My Mitsubishi ASHP has used 1078kWh from 25 November to 31 December – Help please
Posted by: @sarah@derek-m I'm not sure how to bleed out the air - is there normally a valve somewhere?
There will be an air release valve somewhere, but I'm not certain where it will be located, normally in the highest section. I suggest that you Google 'Air Release Valve' and look for something similar. If you provide a close up photo of your water pump, I will see if I can locate any details.
It would appear that you have 3 water pumps and what could possibly be a plate heat exchanger. I would need to be able to read the model number from the nameplate on the pumps or you could provide it.
Do any of the pumps have more than one cable connected?
OK looking at the picture of the three pumps - the one on the right has a fixed setting of 3, whereas the other two only light up on demand - although I've only seen the middle pump light up. I've just looked at the flow rate (at 21:50) and it is zero - so tomorrow morning - I will go down and sit in the machine room for bit and see if both the middle pump and the one on the left both "switch" on and then will see what the flow rate on the control panel is. Thanks once again.
Given that your living room wasn't getting up to target with a fixed flow of 40° then it is not surprising that changing it to a lower variable temp flow means it is struggling in a cold patch! The flow gauge at 28° seems like it is not as hot as the curve suggests it should be for the current conditions. Without Melcloud to easily monitor flow temps for the previous 24hrs it is down to you to read the controller panel to see what it is registering at the thermistors positioned one the hot water tank pipework – I think if you switch back to a fixed flow temp then you know what the unit is being asked to produce and you can see whether it is actually producing something like that. This comes with the caveat that actual flow temps do vary quite a bit as the system is working.
Looking at your spreadsheet I see you had a U1 alert, which I presume was down to the low water pressure, which should now be resolved. Generally your energy usage is reasonable given the area being heated (2/3 of my totals for Jan and Feb for example) but the amount of heat the unit calculates is being produced is not good, either in the raw figures or, clearly, in the rooms themselves. When the heating is running for several hours at 40° (lets assume it is) but a room is not getting warmer then something is awry.
Having a setback that has the effect of switching off heating going in for several hours does help keep electricity costs down especially with your solar production during the day but only if you can get enough heat out to raise the temperatures back up. The temps you have noted at 9am seem ok, not far off required temp unless it has been a colder night, and you say the bedroom and bathroom are getting up to temp but the living room isn't. A record of temps during the day would also help to highlight how fast the spaces are getting heat. Tedious I know, but it might help narrow down the source of the issue.
Although I have no experience of UFH systems I merely suspect that it is something possibly quite technical that needs investigation since you have had under-performance since installation.
.... I've just caught up with the latest few posts and I would say there is definitely an issue with some pipework somewhere. I know your Ecodan system is an earlier installation than mine but I don't think the basic design is any different. My pump speed set at 5 gives a flow rate of 26l/m, even 1 gives me 15l/m. The required flow rates are 11-24l/m so yours is at the bottom of the range. The question is why is it low – a faulty pump? or a restriction in the circulation somewhere?
What is the temperature like in your plant room? There is no insulation on that copper, including round the flow and return temperature thermistors clipped to the pipes! Not ideal.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Posted by: @sarahOK looking at the picture of the three pumps - the one on the right has a fixed setting of 3, whereas the other two only light up on demand - although I've only seen the middle pump light up. I've just looked at the flow rate (at 21:50) and it is zero - so tomorrow morning - I will go down and sit in the machine room for bit and see if both the middle pump and the one on the left both "switch" on and then will see what the flow rate on the control panel is. Thanks once again.
I would suggest that you check where each pump is connected and feeding. I suspect that the right-hand one may be for your DHW, since it appears to be connected to a plate heat exchanger. This pump should only run when the DHW is being heated.
The other two pumps could be feeding each of the UFH manifolds, but it is difficult to tell from photo's. See if you can sketch where the pipes are connected to the equipment.
If your rooms are not up to temperature then the central heating pumps should be running, along with the heat pump. If these pumps are not running then increase your thermostats by 1C.
- 26 Forums
- 2,417 Topics
- 54.8 K Posts
- 426 Online
- 6,096 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Sunsynk Whole House Backup Issue
I have options to do both. I'm an innovator, for whic...
By Transparent , 2 minutes ago
-
RE: Running my new Nibe ASHP efficiently
I didn't. I spent a while manually messing around with ...
By jamieheatpumpnew , 3 minutes ago
-
Hi, I think I’m having some issues with my Ecodan as...
By Patch321 , 12 minutes ago
-
RE: I’m glad the cold spell is over!
I comparison with the 65kWh used above yesterday was on...
By Judith , 16 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Hi, looking for help and advice as my installer is usel...
By LostandConfused , 21 minutes ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
@synthbuilder Further to the above…‘What a difference t...
By Toodles , 34 minutes ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
I should think so, I thought that pretty much universal...
By JamesPa , 1 hour ago
-
RE: Setback savings - fact or fiction?
I'm also inclined to look into how a defrost is actuall...
By cathodeRay , 1 hour ago
-
MLCP (Multi-Layer Composite Pipe) for ASHP
@editor nope. The info you reported was sufficient for ...
By iotum , 12 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
@robs Quick response while I'm in stationary traffic le...
By Sheriff Fatman , 12 hours ago
-
RE: Ideal HP290 14kW ASHP - how to optimise
@jamespa I wasn’t offended at all. You are very knowled...
By Davesoa , 13 hours ago
-
RE: Experience - New Build / Complete New Heating System
@vincro I would be surprised if it is much above 5 to 6...
By ASHP-BOBBA , 13 hours ago
-
RE: Post-Traumatic Heat Pump Stress Disorder
Yes bang on and maybe I can illustrate that by way of e...
By iotum , 15 hours ago
-
-
RE: Replacing my 18 month old Hitachi Yutaki ASHP
A big thank you to @jamespa for all his efforts online ...
By trebor12345 , 18 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor It is indeed for servicing. My current service ...
By Morgan , 19 hours ago
-
RE: Speedcomfort radiator fans
In case it helps Andrew Kuhne on openenergy monitor has...
By JamesPa , 20 hours ago
-
Things have gone quiet with you @drei. Any updates?
By Mars , 23 hours ago