Low loss header
Does anyone have the latest info from freedom on low loss headers? I asked my fitter to remove the current one and he won't do so because he said it would invalidate the warranty.
I'm sure someone said it's been updated in their documents to not be required anymore.
I've spoken with Freedom and after a really long and useful call (the guy has very helpful in talking over the system) he said the following things at the high level
- There is no reason why you need a low loss header and they will warranty a system without one provided the proper calcs have been done and your system has been designed/confirmed to work without one
- They say a low loss header loses you around 10%-15% efficiency
- They put them in (low loss headers) to ensure customers don't have issues through poor design from the trade
- Weather compensation is set high as they expect the installer to have done the work to set the correct curve
- Midea specify low loss headers in their documents so Freedom is just repeating the statement
- Ideally you should run off the controller and not a thermostat
- They do have an additional sensor to monitor return temps that allows the system to adjust weather compensation on the fly (or that was my understanding)
Now its down to me to see if I can get my fitter to actually make the changes and calculations needed.
Posted by: @bataltoI've spoken with Freedom and after a really long and useful call (the guy has very helpful in talking over the system) he said the following things at the high level
- There is no reason why you need a low loss header and they will warranty a system without one provided the proper calcs have been done and your system has been designed/confirmed to work without one
- They say a low loss header loses you around 10%-15% efficiency
- They put them in (low loss headers) to ensure customers don't have issues through poor design from the trade
- Weather compensation is set high as they expect the installer to have done the work to set the correct curve
- Midea specify low loss headers in their documents so Freedom is just repeating the statement
- Ideally you should run off the controller and not a thermostat
- They do have an additional sensor to monitor return temps that allows the system to adjust weather compensation on the fly (or that was my understanding)
Now its down to me to see if I can get my fitter to actually make the changes and calculations needed.
10-15% is a lot of money at upcoming prices (I appreciate not so much for you personally!). But sounds like good news. Maybe your guy could bypass the LLH but leave in place just in case?
@kev-m speaking frankly I'm not sure my installer is up for it. He's more of a plumber by his own admission. I might need to call freedom and see if they can recommend an engineer Vs a technician.
The low loss header (LLH) is typically used to ensure flow rates and reduce call outs due to restrictive conditions in retro fit setups.
whilst they do work, in practice there is a trade off as the secondary pump, the one which then becomes the heating circulator, has no modulating control from the heat pump. A modern heat pump, such as the Midea, controls flow temp using a combination of fan speed, compressor duty and circulator flow rate. It’s extremely efficient when used this way.
When you separate the ASHP and house circulation this way, the only compensated flow is the primaries from the ASHP.
ideally we wouldn’t use them. In practice there are a number of issues.
1- lack of maintenance leads to flow issues. An LLH Reduces load and gives a low speed area of water in the vessel, this naturally aerates and drops dirt to the internal magnet. Therefore extending the period between faults. It’s a fix rather than a cure.
2- retrofit plumbing can have a number of issues. Unknown pipe routes. Unknown sizing etc. separating the flows means we don’t have to worry too much about that.
3- the manual actually shows it installed. Most installers will not go off piste and the manual is gospel and the word of the warranty gods. Most of it is pure nonsense but it will cause a bun fight in the event of a claim.
there are situations where an LLH is a must. Micro bore setups will not generally allow the high flow rates needed for heat pumps and will constantly fault on flow. LLH fixes that.
In an ideal world, we wouldn’t bother with separation at all. If your plumbing system is good, then theoretically it will work fine. It’s an acceptance of liability. If you were asking me as an installer, I’d be ok with it, I’d just provision to retro fit later, so leave space in the pipework for the LLH and a pump. Four lever valves to allow a section of pipe to be easily removed on the flow and return. Probably install the auto bypass in that section as it can go when an LLH is used.
hope some of this helps.
Internationally recognised award winning installer of heat pumps and stuff
@saenergy I have a feeling you are the person who has been recommended to me by Freedom to modify my system. I sent you an email yesterday (if you're that same SA energy they recommended)
ah that is likely. I’ll be in touch. Been laid up with a broken back.
Internationally recognised award winning installer of heat pumps and stuff
@saenergy that'll be you. The nice lady on the phone said you were at home because of an injury and were just doing emails etc - and clearly checking forums. Hope you make a speedy recovery. In the meantime happy to share any info you might need to understand my system/issues I am trying to fix.
Posted by: @bataltoany idea when you might be able to come to make those system changes?
hi @batalto I’m interested in what you did in the end. Did you manage to remove your low loss header? What was the layout you chose. I’m thinking of leaving the LLH in place and connect the returns through it and then bypass the two flows, connecting them together, with an air vent included.
- 22 Forums
- 2,073 Topics
- 45.5 K Posts
- 49 Online
- 3,352 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Commencing on an ASHP Installation Process
I think therein lies the problem. Ratio of quotes to i...
By JamesPa , 12 hours ago
-
RE: Why Your MCS-Certified Installer Might Not Be As Competent As You Think
Hive and most other smart thermostats don't play well w...
By JamesPa , 15 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
Thanks for the input. I've been running various experim...
By Grahamh-uk , 15 hours ago
-
RE: Radiators downstairs are cooler at the bottom after ASHP install
@melonbuffet Hi, this sounds great is you are getting 5...
By ASHP-BOBBA , 17 hours ago
-
RE: 5 Star Service from Havenwise
... a mode of operation which increases losses due to p...
By Transparent , 18 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
I believe there's another reason that network upgrades ...
By Transparent , 1 day ago
-
RE: What’s the modern take on advised types of insulation?
@jeff I am sorry @jeff if I have misunderstood what you...
By Toodles , 2 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@editor Cobbler’s Mantra that!
By Toodles , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Australia Blue, the first wind farm in Western Victoria...
By Morgan , 3 days ago
-
RE: Flow rate discrepancy between ASHP and manifold
That's useful thanks, I hadn't seen that table before. ...
By AshRolls , 3 days ago
-
In principle I agree, @johnmo, but with provisos. The...
By Majordennisbloodnok , 4 days ago
-
RE: Heat pump installation and BUS Grant timings
@jamespa Thats how I understood it too. 🙂
By ASHP-BOBBA , 4 days ago
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@sallyl That sounds about right if they are re-filling ...
By Brendon Uys , 4 days ago
-
I wouldn't be so sure about that. Heat pump designers ...
By JamesPa , 4 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@toodles they're a rowdy bunch!
By Mars , 5 days ago
-
RE: Home energy storage & battery register
@jamespa To a certain extent, by exporting to the grid ...
By Toodles , 5 days ago
-
RE: Forum updates, announcements & issues
@editor Fairy Nuff Mars, I doubt that my ramblings woul...
By Toodles , 7 days ago
-
RE: Confusion about heat pump sizing
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 7 days ago
-
We’ve published a deep dive into heat pump sizing, and ...
By Mars , 7 days ago