Mitsubishi Ecodan 8.5kW Monobloc (FTC5) Defrost Mode
@davidnolan22 I will continue to think about this.
We could do with a comment from @bobtskutter on the pump arrangement , he is good on the hydronics. It feels like there is the potential for the 4 pumps on the emitter side to create a racetrack around the LLH which could exclude or inhibit energy from transferring across from the heat pump side.
Furthermore since, at max output, you need a DT of 6 there is the likelihood of quite a sizable penalty due to the mixing. Given that you appear to have separate returns from the various emitter loops, I can see an easy way to get a handle on flow rates either side.
I would also imagine that its impossible to keep this in balance with zones opening/closing, so treating the whole house as a single zone, which you are currently doing, may well be sensible.
Its good that it is at least almost working, and agree it shouldn't be this difficult. The installer really needed to think about why it was sensible to have 5 separate pumps in the system and how they were going to work seamlessly together, but evidently he didnt.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hi Gary,
Yes, I think I’m getting the hang of it and whats gone on this winter. And yes, during the cold snap previously there was not enough energy going into the floor constantly. But I’ve been told to set the flow to 45 and use the stats.
After I set the flow much lower, in the low 30s and ran it constant, it ran so much better. I think my system design temp is 36 at -3 not 45. Despite that not being the plan…..
Anyhow, the new header has not helped matters much, but I’ll get it back balanced as best I can and I think I will be able to get it to work.
And then the defrost. I’m if the secondary circuits are meant stay open due to the lower temps and not enough volume and the primary loop, is there a way to protect the system during heavy defrost conditions. I assume it’s total system volume.
I’ve got 65L in the UFH that I know from the UFH design. I’ve got 6 big rads, so maybe another 60 to 80. The the pipes to and from things.
maybe 175L total volume for 11.2kw systems. Is that optimal? I know paul Spence put a post about 25L per KW, which is 280L for me. Or is this overkill? Again, I’m told so many different things it’s hard to make heads or tails of it.
@jamespa thanks again. It makes sense. Before the new bigger LLH, I had a 35mm piped distribution header. There was no blending there, only when I put the UFH flows too high, past I assume the 28l a min on the primary, and this was only on the rad circuit. As soon i turned down a flow on the UFH a bit, the rads went straight back to the primary temp sensor. That was kind of my guide of when to stop increasing flows in the UFH
Posted by: @davidnolan22And then the defrost. I’m if the secondary circuits are meant stay open due to the lower temps and not enough volume and the primary loop, is there a way to protect the system during heavy defrost conditions. I assume it’s total system volume.
I’ve got 65L in the UFH that I know from the UFH design. I’ve got 6 big rads, so maybe another 60 to 80. The the pipes to and from things.
maybe 175L total volume for 11.2kw systems. Is that optimal? I know paul Spence put a post about 25L per KW, which is 280L for me. Or is this overkill? Again, I’m told so many different things it’s hard to make heads or tails of it.
The spec for your model calls for a total of 39l for 'cooler climates'. I think we are in the 'warmer climate' region according to the relevant EU directive, but since we are also very damp I would be wanting 39l plus. There is absolutely no harm in 'additional' volume; 175l should be fine.
I dont know about 25l/kW, this might be a figure to reduce cycling but you haven't yet posted a problem with cycling and, since your heat pump appears to be well matched size wise to your house you most likely wont!
There should be no need to 'protect' the system, if it needs so much heat for defrost that it is going to materially cool the house then something radical needs to be done (like a very large volumiser which can somehow be separated) but again no evidence you need this nor have I heard of a case where it is needed. The amount of energy required for defrost is pretty predictable so it shouldn't be a problem.
For now Id balance the system as best you can, adjust the WC curve if needed to get the house at the right temperature with everything running constantly and all the stats set above the desired temperature, and see how it goes. We may not get another deep frost until next season, so you may not know for a while!
Posted by: @davidnolan22Again, I’m told so many different things it’s hard to make heads or tails of it.
Heating systems, not just those with heat pumps, can be quite complex, because there are so many variations and variables. That said, the underlying physics, and it is physics, is actually very simple, so a little genuine understanding goes a long way. However only a proportion of 'professionals' actually seem to understand it, many go 'by experience' and some spout pure BS. That's just how it is. The simple test is to ask for an explanation and, if one isn't forthcoming, or it doesn't make sense, or its 'because we have been doing it like that for 40 years, then doubt the advice!
Not content with that problem, we make heating systems more complex by trying to impose control that, in reality, we dont have because of the thermal mass of the house and the fact that rooms within the house aren't thermally separated to any material extent. This is counter-productive to cost in many, perhaps most, cases with a heat pump (and even in at least some cases with a boiler). However the manufacturers of 'smart' controls would go out of business if they told us that!
Time and time again we find on this forum that KISS applies (Keep it simple, stupid). Most houses, including, Im fairly certain, yours, would be best (cheapest and most comfortable) run on a single zone (with perhaps TRVs on a small minority of emitters, eg in some bedrooms), 24*7 on pure weather compensation and without system separation. Unfortunately only some installers currently do this!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I think many installers feel that they have not completed an installation if they haven’t fitted an LLH, TRV’s on every radiator (without leaving instructions to leave them wide open as they are only really to tidy up the look of the emitter in most rooms!😉) a secondary pump plus an on/off thermostat to knacker the heat pump when it has a hysteresis of 0.1 degree C and has no pity at all on that heat pump’s life; extra satisfaction may be gained by these same installers if they can include a third pump and a buffer tank too! 😉 Ruefully, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 22 Forums
- 2,070 Topics
- 45.3 K Posts
- 76 Online
- 3,343 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Home energy storage & battery register
Really depends how you use them, and how you have them ...
By Johnmo , 49 minutes ago
-
Check the detailed specs. 7kW Vaillant is actually 8kW...
By JamesPa , 52 minutes ago
-
RE: Heat pump installation and BUS Grant timings
Where do you get the requirements for EPC rating above...
By Johnmo , 1 hour ago
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent ‘Protein’s extra Luv’.
By Toodles , 2 hours ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnnyb I was on Smart, mostly because I was on Agile ...
By Arundalep , 15 hours ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 21 hours ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@johnmo You are correct, standard Ethylene glycol used ...
By Brendon Uys , 22 hours ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 1 day ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 1 day ago
-
RE: Kensa GSHP finally installed - now to start the optimisation process
Just had a quick scan of the manual and should be weath...
By Johnmo , 2 days ago
-
RE: Potentially more choice including air to air heat pump grants
Hi all, I agree, the consultation documents are alway...
By madbilly , 2 days ago
-
RE: Commencing on an ASHP Installation Process
I think those are pretty much the standard figures that...
By JamesPa , 2 days ago
-
RE: Load Compensation and Weather Compensation
I think that maybe what the adia thermal system does, b...
By JamesPa , 2 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
@old_scientist @profzarkov thanks to you both for the v...
By Grahamh-uk , 2 days ago
-
RE: Nibe F2040 periodic warm water increase fails
@tribol here's an official reply from NIBE on your case...
By Mars , 2 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
@ecodan-efficiency On the other hand, the fact that the...
By Richard24738 , 3 days ago
-
RE: How accurate was your heat loss survey?
@scalextrix for our house 1950s detached the air leakag...
By Judith , 3 days ago
-
-
RE: Air Changes per Hour - ACH and the MCS requirement
@matwin If you plan to commission one it might b...
By JamesPa , 4 days ago