My horrific Samsung heat pump installation and experience

946 Posts
28 Users
125 Reactions
45.9 K Views
(@jamespa)
Famed Member Moderator
10776 kWhs
Veteran
Joined: 2 years ago
Posts: 2032
 

Posted by: @iantelescope

 That would imply that I  cannot use Weather compensation without also using a Physical Thermostat

Sorry but I simply don't believe that.  Interpreting Samsung's language is difficult I concede,.

Clearly for wl to work there must be an external temperature sensor.  But equally clearly there is no need for an internal one.  Furthering if a third party thermostat were required Samsung would provide a spec.  

I will take a look much later but no way di I believe that a third party thermostat is required for wl to work 

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@iantelescope)
Prominent Member Contributor
2596 kWhs
Joined: 2 years ago
Posts: 430
Topic starter  

@derek-m 

 

Yes derek that is my desired end game,

but, ...............from experience over two years ...................at what cost ,where?

 

 

 

 


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10776 kWhs
Veteran
Joined: 2 years ago
Posts: 2032
 

Posted by: @iantelescope

On my Samsung the Thermistor on its own does not work with the Radiator motor still being controlled by an essential physical Thermostat!.

Thats because of how your installer wired it IE wrongly.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote



(@derek-m)
Illustrious Member Member
15283 kWhs
Veteran Expert
Joined: 4 years ago
Posts: 4429
 

Looking at the charts, I suspect that your heat pump was only running the primary water pump but not the compressor, but without being able to observe the process I cannot say for certain what appears to be happening.

 

This post was modified 7 months ago by Mars

   
ReplyQuote
(@iantelescope)
Prominent Member Contributor
2596 kWhs
Joined: 2 years ago
Posts: 430
Topic starter  

@jamespa 

In itself , the Samsung Weather compensation , aka Water law  is excellent , with my water temperatures following the Water Law graphs perfectly .

As the French Samsung engineer said , the Water Law , WL , Weather compensation will save about 7 to 10% of your running costs .

In my experience , an accurate estimate.................

My installer complained that Samsung had not supplied a Thermostat , ( along  with several other components) in the initial package.

The Thermostat appearing some three weeks after the start of the installation.

Certainly My Heat Pump , currently will not work without a Thermostat to switch the Radiator motor ON.

currently , a Heat Pump that will not provide heat without a Thermostat!

This post was modified 7 months ago by Mars

   
ReplyQuote
(@iantelescope)
Prominent Member Contributor
2596 kWhs
Joined: 2 years ago
Posts: 430
Topic starter  

@jamespa 

Thermostat Wiring:

The Physical Thermostat wiring was done by Telford under the instructions from Samsung,  not , for once, by my "installer".

The External Physical Thermostat has two connections :

1) starting the Radiator , Secondary water loop motor.

and

2) Connected to the RUN input terminal , the Physical Themostat starts  the Compressor Running.

This , with the WL Thermostat is the logical OR given in the 2091/2092/2093 options 2, 3 or 4 .

Certainly , currently, my Heat pump will not heat without a Physical Thermostat.

Other Samsung s will be different however.

This post was modified 7 months ago by Mars

   
ReplyQuote
(@jamespa)
Famed Member Moderator
10776 kWhs
Veteran
Joined: 2 years ago
Posts: 2032
 

Posted by: @iantelescope

Certainly My Heat Pump , currently will not work without a Thermostat to switch the Radiator motor ON.

currently , a Heat Pump that will not provide heat without a Thermostat!

Once it is replumbed there won't be a radiator motor, there will be only be one motor switched by the heat pump.

Posted by: @iantelescope

2) Connected to the RUN input terminal , the Physical Themostat starts  the Compressor Running.

This , with the WL Thermostat is the logical OR given in the 2091/2092/2093 options 2, 3 or 4 .

Certainly , currently, my Heat pump will not heat without a Physical Thermostat.

Other Samsung s will be different however.

This needs to be reworked, either by changing the fsvs or by rewiring, so that the thermostat is not necessary.  Then the heat pump can use it's own temperature sensor to decide what to do.  I don't have time to look at this now but perhaps you do.  I'm at least 95percent sure you don't need a thermostat and that you can use the internal sensor which is designed for the job unlike any third party component.

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@iantelescope)
Prominent Member Contributor
2596 kWhs
Joined: 2 years ago
Posts: 430
Topic starter  

@derek-m 

Hopefully, @derek-m I will have another series of Cloud cloning spectaculars this winter.

My point was , however, no matter what was happening, it was unobserved , happening in the middle of the night , and  consuming no energy!

The large amount of heat was either coming from the Hot Water tank , a perfectly valid alternative , or, from the Buffer tank.

The clouds cost nothing! The Heat Pump was saved!

My further point is that the Buffer tank , initially required by Samsung-Dallium , later required for de-icing duties appeared to work!

Alternatively , the Hot Water tank , which can also dump hot water into the Heat Pump during de-iceing incidents may  also have worked!

Either way , somebody got it right!

This post was modified 7 months ago by Mars

   
ReplyQuote
(@jamespa)
Famed Member Moderator
10776 kWhs
Veteran
Joined: 2 years ago
Posts: 2032
 

All noted.  Can you post the version of the controller manual you have please so when I look at fsvs there is less scope for confusion

The heat for deicing comes from the system whether it is the house, buffer tank or pipework.  It has to be replaced when the heat pump starts working again, so its not free (nothing is free In thermodynamics).  In your case, unless the radiator motor is forced on during deicing (by what?) then, unless there is also a call for heat from your thermostat, the radiator motor will be off and, as @ derek-m says, only the primary circuit will contribute heat.  Anyway that is now in the past.

It seems to me there is a case for an arrangement of valves so that a buffer tank supplies the deicing heat, not the house, which is recharged when the pump is back in heating mode.  I've not seen this in a diagram though, perhaps someone else has.

Can you post the version of the controller manual you have please so when I look at fsvs there is less scope for confusion.

 

This post was modified 7 months ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote



(@iantelescope)
Prominent Member Contributor
2596 kWhs
Joined: 2 years ago
Posts: 430
Topic starter  

@jamespa @Mars 

Gremlins return !!

 

Sorry @jamesPa and @derek-m , the gremlins have returned ...................... I may , again be cut off .

RSVP

@jamespa I can easily allow for a option to try and operate without a Thermostat.

 

I Do , however , want to see and Control the Water Law Thermostat .

With  Weather Compensation 1

My other requirement is to stop this expensive Winter Journey:

Energy consumption 22 24

 

 

 

 


   
ReplyQuote
(@jamespa)
Famed Member Moderator
10776 kWhs
Veteran
Joined: 2 years ago
Posts: 2032
 

Posted by: @iantelescope

I Do , however , want to see and Control the Water Law Thermostat .

The water law thermostat as you call it is the external temperature sensor and the internal sensor measuring the lwt.  You cant control either, they only measure things.  What you can control is the water law itself. 

In addition it's clear that the temperature sensor inside the wired remote can have a  function (other than just reporting it) if the fsvs are correctly set.  It's not clear what but I strongly suspect it's temperature limiting.  This would be logical and would trigger a tweak in the best methodology for setting up the water law curve.  I will explore further once you post your version of the manual.

Posted by: @iantelescope

My other requirement is to stop this expensive Winter Journey:

Energy consumption 22 24

 

You will get a similar shape curve for certain.  The expectation is that it will be lower however, but the shape won't change materially because that's the weather.  Unless you have connections much more senior than any I have, control of the weather is not within your gift.

 

Can you post the version of the controller manual you have please so when I look at fsvs there is less scope for confusion.

This post was modified 7 months ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@iantelescope)
Prominent Member Contributor
2596 kWhs
Joined: 2 years ago
Posts: 430
Topic starter  

@jamespa 

Sorry , @jamespa  the gremlins have struck cutting your message in half!

Can you try again?

Manuals:

I do not have a software copy of the manuals for my Heat Pump for my exact type of heat pump ,but ,

I have the old , 2013 set of manuals.

I have a newer , probably better , more up to date version , undated .

I have a software newer generation 6 manual  which do not quite apply  to my Heat Pump ..

 

 

 

ian

 

 

 

 


   
ReplyQuote
Page 59 / 79



Share:

Join Us!

Heat Pump Dramas?

Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.

Pre-Installation Planning
Post-Installation Troubleshooting
Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)

👉 Book a one-to-one consultation now.

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security