Midea "ECO Mode" - an oxymoron
Does anyone have any docs on what the purpose of ECO Mode is on Midea heat pumps? One would assume it mean "economical" or perhaps "ecological", however as far as I can see, it is neither.
Consider the following:
With ECO Mode on, Weather Compensation is disabled, the flow temperature is set to 1°C above what the non-compensating flow temperature is, the energy consumed goes through the roof, and the heat output is not really any higher than it was with ECO Mode off!
ECO Mode is only of use when using the pre-programmed Weather Compensation curves as described from page 104 onwards in the detailed Midea data.
When ECO Mode is selected, it changes the controller from curve 4 to curve 6, which lowers the specified LWT.
If you are using curve 9, which can be adjusted by the user to match the home's heat loss, then switching to ECO Mode could actually increase the specified LWT.
- 26 Forums
- 2,406 Topics
- 54.6 K Posts
- 399 Online
- 6,092 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Post-Traumatic Heat Pump Stress Disorder
@jamespa Thanks James - and yes yes - am v grateful to ...
By johnbroome , 3 minutes ago
-
RE: Heat pump not reaching flow temperature
Interesting. Judging by my house which is different is...
By JamesPa , 6 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
No because its NOT connected to the neutral, its connec...
By JamesPa , 1 hour ago
-
RE: Please help with the settings ecodan
Hi and welcome to the forums.Does your system use a Mit...
By Sheriff Fatman , 1 hour ago
-
RE: New Daikin 11kW Altherma 3M install - is it working as it should?
I forgot to mention: Octopus measured our heat loss at ...
By Toodles , 2 hours ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
Thanks Mars and thank you for reaching out to so many p...
By iotum , 3 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handle: @davec Manufacturer: Peak Energy Mode...
By DaveC , 3 hours ago
-
RE: Rate the quality of your heat pump design and installation
@radwhispererdwhisperereorourkeditor Well, the guy came...
By razz , 3 hours ago
-
RE: Setback savings - fact or fiction?
Given the weather has been relatively stable, the empir...
By Batpred , 3 hours ago
-
RE: GSHP WOES! Midland based engineer recommendations?
@editor That is very kind! Thank you so much.
By johnbroome , 5 hours ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@wally Hi I am not sure how large your house is b...
By TechnoGeek , 6 hours ago
-
RE: Predicted Heat Loss & Needs from MCS calcs vs EPC vs actual
I've been thinking along similar lines to @tim441 from ...
By Sheriff Fatman , 6 hours ago
-
Thanks, @technogeek. Good to hear about the accuracy. ...
By Majordennisbloodnok , 7 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
In my case it was a very specific pattern of behaviour ...
By Sheriff Fatman , 7 hours ago
-
RE: Vaillant aroTherm not heating with many faults
@ashp-bobba Yeah I'll give it a go, will check filter...
By Anon67 , 7 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@transparent Perhaps the names at the end of the docume...
By Toodles , 7 hours ago
-
RE: Heatpunk Floor plan issues
@jamiejones85 A2A they will design on dynamic heat loss...
By ASHP-BOBBA , 8 hours ago
-
RE: Fan unit Making terrible noise HELP!!
can you post a video looking inside, at and through the...
By ASHP-BOBBA , 8 hours ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Agreed, which is no more nor less than a customer shoul...
By Majordennisbloodnok , 1 day ago