Mitsubishi 8kW - strange energy use readings
Posted by: @westkentone issue I’m having is that my hot water loses very close to 1 degree an hr throughout the day.
I do have an annual service in a few weeks so I’ll mention it.
Mine loses about 0.6 degrees per hour so a bit less. Is your HW tank outside the house, e.g in the garage? That would make it lose a bit more than in the house.
170L tank in the airing cupboard where the immersion tank was.
pipes arnt lagged that feed off the tank which I’d imagine they should be although I’d of thought that reason alone wouldn’t amount to 1 degree an hour??
It will lose heat through the tank insulation as well as the pipes. The pipes will make a small but significant difference. Your tank is smaller than my 250l one so the pipes, etc., will have a bigger effect. If you're really interested in HW tank heat loss then have a look at this.
Also, what is your HW temperature? The hotter it is, the faster the tank will lose energy. A 55 deg tank will emit more heat (i.e. lose energy faster) than a 45 deg one.
Let us know what the engineer says.
Hot water is timed to come on between 5am to 7am at its maximum 60c at 9.5p/kWh.
Thats ample enough h/w for 2 showers and the washing up.
My upcoming service will be carried out by a contractor from the Housing association not Mitubushi unfortunately so I’m unsure how knowledgeable they’ll be with advice on the settings.
My COP over the last 2yrs is only 2.4.
Iv recently changed my setting from adaptive room to curve although we’ve not really used the heating side since the change of setting.
Posted by: @westkentHot water is timed to come on between 5am to 7am at its maximum 60c at 9.5p/kWh.
Thats ample enough h/w for 2 showers and the washing up.
My upcoming service will be carried out by a contractor from the Housing association not Mitubushi unfortunately so I’m unsure how knowledgeable they’ll be with advice on the settings.
My COP over the last 2yrs is only 2.4.
Iv recently changed my setting from adaptive room to curve although we’ve not really used the heating side since the change of setting.
Based on mine, I suspect your losses from the HW tank are as expected. It's not going to cost much; mine costs less than 2kWh per day to maintain temperature even if I don't use any.
Is that your heating COP or overall?
I moved to auto adapt last winter and found COP went down but overall consumption was the same or a little less. With AA you need to be careful if you vary your room temp because AA bumps the flow up quite high when heating up to a target room temperature.
It seems a shame that Mitsubishi can't or won't explain the misreporting of energy consumed, I wonder whether it is a data recording issue rather than measurement issue. It is noticeable that on days when a hot water cycle runs for 1 hour and the remaining 23 hours have no actual heating generated that the system records 2.3kWh consumed – 100Wh each hour. All the reports out of MelCloud are given to 0.1 kWh or 100Wh – there will be a minimum unit of use that is recorded and if the unit is recording in blocks of 100W then it won't distinguish between 0< and 100W. So the 25W or so it draws is inflated from under 0.6 kWh to 2.3kWh. Though as I also find that when there is no hot water cycle either, i.e. just a continuous 24 hrs of not running the pump at all, this figure rises to around 3kWh then it's either a curious anomaly or proves I am spouting nonsense.
All water tanks will lose heat at a rate that Mitsubishi have measured. For a 170l tank they give a standing loss of 1.63kWh over 24hrs. Which I think is measured from a tank filled at 60°. But that will be a best performance and the tank won't have had heat-conducting copper pipes connected to it when that measurement was done. If I grasp this correctly that rate would equate to the water losing around 8° over those 24 hours. My tank pipework was not lagged initially and it was noticeable how warm it made the space it was installed into, and how hot some of those pipes felt. Even the hot water loop that circulates through the heat exchanger would still feel hot several hours after a cycle suggesting to me that the water in the loop was passively circulating from within the tank as it cooled in the pipe. It is damned fiddly trying to insulate the tank pipework as it is all bends and valves and pumps but you are reducing heat loss from the one part that you are trying to keep really warm 24/7/365.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 43 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Midea ASHP – how to set weather compensation
All previous releases are archived on the Planning Port...
By Transparent , 4 hours ago
-
My Samsung Gen6 (probably same controller as yours) onl...
By Old_Scientist , 7 hours ago
-
@drei When I was in local government we were of cours...
By JamesPa , 7 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 9 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
@rob-nezard you can see more of Drei's rad dramas here ...
By Mars , 9 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@drei I will say again that Im sorry to heat about your...
By JamesPa , 10 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 21 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 22 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 23 hours ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 1 day ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 1 day ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 1 day ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 1 day ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 2 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 2 days ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 2 days ago
-
What is the Heat Geek Guarantee?
We regularly hear from homeowners who are researching i...
By Mars , 3 days ago