I think it is so the water from the defrost cycle has somewhere to run too. Rather than over a path, freezing and causing a potential hazard. My installer asked the question and will fit a pipe (heated) and run off water will flow into the nearby drain. No soak away required 

Daikin Altherma 3H HT 12kWh ASHP with Mixergy h/w cylinder; 4kW solar PV with Solic 200 electric diverter; Honda e and new Hyundai Ioniq 5 N electric vehicles with Myenergi Zappi mk1 charger


   
ReplyQuote
(@kev-m)
Famed Member Member
5606 kWhs
Joined: 4 years ago
Posts: 1276
 

This is an extract:

4.2 Safer design of the condensate discharge

The product contains R290 refrigerant. In the event of a leak, escaping refrigerant may get into the ground via the condensate discharge. The refrigerant must not get into the waste­water system. For the ground installation, the condensate must be discharged via a downpipe into a gravel bed which is located in the frost­free area.

4.3 Safe execution of the condensate discharge,

The downpipe must flow into a sufficiently large gravel bed so that the condensate can trickle away freely. To prevent the condensate from freezing, the heating wire must be threaded into the downpipe via the condensate discharge tundish.
The downpipe must not be connected to an existing underground drain pipe that is connected to the waste­water system.

I assume it's because of the R290 refrigerant, which (courtesy of google) is propane.  But this is only in the event of a leak, it would normally be just be water that is discharged? 

But don't forget I'm just looking stuff up and don't have any experience of these matters!! 


   
👍
2
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26763 kWhs
Veteran
Joined: 4 years ago
Posts: 3030
 

@julianc, I guess that technically we have a soak away for water to run off into over gravel around the ASHP. To be fair, I've monitored that and it never discharges huge amount of water, but I suppose if it was on a pathway, it could freeze over and become dangerous.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote



Mars
 Mars
(@editor)
Illustrious Member Admin
26763 kWhs
Veteran
Joined: 4 years ago
Posts: 3030
 

@kev-m, that's actually really helpful and I never considered the refrigerant. My installers are here today, and I'll ask them about this.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@bobbt9866)
Estimable Member Member
0 kWhs
Expert
Joined: 4 years ago
Posts: 46
 

@kev-m

Never been asked for a soakaway across a wide range of manufacturers over decades.

I have just checked the LG manuals for the Therma V and they are more concerned with fixing the unit to a secure base.

Most manufacturers require a concrete base with the unit mounted on anti vibe mounts with adequate drainage, given the small amount of moisture produced during defrost.

If in doubt, pipe it away.


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
26763 kWhs
Veteran
Joined: 4 years ago
Posts: 3030
 

I have some clarity about the soak away on the Vaillant units and it's to do with the R290 refrigerant which is propane (and therefore flammable). Vaillant are therefore very strict on their installation criteria with regards to drainage, soak aways and clearances around and above the pumps.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@bobbt9866)
Estimable Member Member
0 kWhs
Expert
Joined: 4 years ago
Posts: 46
 

@kev-m

The best solution, of course, is not to have a leak in the first place!

This is why we insist on FGas registration to ensure that proper procedures are followed.

No gas should enter the system unless you are sure that the system holds a vacuum and passes pressure tests.


   
👍
4
ReplyQuote
(@witchcraft)
Reputable Member Contributor
614 kWhs
Joined: 4 years ago
Posts: 91
 

@frevillebabe Just had my Vaillant Aerothem Plus installed and as you say no condensate pipe has been provided, distilled water all over the patio.  I have just suggested to the installers that they supply a drain pipe on their snagging visit and I will dig the pit


   
ReplyQuote
(@bobbt9866)
Estimable Member Member
0 kWhs
Expert
Joined: 4 years ago
Posts: 46
 

@witchcraft The drain pan on the units should have a connection point, one or more, that allow connection of a drain pipe. The units require a strong base to stand on but provision needs to be made for drainage of condensate to a suitable point. It should be part of the site survey at the very least.

I attach a diagram of the LG Therma V base pan showing five drain connection options. they usually come with drain plugs installed to be removed as required.

 


   
👍
2
ReplyQuote



Page 2 / 2
Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security