Mitsubishi Ecodan & Raspberry Pi automations
Hi. I'm a webmaster (and server admin/software developer/troubleshooter) based in Norfolk, with an Mitsubishi Ecodan ASHP installed last autumn, monitored by both melcloud and an Raspberry Pi running OpenEnergyMonitor (because the melcloud user interface is poor). At the start of this month, I started letting a program on the Pi use the controls to make adjustments of the sort I was making manually (which I can't find any way to program into the ecodan controller), but it does goes to sleep if detects someone else using the controls. I've registered on the forum after lurking for a while because I saw a problem I thought I could answer.
@mikefitz some examples:
- adjusting the target temperature by a few degrees with the strength of wind or sun: we're in a fairly windy location, but get good evening sun, but the system has only one thermometer on the landing where it's fairly stable, so it's the last to know it needs to adapt. I guess we should have put it in a different location or added a remote sensor: benefit of hindsight! The Pi has its own thermometer connected too and gets weather reports and forecasts;
- heating a tank of water a bit hotter than usual on warm late afternoons: so it ends up a similar temperature to letting the water run out mid-evening and reheating as usual but costs less because COP is better when it's warmer;
- running the heating for an hour after heating the water tank, because it beats bringing the system up to temperature from cold twice — unless the house is already hot and unlikely to need further heat today. The Pi tries to estimate if that's the case from time and forecasts; and
- pausing heating (actually dropping the target temperature 3 degrees temporarily) when the predictions were a bit wrong and the house is overheating. If I don't do that and leave it solely to Mitsubishi's "auto adaptive", the heat pump starts cycling frequently for a while, which reduces COP.
@derek-m the system runs with weather compensation except for when the heating is "off" overnight or after overheating. As I hinted at, the auto adaptation does not seem to work well for our house, but this may be due to the controller thermometer being in a stable-temperature room instead of the living room. It seemed to get worse after the last firmware update in November and it irritates me a bit that we do not know the specifics of how it is intended to work, or what changed in the update.
I don't think the controller would do the other tweaks in any mode, though.
Posted by: @mjr@derek-m the system runs with weather compensation except for when the heating is "off" overnight or after overheating. As I hinted at, the auto adaptation does not seem to work well for our house, but this may be due to the controller thermometer being in a stable-temperature room instead of the living room. It seemed to get worse after the last firmware update in November and it irritates me a bit that we do not know the specifics of how it is intended to work, or what changed in the update.
I don't think the controller would do the other tweaks in any mode, though.
Hi mjr,
I suspect that you are perfectly correct, that certainly the Mitsubishi, and I don't believe any other manufacturer, have controllers that take account of solar gain and additional heat loss due to wind and rain. Though it would be quite feasible, I don't know that any manufacturer would bother to create such a system, since it would require the addition of a number of sensors, which would require careful positioning, and software that even if it can auto tune, would need to be adapted to the requirements of each individual property. I don't think that there would be many customers willing to pay the added cost that such a system would entail.
From the observations and tests that I have carried out over several years on our home heating system, the above external affects happen very slowly in most cases, so should be adequately accommodated by a correctly configured auto adaptation system.
The reason I was asking about the settings of your weather compensation parameters, is that I suspect if these are not correctly adjusted in the first place, then when auto adaptation control is enabled, it may not respond correctly as the outside air temperature varies. You could check this by switching off auto adaptation for a while, and see how the indoor air temperature varies with changes in outdoor air temperature. If the indoor air temperature does not remain within 1C of the desired temperature then the weather compensation parameter settings may need to be refined.
If you would care to provide details of what it is that you are trying to achieve, I may be able to suggest a design that more closely meets your requirements.
@derek-m I am using straight weather compensation ("curve" mode) most of the time because it works fine, holding temperature unless the wind changes (there is one line of trees a few hundred metres to our SW then flattish farm fields for 10 miles, to the NW no trees and 6 miles of fields). I read posts from you on here when setting it up, so belated thanks for that.
As mentioned, the auto adaptation mode doesn't work as well, which makes me think it's not starting from the same curve.
Posted by: @mjr@derek-m I am using straight weather compensation ("curve" mode) most of the time because it works fine, holding temperature unless the wind changes (there is one line of trees a few hundred metres to our SW then flattish farm fields for 10 miles, to the NW no trees and 6 miles of fields). I read posts from you on here when setting it up, so belated thanks for that.
As mentioned, the auto adaptation mode doesn't work as well, which makes me think it's not starting from the same curve.
Hi mjr,
Auto adaptation is the type of control that is normally used in industrial control systems.
In its most basic form, the variable to be controlled is measured using a suitable sensor, this Process Variable (PV) as it is normally described is compared against the desired Setpoint (SP), the resultant being the error. Obviously the error can have a positive or negative value, dependent upon whether PV is greater than SP or lower than SP.
These signals would normally be fed into a 3-term PID controller, the three terms being Proportional Action, Integral Action and Derivative Action, which you will no doubt recognise as mathematical functions, since the controller is merely performing a complex calculation. The output signal is then used to drive some form of actuating device, which hopefully will keep the process variable at approximately the desired setpoint.
An industrial controller can be configured for P only control, PI control, PD control or PID control, dependent system requirements and response times etc. The P, I and D settings are also adjustable, which allows fine tuning of the system for optimum control.
A heat pump controller probably contains a similar algorithm, which may have some self tuning capability, but as you are aware it is not possible for the end user to see what is actually happening within the controller itself, or make any adjustments that would change the characteristics or response of the controller.
Wind speed and direction is more likely to have a more rapid effect on the indoor temperature, particularly if there are areas where there are possible drafts due to leaky seals round windows and doors. It would probably be useful to monitor the wind speed and direction and also record the variations caused to the indoor conditions. This may then highlight areas to investigate for possible drafts.
Posted by: @mjr@derek-m I am using straight weather compensation ("curve" mode) most of the time because it works fine, holding temperature unless the wind changes (there is one line of trees a few hundred metres to our SW then flattish farm fields for 10 miles, to the NW no trees and 6 miles of fields). I read posts from you on here when setting it up, so belated thanks for that.
As mentioned, the auto adaptation mode doesn't work as well, which makes me think it's not starting from the same curve.
From what I have read on other forums, the Ecodan auto adaptation function doesn't use the weather compensation curve. Instead it uses the room and outside temperature, with some sort of 'learning' function. There are a couple of implications; if you're heating your house up from cold it will boost the flow much higher than your weather compensated curve so you'll get a warmer house quicker but higher bills. It's also been suggested that in the event of a power down, the learning is forgotten and has to be done again.
But this is only what I've heard and I've never used auto adaptation myself...  Â
EDIT - a Mitsubishi-trained engineer I spoke to who knew I was successfully using weather compensation without thermostats advised me not to bother with auto adaptation.  Â
Hi Kev,
I can't remember if it was in the Ecodan manual, or some other manufacturers manual, where the instruction was to set the weather compensation parameters before enabling auto adaptation.
I would expect the control algorithm, within the FTC controller, to initially set the water flow temperature dependent upon the outdoor air temperature (weather compensation) and then fine tune the control to achieve the desired indoor temperature (auto adaptation), with both working together.
The 'learning' capability I suspect is the self tuning aspect, where the controller adjusts the internal control parameters to accommodate the response times of your particular system. I would have expected these parameters to be stored in non volatile memory, so should not be changed by a power shutdown. It is possible that they could be changed by a full reset, or the installation of updated software.
If you find any further details I would be interested to know.
- 21 Forums
- 1,983 Topics
- 43.2 K Posts
- 32 Online
- 2,309 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@sunandair I can't get my system higher than 35 or 3...
By davidnolan22 , 26 minutes ago
-
RE: Confused about Samsung Gen6 Hot Water Controller
As far as I am aware the only way to persuade the heat...
By DerekDeLeon , 1 hour ago
-
RE: Nibe F2040 ASHP PCB failure
@delta I’ve raised this with NIBE today. Their team is ...
By Mars , 10 hours ago
-
RE: Are MCS are finally improving (some of) their guidelines?
Encouragement of installers to take account of the emit...
By JohnR , 10 hours ago
-
RE: Smart TRV experiences (ideally integrating with Midea heat pump)
Yes, I'd read that and already knew that LSVs exhibit a...
By madbilly , 10 hours ago
-
In our case the pipe run for the heat pump is short and...
By madbilly , 10 hours ago
-
Plug and play solar. Thoughts?
What do you think of these plug-and-play Balcony Solar...
By Lucia , 13 hours ago
-
@toodles no, unfortunately we don’t have access to the ...
By Simon and Zoe , 13 hours ago
-
RE: The EPC Dilemma: How Current Ratings Fail Heat Pumps
Hi, im not an expert on EPCs but today got a D for my 1...
By rodwebster , 14 hours ago
-
@sandman1600 What I mean is, your UFH power is 79wm2...
By davidnolan22 , 14 hours ago
-
RE: Vaillant AroTherm Plus 7kW
Thank you James for such a complete write up. We also h...
By Judith , 15 hours ago
-
RE: Ecodan Auto Adapt Questions
It wasnt me that mentioned this, was someone else, I wa...
By JamesPa , 15 hours ago
-
RE: Renewables & Heat Pumps in the News
In a move that potentially promises to benefit homeowne...
By Mars , 15 hours ago
-
RE: Vaillant water pressure gauge vs Analogue gauge
I have the same, so equally interested in the answer. ...
By JamesPa , 15 hours ago
-
RE: Thinking of ripping our my IVT Greenline HT Plus C model and replacing with a gas boiler.
Somebody has to pay for their ignorance! In fairness ...
By JamesPa , 20 hours ago
-
Thats simply not true (to any material extent), which i...
By JamesPa , 1 day ago
-
Database of heat pump performance data?
Hi all, I really like Heatpunk, especially the way th...
By madbilly , 1 day ago
-
RE: Air source heat pump roll call
Good idea 🙂 Manufacturer: MideaModel:10kW R32 Monob...
By madbilly , 1 day ago
-
RE: What is the best approach for primaries in heat pump installations?
Don't forget there is no such thing as zero loss insula...
By Judith , 1 day ago
-
RE: Battery storage to run Heat Pump.
@transparent Flexibility Services are different to w...
By Lucia , 2 days ago
Latest Topics
-
Plug and play solar. Thoughts?
By Lucia 13 hours ago
-
By JamesPa 15 hours ago
-
Vaillant water pressure gauge vs Analogue gauge
By jeegnesh 17 hours ago
-
Database of heat pump performance data?
By madbilly 1 day ago
-
By madbilly 1 day ago
-
Confused about Samsung Gen6 Hot Water Controller
By ntruby 2 days ago
-
help with new bathroom and towel radiator
By AdamK 3 days ago
-
Grant Aerona fine tuning advice needed
By Stopbar 3 days ago