Newbie: utterly confused with my Mitsubishi Zubadan air source heat pump running on 55C set flow temperature
@jamespa Thanks again for this info.
Just by way of an update, I’ve spoken to Mitsubishi support today and while they wouldn’t commit to anything because they’re obviously not in receipt of all the facts, he did say that a) he’s never seen a 14kWh machine on a single zone install before. And b) the flow rate is concerning. He said he’d expect 40l per hour rather than the often sub minimum 16 or 17 l per hour we’re seeing.
The R290 does sound like a good option but as you say; I doubt we’ll get the choice if they do arrange a swap.
Looking at the energy usage yesterday the COP is around 2.5 (or 2.9 if just looking at heating and not DHW).
Sadly the MelCloud charts don’t give you exact figures so there’s an element of guess work.
We seemed to see less cycling over the last 24 hours. Other than it bouncing around between 7am and 8am today it’s been fairly stable.
it was “buoyant” during warmer/sunnier hours yesterday (from 10am to 3pm) though.
Temperatures are looking warmer over the next couple of days so I’ll keep my eyes on it. My concern is that the $#!£ will really hit the fan when the weather gets warmer.
It may be unrelated but the concerns that @davidnolan22 initially raised about the low flow rate and also Mitsubishi’s reaction would suggest something’s amiss with the setup.
It does now feel like the size is overkill for this house.
We don’t have a diagram of the tank setup sadly. And I appreciate there’s a lot to try to fit into photos amidst the sea of lagging.
One thing that did occur to me is that we have motorized valves (image attached) on each manifold. When our original heating engineer was on site a few months ago he said we wouldn’t need that if we had a heat pump. He’s not a heat pump expert though.
Could that be causing an issue with performance?
Thanks for the legal references. I spent ages yesterday searching for them all but I couldn’t find the pertinent ECO4 references so this is all really useful again.
@sandman1600 just for comparison purposes and in case useful as evidence (!) here's my energy usage and flow temps for the same day and same Mitsi 14kW unit:
Mitsubishi Zubadan 14kW with Mixergy 210l DHW in 220m2 barn property. 24 solar panels = 9kWp with GivEnergy 5.0kW Hybrid inverter and 19kWh GivE batteries. Jaga Strada fan-assisted rads throughout. Landvac vacuum glazing/triple glazed windows.
Posted by: @sandman1600One thing that did occur to me is that we have motorized valves (image attached) on each manifold. When our original heating engineer was on site a few months ago he said we wouldn’t need that if we had a heat pump. He’s not a heat pump expert though.
If they arent permanently open then yes they would cause a problem (unless they are all wired to close simultaneously when the DHW comes on - instead of a diverter valve. But I think I saw a diverter valve in the photo. What opens/closes them, room stats?
Posted by: @sandman1600Just by way of an update, I’ve spoken to Mitsubishi support today and while they wouldn’t commit to anything because they’re obviously not in receipt of all the facts, he did say that a) he’s never seen a 14kWh machine on a single zone install before. And b) the flow rate is concerning. He said he’d expect 40l per hour rather than the often sub minimum 16 or 17 l per hour we’re seeing.
14kW is a big machine, the sort of machine you put in houses that are likely to have more than one zone. However it shouldn't be a problem.
I assume you mean l/min not l/hr. 14l/min would be normal for a ~6kW machine. 40l/min for a 14kW machine. I am guessing the installers adjusted it down to get a specific deltaT across the emitters but thats only really a guess. Or alternatively something in the circuit is limiting it. But the fact the house is getting hot suggests that you dont need much more!
I note 25kWh consumed for heating, about 70kWh delivered on the 16th, COP as you say ~2.8/2.9. One day alone is a bit meaningless but nevertheless, for comparison, my figures were 23kWh consumed, 96kWh delivered (COP 4). Thats for a 7kW house.
Heating COP 2.9 is a bit better but really you should be seeing better still now its warm during the day.
Posted by: @sandman1600Temperatures are looking warmer over the next couple of days so I’ll keep my eyes on it. My concern is that the $#!£ will really hit the fan when the weather gets warmer.
Costs should get better as it gets warmer. Heat pumps get more efficient as flow temp falls or OAT rises.
The Melcloud user manual shows plots of various things over multiple days https://library.mitsubishielectric.co.uk/pdf/book/MELCloud_USER_MANUAL_UK1#page-1 It would be really helpful if you got these for the key parameters (eg energy, flow temp, outside temp, indoor temp) since it was installed, preferably, if it will let you do so, on the same scale.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
There is a private website called mel cloud. This logs into your data via the internet and gives loads more data. It will give you the compressor output live.
What I would ask mitshi engineer would be whats the COP consequence of 16-17 l/minute through the I assume a lager heat exchanger of the 14kw unit too. I ask this as with flow on the 30s generally, the COP should be higher than that.
even though the flow rate is concerning, I’m not sure id turn it up or ask for it to be, as this will deliver more energy into the house. Not sure you need that.
this there any way to increase the flow through the manifolds (twist the knob) are Some showing more flow than others? This is tricky and balancing, but if you can increase secondary side flow and output, it would help
If you want to check what your pump speeds are set to here is the video, they can be set to 1-5 for heating and DHW as others have said 17L is low for a 14kw unit the recommended is 25L/min this is based on a dT of 8 which is what all Mitsubishi heat pumps are designed to.
Posted by: @davidnolan22even though the flow rate is concerning, I’m not sure id turn it up or ask for it to be, as this will deliver more energy into the house. Not sure you need that.
I think what will actually happen is that the deltaT from flow to return will decrease. There may be a slight increase in energy to the house (because the average emitter temp will be higher as a result of lower deltaT) but not much as energy to house is principally goverened by how much the emitters emit, which in turn is goverened by emmitter temperature and room temperature. The heat pump responds to this, not the other way round.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@gary Thanks for the link to the video. Appreciate it. I'll check out what its's currently set to but I'm reluctant to change it until I get a better idea of what I'm doing.
The MELPump website looks very promising. There's a lack of data on a lot of the reports at the minute but I assume it will start logging the daily data now I've signed up.
I'm very wary of anyone adjusting the flow temperature until I know what's going on. Looking at the Polypipe design documents it breaks down the circuit flow rate for each room and it's between 0.5 to 2 in each room. I'm assuming there is a way of controlling this on the manifold but I'm not sure I'm confident with changing stuff I don't really understand.
It looks like some of them are at slightly different levels.
- 27 Forums
- 2,495 Topics
- 57.8 K Posts
- 351 Online
- 6,220 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
@jancold I only discuss data.. Fogstar were not impress...
By Batpred , 10 minutes ago
-
RE: What determines the SOC of a battery?
@batpred Ironically you didn't have anything good to...
By Bash , 44 minutes ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
Here’s a current graph showing a bit more info. The set...
By benson , 58 minutes ago
-
RE: Setback savings - fact or fiction?
True there is a variation but importantly it's understa...
By RobS , 58 minutes ago
-
Below is a better quality image. Does that contain all ...
By trebor12345 , 1 hour ago
-
Sorry to bounce your thread. To put to bed some concern...
By L8Again , 1 hour ago
-
@painter26 — they (the analogue gauges) are subtly diff...
By cathodeRay , 2 hours ago
-
RE: Electricity price predictions
I am always impressed with how you keep abreast of so m...
By Batpred , 3 hours ago
-
RE: Humidity, or lack thereof... is my heat pump making rooms drier?
@majordennisbloodnok I’m glad I posted this. There see...
By AndrewJ , 3 hours ago
-
Our Experience installing a heat pump into a Grade 2 Listed stone house
First want to thank everybody who has contributed to th...
By Travellingwave , 6 hours ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Welcome to the forums.I assume that you're getting the ...
By Sheriff Fatman , 9 hours ago
-
RE: Say hello and introduce yourself
@editor @kev1964-irl This discussion might be best had ...
By GC61 , 10 hours ago
-
RE: Oversized 10.5kW Grant Aerona Heat Pump on Microbore Pipes and Undersized Rads
@uknick TBH if I were taking the floor up ...
By JamesPa , 1 day ago
-
RE: Getting ready for export with a BESS
I would have not got it if it was that tight
By Batpred , 1 day ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
@judith thanks Judith. Confirmation appreciated. The ...
By DavidB , 1 day ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
That makes sense. I thought better to comment in this t...
By Batpred , 1 day ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
My heat pump journey began a couple of years ago when I...
By Slartibartfast , 1 day ago
-
RE: How to control DHW with Honeywell EvoHome on Trianco ActiveAir 5 kW ASHP
The last photo is defrost for sure (or cooling, but pre...
By JamesPa , 1 day ago
-
RE: Plug and play solar. Thoughts?
Essentially, this just needed legislation. In Germany t...
By Batpred , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
@toodles Intentional opening of any warranty “can of wo...
By Papahuhu , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thanks @transparent Thankyou for your advic...
By Bash , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: Odd_LionManufacturer: SamsungModel: Samsu...
By Odd_Lion , 1 day ago
-
RE: Configuring third party dongle for Ecodan local control
Well, it was mentioned before in the early pos...
By F1p , 2 days ago