New Samsung 12KW Heat Pump Help
Posted by: @bontwoodyThe seem to think that the situation is the same as the Vaillant one
FWIW, the Vaillant app gives the energy efficiency (=COP) as (total heat generated including heat pump energy used)/ energy used. See this screenshot. However, the numbers don't quite add up.
Posted by: @bontwoodyUsing the adjusted calculation for the Samsung alters its COP to 4.76. Much closer to mine.
@bontwoody I think the fact that your Samsung displays generated energy as less than OEM generated energy whereas mine is the reverse may just demonstrate the inaccuracy of how Samsung measures flow rate and delta T. It uses external temperature probes whereas the heat meter uses pockets and paired probes.
I monitored what Samsung was displaying as delta T and flow rate through ESPHome and it correlated well with its displayed heat output of around 4kW. After an hour of stable heat output, generated energy had increased by 4kWh. So I am pretty sure that generated energy includes electrical input energy and is different to the Vaillant. It is noteworthy that the latter calls it environmental yield.
@mike-h Im not sure I follow you Mike. I can see that external temperature probes may differ from internal, especially if there is a long pipe run.
My interest in the correct formula is academic really, but there seem to be people on both sides of the fence.(see @technogeek here https://renewableheatinghub.co.uk/forums/renewable-heating-air-source-heap-pumps-ashps/new-heat-pump-owner-questions)
I think the argument about whether its called environmental yield or something else might be a translation one from the Korean.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@mike-h Im not sure I follow you Mike. I can see that external temperature probes may differ from internal, especially if there is a long pipe run.
@bontwoody Sorry for the lack of explanation. I was taking my comment from Glyn Hudson's recent observation on the OEM forum - "I found the onboard Samsung flow and return temperature sensors are quite inaccurate, if you do a mass flow rate calculation to calculate heat delivered it could be significantly inaccurate because of the inaccurate onboard sensors. My Samsung is 20% out. Heat meters use matched pairs of temperature sensors in wet pockets, which have maximum 2% error."
I was concerned that users with poor COPs might be falsely reassured that all was OK if they added electricity usage to generation before dividing by usage. Of course, if the Samsung consistently underestimates generation, then the poor COP might be completely false and using the G+EU/EU formula might be closer to reality. But if it overestimates it as often as it underestimates it then using the correct formula might be more important. At the end of the day, if you are happy with your electricity consumption then that is what matters.
@mike-h Yes, totally agree about false reassurance Mike. I was thinking that an error would always be in the same direction but I guess that doesnt have to be the case.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
- 26 Forums
- 2,171 Topics
- 47.8 K Posts
- 66 Online
- 5,744 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Big Changes Coming to Our Heat Pump System
Day 2 was a beast. All the excess zoning, on/off stats ...
By Mars , 6 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
Water pump will certainly make a hum (which could conce...
By JamesPa , 2 hours ago
-
@jamespa Thanks. Yeah any adjustments Ive made at pr...
By cliffhanger , 2 hours ago
-
RE: Mitsu PAR-WT60R Wireless Controller - options
I have been running mine in auto adapt since 2019 and i...
By Abernyte , 4 hours ago
-
RE: Powerwall 3 or Myenergi or something else?
Many of those tariffs are simple time of use tariffs, w...
By Temperature_Gradient , 14 hours ago
-
So far as I can tell designing for DT5, which is 'the n...
By JamesPa , 15 hours ago
-
RE: How to choose Towel Rails for an ASHP
@rob-nezard yes absolutely. Here is the link and a pho...
By GrahamF , 2 days ago
-
@mixergy Thanks for the update, I would appreciate some...
By bontwoody , 2 days ago
-
RE: Is Your Broadband Router the Weak Link in Your High-Tech Home?
Unfortunately I'm not that well connected 😂 ...
By Scalextrix , 2 days ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
It is interesting to see what our new Grant Aerona 290 ...
By GrahamF , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I've never physically seen it, but I seem to recall som...
By cathodeRay , 2 days ago
-
RE: Midea ASHP – how to set weather compensation
I noticed that too and thought the same thing, but then...
By cathodeRay , 3 days ago
-
RE: Ya can’t win! It is S*d’s Law!
@old_scientist If IOF is still running next late spring...
By Toodles , 3 days ago
-
RE: Electricity price predictions
Those of you on Agile will do well tomorrow; there are ...
By Toodles , 3 days ago
-
RE: Who’s Caved and Switched the Heating On Already?
We've been running our Ecodan system, installed in June...
By Sheriff Fatman , 3 days ago
-
Ok. Two schools of thought. The first is to run the ...
By JamesPa , 4 days ago
-
@drei Willing as I am to help, I don't think I'm yet ...
By JamesPa , 4 days ago
-
Selling 5 year old ASHP & Gas Combi Boiler - £590
Selling a 5-year-old Daikin Altherma Hybrid Air Source ...
By Paul G , 4 days ago
-
RE: Is a Valliant Inline 6kW heater a BUS buster?
Much of that is true in principle, but its not likely t...
By JamesPa , 6 days ago