Low loss header
Does anyone have the latest info from freedom on low loss headers? I asked my fitter to remove the current one and he won't do so because he said it would invalidate the warranty.
I'm sure someone said it's been updated in their documents to not be required anymore.
I've spoken with Freedom and after a really long and useful call (the guy has very helpful in talking over the system) he said the following things at the high level
- There is no reason why you need a low loss header and they will warranty a system without one provided the proper calcs have been done and your system has been designed/confirmed to work without one
- They say a low loss header loses you around 10%-15% efficiency
- They put them in (low loss headers) to ensure customers don't have issues through poor design from the trade
- Weather compensation is set high as they expect the installer to have done the work to set the correct curve
- Midea specify low loss headers in their documents so Freedom is just repeating the statement
- Ideally you should run off the controller and not a thermostat
- They do have an additional sensor to monitor return temps that allows the system to adjust weather compensation on the fly (or that was my understanding)
Now its down to me to see if I can get my fitter to actually make the changes and calculations needed.
Posted by: @bataltoI've spoken with Freedom and after a really long and useful call (the guy has very helpful in talking over the system) he said the following things at the high level
- There is no reason why you need a low loss header and they will warranty a system without one provided the proper calcs have been done and your system has been designed/confirmed to work without one
- They say a low loss header loses you around 10%-15% efficiency
- They put them in (low loss headers) to ensure customers don't have issues through poor design from the trade
- Weather compensation is set high as they expect the installer to have done the work to set the correct curve
- Midea specify low loss headers in their documents so Freedom is just repeating the statement
- Ideally you should run off the controller and not a thermostat
- They do have an additional sensor to monitor return temps that allows the system to adjust weather compensation on the fly (or that was my understanding)
Now its down to me to see if I can get my fitter to actually make the changes and calculations needed.
10-15% is a lot of money at upcoming prices (I appreciate not so much for you personally!). But sounds like good news. Maybe your guy could bypass the LLH but leave in place just in case?
@kev-m speaking frankly I'm not sure my installer is up for it. He's more of a plumber by his own admission. I might need to call freedom and see if they can recommend an engineer Vs a technician.
The low loss header (LLH) is typically used to ensure flow rates and reduce call outs due to restrictive conditions in retro fit setups.
whilst they do work, in practice there is a trade off as the secondary pump, the one which then becomes the heating circulator, has no modulating control from the heat pump. A modern heat pump, such as the Midea, controls flow temp using a combination of fan speed, compressor duty and circulator flow rate. It’s extremely efficient when used this way.
When you separate the ASHP and house circulation this way, the only compensated flow is the primaries from the ASHP.
ideally we wouldn’t use them. In practice there are a number of issues.
1- lack of maintenance leads to flow issues. An LLH Reduces load and gives a low speed area of water in the vessel, this naturally aerates and drops dirt to the internal magnet. Therefore extending the period between faults. It’s a fix rather than a cure.
2- retrofit plumbing can have a number of issues. Unknown pipe routes. Unknown sizing etc. separating the flows means we don’t have to worry too much about that.
3- the manual actually shows it installed. Most installers will not go off piste and the manual is gospel and the word of the warranty gods. Most of it is pure nonsense but it will cause a bun fight in the event of a claim.
there are situations where an LLH is a must. Micro bore setups will not generally allow the high flow rates needed for heat pumps and will constantly fault on flow. LLH fixes that.
In an ideal world, we wouldn’t bother with separation at all. If your plumbing system is good, then theoretically it will work fine. It’s an acceptance of liability. If you were asking me as an installer, I’d be ok with it, I’d just provision to retro fit later, so leave space in the pipework for the LLH and a pump. Four lever valves to allow a section of pipe to be easily removed on the flow and return. Probably install the auto bypass in that section as it can go when an LLH is used.
hope some of this helps.
Internationally recognised award winning installer of heat pumps and stuff
@saenergy I have a feeling you are the person who has been recommended to me by Freedom to modify my system. I sent you an email yesterday (if you're that same SA energy they recommended)
ah that is likely. I’ll be in touch. Been laid up with a broken back.
Internationally recognised award winning installer of heat pumps and stuff
@saenergy that'll be you. The nice lady on the phone said you were at home because of an injury and were just doing emails etc - and clearly checking forums. Hope you make a speedy recovery. In the meantime happy to share any info you might need to understand my system/issues I am trying to fix.
Posted by: @bataltoany idea when you might be able to come to make those system changes?
hi @batalto I’m interested in what you did in the end. Did you manage to remove your low loss header? What was the layout you chose. I’m thinking of leaving the LLH in place and connect the returns through it and then bypass the two flows, connecting them together, with an air vent included.
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 79 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@davidnolan22 I genuinely do not know the answer, unles...
By ASHP-BOBBA , 3 hours ago
-
RE: Renewables & Heat Pumps in the News
@transparent my reading of the report P28 (and probably...
By Judith , 4 hours ago
-
RE: 4 Year Ongoing Heat Pump Battle With Poor Heat Pump Installation
@jamespa Oh, I know some that are good and some not so....
By ASHP-BOBBA , 4 hours ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
I don't know how many pumps you have but I guess it's o...
By JamesPa , 5 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
That's just human nature unfortunately, not special to ...
By JamesPa , 5 hours ago
-
RE: Octopus tariffs - a quick comparison
Absolutely. That’s one of the reasons I wouldn’t want t...
By Majordennisbloodnok , 6 hours ago
-
@editor The season to start inviting prospectives to ‘V...
By Toodles , 12 hours ago
-
@bontwoody how long has it been now since you started t...
By Mars , 12 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
Yes, over the last few days I've been keeping a very cl...
By Steelbadger , 12 hours ago
-
Absolutely. I am one of those members and I most certai...
By Majordennisbloodnok , 14 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
@darrell-p There's another new Forum Member, @wully who...
By Transparent , 14 hours ago
-
RE: Forum updates, announcements & issues
We've had a slight glitch with our security software fo...
By Mars , 16 hours ago
-
RE: Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
If you do suggest you consider repurposing it as a 2 po...
By JamesPa , 1 day ago
-
RE: Say hello and introduce yourself
Fully agree with @cathoderay. My journey took 2 years ...
By JamesPa , 1 day ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
Tim, Yes ChatGPT thought I could get another...
By Mike Patrick , 2 days ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
No problem, @richdorm; glad it helps.
By Majordennisbloodnok , 2 days ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
I do already have the same basic setup, all room influe...
By cathodeRay , 2 days ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
OK. You dont say whether it is from the feeds to/from ...
By JamesPa , 2 days ago