Load Compensation and Weather Compensation

49 Posts
7 Users
9 Reactions
207 Views
(@johnmo)
Noble Member Member
Joined: 2 years ago
Posts: 534
 

A Salus auto balance UFH valve, could be a simple bolt on to replace a trv. Just open the lock shield fully. Not sure what dT your radiator works at? The Salus above 30 Deg holds a 7 Deg dT and below 30 degs a 4dT. They use a clip on temperature probe on the supply and return piping, but also require a power supply.

The original ones had a couple of hours self commission period, new one fit in place, zero commission period.

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2467
 

Posted by: @johnmo

A Salus auto balance UFH valve, could be a simple bolt on to replace a trv. Just open the lock shield fully. Not sure what dT your radiator works at? The Salus above 30 Deg holds a 7 Deg dT and below 30 degs a 4dT. They use a clip on temperature probe on the supply and return piping, but also require a power supply.

As I understand it these balance for fixed dT

That's not what's needed unless emitters are perfectly sized (which they inevitably aren't).  What's needed is to balance for room temperature (but slowly, like an lsv being manually tuned,) thus taking out inevitable variations in sizing.  

I agree that the right device would allow lsvs to be fully open.

This post was modified 1 hour ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@johnmo)
Noble Member Member
Joined: 2 years ago
Posts: 534
 

Posted by: @jamespa

That's not what's needed unless emitters are perfectly sized (which they inevitably aren't).  What's needed is to balance for room temperature

So a thermostat is what you are describing, that modulates flow instead of shutting it off? So a trv with remote sensor?

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote



(@grantmethestrength)
Estimable Member Member
Joined: 4 months ago
Posts: 63
 

Posted by: @johnmo

Posted by: @jamespa

That's not what's needed unless emitters are perfectly sized (which they inevitably aren't).  What's needed is to balance for room temperature

So a thermostat is what you are describing, that modulates flow instead of shutting it off? So a trv with remote sensor?

 

That is kind of what I was thinking.

 

Kind Regards
Si
——————————————————————————
Grant Aerona3 13kW
13 x 435w Solar Panels
Solax 3.5kW Hybrid Inverter


   
ReplyQuote
(@johnmo)
Noble Member Member
Joined: 2 years ago
Posts: 534
 

https://www.wolseley.co.uk/product/drayton-angled-trv4-and-remote-head-15mm-2mtr/?srsltid=AfmBOoo4jcmaNl95M-YB7CJiJLp6XyfxkJfEVR2b-8KGX5CcPcbmJAr5

These have been about for a few decades. Simple. Sure you could get a wireless version. Just look around. Do a basic radiator balance, let them fine tune.

But you really need them, cash rich, time poor maybe, a couple of fine tunes, over a few evenings, no you don't need them. If your radiator sizing is reasonable shouldn't be much to do apart from hydraulic balance. Just follow heat geek instructions on their website.

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2467
 

Posted by: @johnmo

Posted by: @jamespa

That's not what's needed unless emitters are perfectly sized (which they inevitably aren't).  What's needed is to balance for room temperature

So a thermostat is what you are describing, that modulates flow instead of shutting it off? So a trv with remote sensor?

Almost but not quite a trv with remote sensor.  A trv with or without a remote sensor operates principally, so far as I know, as an on off device (albeit that there is an element of analogue control).  That's not what we want, we want a device that adjusts the flow on a longer timescale (hours) so that it's just the right flow to achieve the desired room temperature.  WC still applies. 

It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.

I completely agree that householders could in principle do this manually, but doubt that many can/will hence the need for a fit and forget solution.  Don't forget we need to assume that a)householders have no interest in heating and b) that a high proportion are incapable of (or unwilling to)  following simple instructions.

This post was modified 1 hour ago 3 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@andrewj)
Estimable Member Member
Joined: 4 months ago
Posts: 45
Topic starter  

It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.

Is that really the case?  Won’t the rate of heat loss in the room change as it cools/warms outside and thus what it is balanced for today at 1c isn’t the same as tomorrow when it’s -3c?  The flow temperature would have increased but is the radiator still properly balanced in the changed scenario?

 

This post was modified 1 hour ago by AndrewJ

   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2467
 

Posted by: @andrewj

 

It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.

Is that really the case?  Won’t the rate of heat loss in the room change as it cools/warms outside and thus what it is balanced for today at 1c isn’t the same as tomorrow when it’s -3c?  The flow temperature would have increased but is the radiator still properly balanced in the changed scenario?

 

Yes it really is the case to a good (good enough) approximation.  Once emitters are balanced open loop WC with all emitters permanently on works pretty well, and all this is is open loop WC with an automated balancing instead of manual balancing.

 

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@andrewj)
Estimable Member Member
Joined: 4 months ago
Posts: 45
Topic starter  

Posted by: @jamespa

Posted by: @andrewj

 

It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.

Is that really the case?  Won’t the rate of heat loss in the room change as it cools/warms outside and thus what it is balanced for today at 1c isn’t the same as tomorrow when it’s -3c?  The flow temperature would have increased but is the radiator still properly balanced in the changed scenario?

 

Yes it really is the case to a good (good enough) approximation.  Once emitters are balanced open loop WC with all emitters permanently on works pretty well, and all this is is open loop WC with an automated balancing instead of manual balancing.

 

That's good to know - and in which case, adding anything fancy to the system to "automate" it sounds like (a) an unnecessary complication; and (b) likely to not work very well and/or just become aggravating (in my somewhat jaded and world-weary opinion)

 

 

 


   
ReplyQuote



(@jamespa)
Illustrious Member Moderator
Joined: 2 years ago
Posts: 2467
 

Posted by: @andrewj

Posted by: @jamespa

Posted by: @andrewj

 

It's literally the same as adjusting the lsv manually, something you do slowly over hours or days until it's right, then leave forever.

Is that really the case?  Won’t the rate of heat loss in the room change as it cools/warms outside and thus what it is balanced for today at 1c isn’t the same as tomorrow when it’s -3c?  The flow temperature would have increased but is the radiator still properly balanced in the changed scenario?

 

Yes it really is the case to a good (good enough) approximation.  Once emitters are balanced open loop WC with all emitters permanently on works pretty well, and all this is is open loop WC with an automated balancing instead of manual balancing.

 

That's good to know - and in which case, adding anything fancy to the system to "automate" it sounds like (a) an unnecessary complication; and (b) likely to not work very well and/or just become aggravating (in my somewhat jaded and world-weary opinion)

 

 

 

In principle I agree.  However how else can you correctly adjust the lsvs?  Installer won't spend the hours that it takes to do it (they may adjust for DT but won't in most cases adjust for room temperature) and most homeowners not capable/not willing.  The alternative (as I fear the default) is fitting trvs which are a bad option.  

 

It's a real problem that needs a solution that works for the average householder, not just the ones on this forum!

This post was modified 28 minutes ago by JamesPa
This post was modified 23 minutes ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@johnmo)
Noble Member Member
Joined: 2 years ago
Posts: 534
 

Posted by: @jamespa

Almost but not quite a trv with remote sensor.  A trv with or without a remote sensor operates principally, so far as I know, as an on off device (albeit that there is an element of analogue control). 

No they are not on/off valves, they modulate flow. Exactly what you say you want, they do our the box. Modulate radiator flow based on room temperature. So as to keep room a a set temperature. Add weather compensation, they will continue to modulate flow as needed.

Simple description of a trv

https://www.traderadiators.com/blog/how-do-thermostatic-radiator-valves-work

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
(@johnmo)
Noble Member Member
Joined: 2 years ago
Posts: 534
 

But the disadvantage of trv modulation or any self balancing devise is variation in flow rate at the heat pump. You ideally need as much flow as possible, to give smallest dT to get maximum radiator output, for minimum flow temp, to get best CoP.

Hence the reason everyone is saying minimise their usage.

Auto balance anything, is just a band aid on a fully open system. They really have no place. People should either self install or get a professional install, the professional install should balance they system, if they don't call them back, you have paid good money for an install.

 

Maxa i32V5 6kW ASHP (heat and cooling)
6.5kW PV
13.5kW GivEnergy AIO Battery.


   
ReplyQuote
Page 4 / 5
Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security