Low Loss Header is losing 1.5c from flow temperature
@iancalderbank thanks Ian
yes there is a drop in flow temp across the LLH but there is a more or less equal rise in return temp across the LLH. These were tested with a separate thermistor…
I don’t know if there is a way of working out a quantifiable energy cost for the increased generated DT to create the desired DT at the emitters but perhaps it isn’t as big as I’m thinking it might be?
thanks for your insights on this
Posted by: @sunandair@iancalderbank thanks Ian
yes there is a drop in flow temp across the LLH but there is a more or less equal rise in return temp across the LLH.
doesn't matter. check the datasheet 2 posts up. the higher the flowT, the worse the COP. same for any heat pump.
also you are talking about loss of DT, but in your sketch, DT is the same both sides, which it would be if flow rate is the same. heatgeeks explanation is pretty good as they usually are
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
Posted by: @iancalderbankDT is the same both sides,
hi Ian,
here is my sketch again what do you mean that the DT Is the same both sides? The sketch shows a 1degC drop in one direction and a 1degC rise in the other direction…. Is that what you mean?
the Heat Geek info looks interesting
Will look in due course… thanks
Posted by: @sunandair@iancalderbank thanks Ian
yes there is a drop in flow temp across the LLH but there is a more or less equal rise in return temp across the LLH. These were tested with a separate thermistor…
I don’t know if there is a way of working out a quantifiable energy cost for the increased generated DT to create the desired DT at the emitters but perhaps it isn’t as big as I’m thinking it might be?
thanks for your insights on this
Assuming I understand the question correctly (which I may not) then yes there is. Plot COP vs flow temperature, then work out the COP (at some representative OAT eg 7C) for the two 'alternative' flow temperatures required to achieve the same FT at the emitters (ie with and without the LLH, or more simpl the original design FT and that plus the reduction in FT across the LLH). Then use that to work out the change in energy consumption due to requiring a higher FT from the ASHP.
So for example with a Mitsubishi R32 11.2kW the COP at 7/40 is 4.55 and its 5.11 at 35/40. That translates to a 12% increase in consumption for a 5C rise in Flow temp, so about 4% for a 1.5C rise.
Here is a quick table for the 11.2kW Mitsi
This accounts only for the reduction in thermodynamic efficiency of the heat pump, not for any energy losses in the LLH (which, assuming its well insulated, should be negligible). It also assumes that the pump speeds (l/s) both sides of the LLH are approximately equal (if they aren't then youare forcing mixing which is a bad idea)
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa perfect….
thanks James
Added
(We tried a number of secondary pump settings until we got the lowest change in DT but we couldn’t do much better than 1degC. At least we are dealing with constant flow rates…. )
Ive already built my secondary pump bypass….
DT is a phrase used too much in HP discussions, one needs to be clear about between what points the difference is being measured. Its normal that DT is used to refer to the difference between flowT and returnT. In your case, DT on the left side is 5C. (39-34). DT on the right side is also 5C (40-35). DT times flow rate gives you the heat energy transfer rate, which has to be the same each side - there is no input or output of energy in the LLH. If the flow rates are different on each side then DT would be different each side, but the energy transfer would still be (MUST BE) the same. The LLH isn't "losing" energy (it can't, its not an emitter - assuming its well insulated).
But what the LLH does, is force mixing to happen, which MUST reduce the flowT on the emitter side. this reduces the efficiency of the system as a whole, once you consider how the energy input device (the HP) works. To get an emitter temp of 39C, you have to run your HP at 40C. This costs you x% in HP efficiency - its guaranteed, for any HP, the higher the HP flowT, the less efficient it is. (as per jamespa, probably around 3% for 1C). If your drop in FlowT is worse, this % gets higher (= worse).
If you have a poorly balanced LLH - widely differing flowT's - then the drop in flowT would be worse, thus increasing the need to run the HP at an even higher temperature OR leading to too-cold emitters that don't warm the house - thus giving an even less efficient system with an even worse COP.
If you've already got it down to only a 1 degree drop in flowT across the LLH, by tweaking your secondary pump, thats pretty good - implies you've got it down the least amount of mixing that you can (whilst still keeping the LLH). the only way to get better will be to repipe without it. additional benefit of that is you only need 1 pump, and you can also potentially use a variable circulation speed (either a CP or PP pump , or a PWM pump controlled by the HP, or a DT-targeted pump), starting point for that discussion should be what is the pump within your ASHP capable of.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
- 26 Forums
- 2,131 Topics
- 46.8 K Posts
- 30 Online
- 5,655 Members
Podcast Picks
Latest Posts
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
MCS have set a potential trap in the new version of MCS...
By JamesPa , 2 hours ago
-
RE: ASHP heat output monitoring
Agreed with the one qualification that increasing the n...
By JamesPa , 5 hours ago
-
RE: Who has a V2G EV installation
General comment on battery care... I guess if ev is on ...
By Tim441 , 20 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist I have never cleaned the mag filter myse...
By Toodles , 20 hours ago
-
@old_scientist like for like comparisons are almost imp...
By Tim441 , 20 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@old_scientist There is an option in the Tesla app that...
By Toodles , 21 hours ago
-
RE: Mitsu Wireless Controller and MelCloud
On the FTC5 I think this requires the dip switch on the...
By Abernyte , 21 hours ago
-
RE: Octopus Cosy & Octopus EV + bidirectional smart tariff, together. What, eh?
@old_scientist me too. Just installed my new heat pump ...
By Eliuccio , 3 days ago
-
RE: Is your heat pump insured?
Yup just spoke to Privilege to inform them of my impend...
By Scalextrix , 3 days ago
-
RE: Forum updates, announcements & issues
Just to keep everyone in the loop, as the site continue...
By Mars , 3 days ago
-
RE: Fast DHW setting on Midea (Clivet) heat pump
@simon-w, is this something you could potentially assis...
By Mars , 4 days ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
Fwiw I called my installer out for the first time a few...
By JamesPa , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@sandy, I'll send Vaillant an email tomorrow and see if...
By Mars , 4 days ago
-
RE: Long term efficiency degradation
@jamespa yes as I thought thanks. We have a reaso...
By Scalextrix , 4 days ago
-
RE: Sunamp Thermino Heat Battery
@jamespa A few days after the installation had been com...
By Toodles , 5 days ago
-
RE: Planning Permission May 2025
Fair enough. I have read the legislation and MCS020a ...
By JamesPa , 7 days ago
-
RE: How do I choose a single room MVHR to prevent losing heat in my bathroom ?
An update on the Heatsava. It is the most difficult thi...
By heat-pump-newbie , 1 week ago
-
RE: Renewables & Heat Pumps in the News
this document extensively describes (in a non-blame, ne...
By Judith , 1 week ago
-
RE: Ecodan - Legionella Operation Time and Target Temperature
Once the white plastic cap is removed, my immersion loo...
By Old_Scientist , 1 week ago
-
RE: Replacing Refrigerant on Mitsubishi Heat Pump
@dgclimatecontrol I don't know, but they were not happy...
By DavidAlgarve , 1 week ago