Low loss header
Does anyone have the latest info from freedom on low loss headers? I asked my fitter to remove the current one and he won't do so because he said it would invalidate the warranty.
I'm sure someone said it's been updated in their documents to not be required anymore.
I've spoken with Freedom and after a really long and useful call (the guy has very helpful in talking over the system) he said the following things at the high level
- There is no reason why you need a low loss header and they will warranty a system without one provided the proper calcs have been done and your system has been designed/confirmed to work without one
- They say a low loss header loses you around 10%-15% efficiency
- They put them in (low loss headers) to ensure customers don't have issues through poor design from the trade
- Weather compensation is set high as they expect the installer to have done the work to set the correct curve
- Midea specify low loss headers in their documents so Freedom is just repeating the statement
- Ideally you should run off the controller and not a thermostat
- They do have an additional sensor to monitor return temps that allows the system to adjust weather compensation on the fly (or that was my understanding)
Now its down to me to see if I can get my fitter to actually make the changes and calculations needed.
Posted by: @bataltoI've spoken with Freedom and after a really long and useful call (the guy has very helpful in talking over the system) he said the following things at the high level
- There is no reason why you need a low loss header and they will warranty a system without one provided the proper calcs have been done and your system has been designed/confirmed to work without one
- They say a low loss header loses you around 10%-15% efficiency
- They put them in (low loss headers) to ensure customers don't have issues through poor design from the trade
- Weather compensation is set high as they expect the installer to have done the work to set the correct curve
- Midea specify low loss headers in their documents so Freedom is just repeating the statement
- Ideally you should run off the controller and not a thermostat
- They do have an additional sensor to monitor return temps that allows the system to adjust weather compensation on the fly (or that was my understanding)
Now its down to me to see if I can get my fitter to actually make the changes and calculations needed.
10-15% is a lot of money at upcoming prices (I appreciate not so much for you personally!). But sounds like good news. Maybe your guy could bypass the LLH but leave in place just in case?
@kev-m speaking frankly I'm not sure my installer is up for it. He's more of a plumber by his own admission. I might need to call freedom and see if they can recommend an engineer Vs a technician.
The low loss header (LLH) is typically used to ensure flow rates and reduce call outs due to restrictive conditions in retro fit setups.
whilst they do work, in practice there is a trade off as the secondary pump, the one which then becomes the heating circulator, has no modulating control from the heat pump. A modern heat pump, such as the Midea, controls flow temp using a combination of fan speed, compressor duty and circulator flow rate. It’s extremely efficient when used this way.
When you separate the ASHP and house circulation this way, the only compensated flow is the primaries from the ASHP.
ideally we wouldn’t use them. In practice there are a number of issues.
1- lack of maintenance leads to flow issues. An LLH Reduces load and gives a low speed area of water in the vessel, this naturally aerates and drops dirt to the internal magnet. Therefore extending the period between faults. It’s a fix rather than a cure.
2- retrofit plumbing can have a number of issues. Unknown pipe routes. Unknown sizing etc. separating the flows means we don’t have to worry too much about that.
3- the manual actually shows it installed. Most installers will not go off piste and the manual is gospel and the word of the warranty gods. Most of it is pure nonsense but it will cause a bun fight in the event of a claim.
there are situations where an LLH is a must. Micro bore setups will not generally allow the high flow rates needed for heat pumps and will constantly fault on flow. LLH fixes that.
In an ideal world, we wouldn’t bother with separation at all. If your plumbing system is good, then theoretically it will work fine. It’s an acceptance of liability. If you were asking me as an installer, I’d be ok with it, I’d just provision to retro fit later, so leave space in the pipework for the LLH and a pump. Four lever valves to allow a section of pipe to be easily removed on the flow and return. Probably install the auto bypass in that section as it can go when an LLH is used.
hope some of this helps.
Internationally recognised award winning installer of heat pumps and stuff
@saenergy I have a feeling you are the person who has been recommended to me by Freedom to modify my system. I sent you an email yesterday (if you're that same SA energy they recommended)
ah that is likely. I’ll be in touch. Been laid up with a broken back.
Internationally recognised award winning installer of heat pumps and stuff
@saenergy that'll be you. The nice lady on the phone said you were at home because of an injury and were just doing emails etc - and clearly checking forums. Hope you make a speedy recovery. In the meantime happy to share any info you might need to understand my system/issues I am trying to fix.
Posted by: @bataltoany idea when you might be able to come to make those system changes?
hi @batalto I’m interested in what you did in the end. Did you manage to remove your low loss header? What was the layout you chose. I’m thinking of leaving the LLH in place and connect the returns through it and then bypass the two flows, connecting them together, with an air vent included.
- 25 Forums
- 1,441 Topics
- 30.2 K Posts
- 28 Online
- 1,225 Members
Join Us!
Latest Posts
-
RE: ASHP Commissioning: What Questions Should I Ask the Installer?
@derek-m thanks - will look out for the point regarding...
By Declan90 , 7 hours ago
-
RE: Noise problems with newly installed Samsung 8kW ASHP
@editor @kenbone Thanks, I would be very interested ...
By Elton , 8 hours ago
-
RE: No-code, plug-and-play monitoring for your heat pump
This is all a bit too frequentist for my liking. The pr...
By scrchngwsl , 8 hours ago
-
RE: Are Octopuses Slowing Consumer Adoption of Heat Pumps?
@ivanopinion I stumbled across this thread Performance ...
By GunboatDiplomat , 10 hours ago
-
RE: EV charger installation question – I don't want to bury the cable
Hmmm... That raises a lot of questions in my mind! ...
By Transparent , 15 hours ago
-
Relax with 4K drone footage of lawn mowing to a smooth Motown tune
Sending out some chilled weekend vibes to everyone. Lis...
By Mars , 18 hours ago
-
RE: Incorrect Billing of Customers with a Smart Meter
The starting point of that discussion on Camelot-Forum ...
By Transparent , 20 hours ago
-
Share Your Experiences with Heat Pump Manufacturer Support
Have you ever reached out to your air source heat pump ...
By Mars , 1 day ago
-
RE: Is this a bad installation and is there something wrong with my Samsung heat pump?
@ant87 thanks for that.
By David999 , 2 days ago
-
RE: Aira Heat Pump: Stylish Scandinavian Heating
I might change my mind again, but I'm currently unlikel...
By IvanOpinion , 2 days ago
-
RE: Samsung ASHP scheduling help
@elgreco69 worth reading the GitHub here as that will a...
By morh , 2 days ago
-
RE: ASHP sizing - value of Heat Transfer Coefficient
@toodles Thanks for the explanation I get it now as I h...
By Jancold , 2 days ago
-
RE: Questions about yearly heat pump maintenance
For the installer, I believe servicing and maintenance ...
By Majordennisbloodnok , 2 days ago
-
RE: Rate the quality of your heat pump design and installation
@retrorich It is very worrying that any of this should ...
By Toodles , 3 days ago
-
RE: Spacing for roof fixing bolts ?
There is another consideration...but alas this doesn't ...
By Transparent , 3 days ago
-
RE: Air source heat pumps and noise
Yes, but when they go wrong things get really sticky. D...
By Majordennisbloodnok , 3 days ago
-
RE: Are You Getting the Most Out of Your Renewable Energy?
As I mentioned, there are going to be some follow-up ar...
By Majordennisbloodnok , 3 days ago
-
RE: Tell us about your Solar (PV) setup
Now, I know that this may be a little simplistic and pe...
By Toodles , 3 days ago
-
-
RE: Save the Energy Save the World using Daikin Altherma 3 operation mode and schedules settings.
Hello Mevl, I won't be able to answer all your question...
By HCas , 4 days ago
Heat Pump Humour
Latest Topics
-
Spacing for roof fixing bolts ?
By heat-pump-newbie 5 days ago
-
ASHP sizing - value of Heat Transfer Coefficient
By jamesw 6 days ago
-
Incorrect Billing of Customers with a Smart Meter
By KoRWraith 1 week ago
-
Home energy storage & battery register
By Mars 1 week ago
Members Online
No online members at the moment