Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that is set to 23LWT @ 16OAT The ASHP doesn't allow a min LWT of less than 23 but as the OAT starts going above 16c there'll be a point where I'd rather the ASHP just stopped completely rather than producing 23c. I do have room thermostats which are set high to run the system open but I don't really want to use them to shut down the heating room by room as I'll probably end up with the ASHP pushing water through one rad in the last bedroom to turn off. I've hunted through the manual but I can't find a setting which says 'stop heating when OAT reaches a set temp' or similar. Has anyone found one?
Hi @damonc, parameter 2015 is the maximum outdoor air temperature corresponding to minimum outgoing water temperature. Default setting is 20degC, in your case you need this set to 16degC if you don't want heating when the outdoor air temperature is above 16degC. Refer to Grant Aerona 3 installation manual 0136 Rev 2.4 page 36
@allyfish thanks for replying, did you mean 2105? (I can't find a parameter 2015) if so that's already set to 16 but I thought it would just carry on producing 23 LWT above 16 rather than turn off heating completely, my reasoning was at the other end of the curve it doesn't get any hotter when you go past your lowest OAT just plateaus there but I guess that assumption doesn't make a lot of sense or it would still be producing 23 LWT right through summer so I think my settings are ok, will see when it gets warmer but I think the pump may continue circulating as I'm sure I was above 16 last week and it didn't cut out .
Sorry, yes, 2105. OOPS! If I recall the unit circulates water if the heating is scheduled to be on, but simply doesn't heat the circulating water if the ambient temperature is >2105 parameter setting.
- 26 Forums
- 2,153 Topics
- 47.3 K Posts
- 17 Online
- 5,673 Members
Join Us!
Podcast Picks
Latest Posts
-
RE: Ecodan software update. Real or scam?
@vinz86 Contact Mitsubishi and an engineer attends and ...
By ASHP-BOBBA , 3 hours ago
-
RE: Midea ASHP – how to set weather compensation
@pash44pump what we did to resolve a not too dissimilar...
By benson , 5 hours ago
-
My Samsung Gen6 (probably same controller as yours) onl...
By Old_Scientist , 13 hours ago
-
@drei When I was in local government we were of cours...
By JamesPa , 13 hours ago
-
RE: Heat Pump SCOPs – The Truth Might Not Be What You Think
Sufficient system volume is also essential for ensuring...
By Old_Scientist , 15 hours ago
-
RE: Boiling Mad: Exposing Radiatorgate
@rob-nezard you can see more of Drei's rad dramas here ...
By Mars , 15 hours ago
-
RE: A Customer's Lessons Learnt from a Heat Pump Installation in a Large House
@drei I will say again that Im sorry to heat about your...
By JamesPa , 16 hours ago
-
RE: Flexi-Orb Heat Pump Scheme: A Game-Changer for the UK's Heat Pump Industry
As someone who has suffered from a Heat Pump installati...
By DREI , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
1040kw Even beat June and July. Great month.
By Andris , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Hope they know what they're doing regarding paint types...
By PatrickVito , 1 day ago
-
RE: What crazy nonsense are inverter limits and why are they imposed?
I’ve also got a dual fuel Rangemaster. We originally ha...
By Majordennisbloodnok , 1 day ago
-
RE: Octopus tariffs - a quick comparison
@tim441 I’d agree wholeheartedly with that, with 2 x Po...
By Toodles , 1 day ago
-
RE: Electricity price predictions
@bontwoody Maybe one for @editor to consider whether a ...
By ChandyKris , 2 days ago
-
RE: is a home battery without an EV worth it?
You would think, but when I had my Powerwall 3 installe...
By Old_Scientist , 2 days ago
-
@mars That response surely deserves a nomination for Tu...
By JamesPa , 2 days ago
-
Specifying batteries, pv solar etc using ChatGPT
I thought I'd try to use ChatGPT to specify my requirem...
By Tim441 , 2 days ago
-
RE: Ecodan & MelCloud scheduling
When I interviewed Mitsubishi Electric at Installer ear...
By Mars , 2 days ago
-
RE: Rodents! A word of warning for heat pump owners
@lucia One look at that protection and the rodents will...
By Toodles , 2 days ago