a Vaillant...
By trebor12345 , 39 minutes ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 1 hour ago
-
RE: Setback savings - fact or fiction?
@cathoderay The input power is largely determined by...
By RobS , 2 hours ago
-
RE: Electricity price predictions
@transparent Im impressed by all your work on this. ...
By JamesPa , 3 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Just to wrap this up here for future readers: The S...
By Batpred , 4 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 4 hours ago
-
RE: What determines the SOC of a battery?
I agree. Fogstar confirmed that the Seplos BMS does ...
By Batpred , 4 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 5 hours ago
-
@painter26 — as @jamespa says, it's for filling and re-...
By cathodeRay , 9 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 20 hours ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 22 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago
-
RE: DIY solar upgrade - Considering adding more panels
I know this is a bit old, but it made me wonder what co...
By Batpred , 2 days ago