New Mitsubishi system, several concerns but just a newbie…..
We have just installed a 17kw cascade ecodan system. Seems too big to me - but the installer insisted based on property size (450 m2) despite our LPG historic usage being less than 30MW per annum which would suggest a 12kw system (and therefore not a cascade) not 17!
We have 10kw of solar panels and 15kwh of battery storage
it is not possible to monitor energy consumption via Melcloud (as it is a cascade system) and apparently Ovo won’t be able to tell how many kWh we have used either - so we can’t use their tariff. But I can’t believe that this is really the case? How is journey to net zero (etc) being measured if the API can’t cope with cascade systems?
the Ovo tariff isn’t available at the moment in any case - so we are with Octopus Cosy.
Because of the cosy tariff we do not want to heat water at peak electricity cost times - so I have configured this. But even though this is off from 16:00 to19:00 and no heat is being called the system still kicks in? Any idea why! Is the water heating timer somehow disabled (even though the controller is suggesting it is enabled?)
and the final point… we are using less energy than with LPG - but the cost per kWh is at least 25% higher on the cheapest tariff - and up to 350% higher on the most expensive. We need a very high SCOP just to break even. Why is gas (even LPG) so cheap compared to electricity?
- Oh dear! There are a lot of imponderables there! If OE can read your consumption - what are OVO playing at??? Perhaps an Ecodan user can assist with the DHW scheduling. I applaud your 10 kWp of PV (I only have 8.1 kWp. (in less than ideal orientation and with some shadowing problems)
- I have found Cosy to be a good deal as I do not have the option of an EV tariff - but I use 27 kWh of battery storage so I only use the lowest rate 8 hours each day. Our 97 sq. metres, well insulated semi is heated with a Daikin EDLA08 8 kW ASHP, as you say that you have your gas consumption figures, would your installer / surveyor not take that into account? Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles I think the installer wanted to up sell / up size so gave me a rubbish EPC for MCS purposes (wrong wall spec, omitted panels, omitted LED etc. etc. ) and not interested in our actual consumption ! I think they are worried about a subsequent owner wanting to heat the property much higher than we do.
@carpenterstationhotmail-com, given the size of your property, the 17 kW system might not be oversized. Have you got two 8.5 kW units? Even if your property is well-insulated, a 17 kW system might not be oversized; it could actually be on the lower end of what’s required, especially during colder spells. Your historic LPG usage might be lower due to intermittent heating or higher indoor temperatures, but heat pumps need to cover the full heat loss of the property when running continuously.
Regarding monitoring, it is surprising that Melcloud and Ovo can’t track energy consumption for cascade systems. This is a notable limitation, particularly as cascade setups become more common. I’ll contact Mitsubishi about this to get their feedback. I’ll also ask Ovo.
The cost comparison between electricity and gas (even LPG) is a sore point for many of us. Electricity prices in the UK are significantly higher, which makes achieving cost parity a real challenge. The key is to maximise your system’s SCOP through careful design, weather compensation and making the most of your solar panels and battery storage.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi Carpenterstation,
Welcome to the forum.
17kW Heat loss on a 450sqm property is definitely on the lower side, that's a peak heat load of just over 37w per sqm.
What's the construction type- was it a major renovation and did you fit MVHR/triple glazing etc?
If your system does not support energy monitoring by default then you may wish to fit a heat meter on each unit to measure the flow/return temps, energy input in kW to allow you to monitor the COP of your system. Examples of this are OpenEnergyMonitor kits, Sontex Superstatic, Kamstrup etc. There are plenty available but they are generally aftermarket.
You can also do this with a flow meter in some circumstances.
You are correct in saying that cascades are notoriously difficuly to monitor usage on and often the manufacturer's controllers don't allow you to view this. Do you just have the one FTC controller (Mitsubishi one)?
Rob at Cirrus Energy
Heat pump consultant and designer at Cirrus Energy.
Thinking about installing a heat pump? Or already have one but it’s not performing as it should? Book a one-to-one session with Rob to discuss things here.
@rob_cirrus_energy Wall construction is 100mm kingspan between concrete block and thermalite block for half the house (all built 2018 to building regs), and 75mm insulated plasterboard on the other half. Ground floor is all heavily insulated UFH (250 m2). All windows double glazed. EPC conducted by installer lists walls as “solid/ poor” - which is just wrong. Why would they do that?
I just have one Mitsubishi controller - not the easiest thing to get to grips with - and the timed water heating doesn’t seem to work, as it kicks in when the water is already hot enough, and nothing is calling for heat (at a time when I have configured the system not to use the 300% tariff). Short of switching off both pumps at 4pm I am not sure how I can avoid this window?
Are you using the scheduler for hot water or is it on constant, if its the latter as soon as the tank drops by a few degrees which will happen when some uses a relatively small amount of water the reheat cycle will kick in.
Sorry not entirely sure what you mean by “scheduler” or “constant”, but I have used the standard Mitsubishi controller to schedule when the hot water should be heated including setting the water to the “timer” icon (rather than always on or always off)
I'm afraid I've forgotten how to do this with the Mitsi controller so I might have to do some digging. However....
I have a similar issue with not wanting to heat the hot water tank during peak expensive times but I also don't want to schedule and therefore potentially heat when no heating is needed. As a result, my DWH is set to heat to 50degC and to start heating if the water temperature drops below 45degC. I have then used the controller to prohibit heating between certain times each day; it's a bit like holiday mode for short times. Sounds like that's what you're after.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Oh, and as far as monitoring is concerned Melcloud has always been seen as OK but limited.
I don't know how technically confident you are but one option available to you - admittedly at an extra one-off cost - could be to fit the heat pumps with the optional modbus module that Mitsi sell, the idea being to allow a system of your choosing to talk directly with the heat pumps and therefore bypassing Melcloud altogether. There are several to choose from (BEMS Interfaces | Mitsubishi Electric) and I've only really looked into the mini one for a single unit so it might need a bit of research but either way going down the modbus route is definitely a more "hands-on" alternative which will require a bit of a learning curve on your part in exchange for far more flexibility and control.
Not a recommendation; just a thought.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
@carpenterstation Here is a video that shows how to program the timer. If you restrict it only to times when you want it to heat then it won't do anything outside of the those periods regardless of what the tank temperature is.
@gary thanks Gary. This is the video I used to set the timer.
so the question remains - why are the units cycling when neither heat, nor hot water are being called?
- 22 Forums
- 2,056 Topics
- 44.9 K Posts
- 47 Online
- 3,293 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
Sounds like your 6kW unit is really just an 8kW with a ...
By logansmith01 , 3 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 3 hours ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 6 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
Here are the reported most common causes for both. Co...
By abbote , 6 hours ago
-
RE: Is your heat pump insured?
@johnmo sorry it comes across like that. The post is au...
By KevinPotts , 6 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo Perhaps a little detail might explain my reason...
By Toodles , 6 hours ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 19 hours ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 20 hours ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 23 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 1 day ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 1 day ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 2 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 2 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 2 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 2 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Took a while to find on the OFGEN site: ”The FIT sche...
By AgentGeorge , 2 days ago
-
RE: why solar diverters for HW instead of the heat pump?
For me there are few factors why you may want to heat w...
By Johnmo , 2 days ago
-
RE: Hydronic plinth heaters and ASHPs
@editor yes I think so. It will be a while until I get ...
By benson , 2 days ago