@johnmo Well thats very clear, just wondering really if you had a big tank it could take 2 hours to heat. on a cold wet day it would seem likely that the HP could ice up. Out of curiosity I might start a thread just to see if different HPs have different strategies. Oh the joys of being retired with time on your hands 🤣
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@johnmo Thanks for clearing up the matter of defrosts during DHW cycles. I was just guessing really. Wouldnt it be more likely though that the HP would need deforsting during the DHW cycle given the higher flow temperature? What happens it it cant heat the hot water anymore untill it defrosts? Especially it it was less than zero outside.
It may be useful to try to understand what is probably happening within the heat pump system.
The main culprit which causes ice to form on the evaporator coil and fins is the amount of moisture within the outside air. Warmer air is less dense, so each cubic metre will contain less water molecules. As the air cools it becomes more dense, so is likely to have a higher water content. Below an ambient temperature of probably -3C, there is likely to be less moisture in the ambient air, because it turns to ice on anything that it comes into contact with that is below 0C. So the higher humidity levels are likely to occur at ambient temperatures between +3C and -3C.
The refrigerant gas entering the evaporator could be at a temperature of -40C, so it quickly absorbs thermal energy from the metal of the evaporator coil and fins. The amount of thermal energy being absorbed will be dependent upon the loading of the heat pump.
Let's consider a situation where a 12kW heat pump is producing 9kW of thermal energy, at a LWT of 40C, and an OAT of 2C, operating at a COP of 3. The heat pump will be drawing 3kW of electrical energy and absorbing 6kW of thermal energy from the outside air.
If the heat pump now commences a DHW heating cycle, where it is now supplying 3kW of thermal energy, at a LWT of 55C, and a COP of 2. The heat pump should now be drawing 1.5kW of electrical energy and absorbing 1.5kW from the outside air.
If my assumptions are correct, the loading on the heat pump during the DHW cycle could be much lower than when in CH mode, so would be less likely to cause icing on the evaporator.
@derek-m Thanks Derek, thats an interesting way of looking at it.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Work expands to fill the time available. 😄
Toodles, he heats his home with cold draughts and cooks his food with magnets.
@toodles I dont know how I ever managed to find the time to fit work in! 😆
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Of course, since retirement, we all suffer the 50% time taxation - 12 hours per day is hardly enough to contemplate working as well as living! Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Well this has all been surprisingly stressful so I'm going to take a week out and go to Plymouth and back via some interesting stopovers. If all goes well it'll take only two days out and a leisurely return by water, I may even get to sail some of the way! All your help and explanations make me feel like I am getting a good understanding of the process thanks.
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
So after signing in Sept in two weeks the install may start (my choice to delay). I say may as last week it turned out Octoes sent me the wrong plan!! I had stripped a flower bed and dug a trench. Although I am not happy I have gone along with the new plan which will put the HP on the path not the flower bed. My preparations continue, I have fitted new upgraded emitters in the bedrooms and run pipework for the extra Emitters. I was pleased to see the old emitters were not full of black debris at all. Oh my poor knees! Thankfully my son ,Liam, came down to provide help. I will use the trench to run the supply to the Zappi. My coordinator told me to "now fill in the trench" so I will but only when it suits me, cheek!!
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
The Zappi was installed last week and the ASHP "bits" came next day. The team arrived this morning all very pleasant and helpful. They were at a bit of a loss to get the Daikin up the 5 steps so I rang my daughters partner who turned up 25 minutes later with a Telehandler. He then lifted it into position. Now that is a useful daughter!! Tomorrow they hope to have got the DHW working.
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
@jancold It’s not what you know but who you know!😉 My installers faced a similar situation when faced with installing my ~200 kg. Sunamp Thermino upstairs! Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
Day 2, working in all rooms now but particularly installing the DHW tank. Cold water off for most of the day but on late afternoon and hot by immersion 1900. Most radiators hung and two to go then connect all. They finished at 1800, so a long day.
Daikin 6Kw ASHP.
MG4 EV
1926 Semi with loft and wall cavity insulation, all radiator.
- 26 Forums
- 2,102 Topics
- 46.2 K Posts
- 71 Online
- 3,388 Members
Join Us!
Latest Posts
-
RE: Ecodan consuming 100kwh per day in new build!!!
From what you say about the radiators upstairs it does ...
By JamesPa , 1 hour ago
-
RE: Compressor attempts start but fails - Nibe Fighter 2005 8kW
@skyefarmer pleased you found it!
By JamesPa , 2 hours ago
-
The Importance of Radiator Balancing for Efficient Heating: Introducing the Flow Regulating Valve
It’s fascinating to watch how low-temperature heating i...
By Mars , 4 hours ago
-
@heacol, if you're around, can you please provide some ...
By Mars , 7 hours ago
-
RE: Servicing Hitachi HP in rural Somerset
I'd give GreenGenUK a call or email them: sales@greenge...
By Mars , 7 hours ago
-
RE: Heating coming on when not required
I played with a max heating temp but there is a world o...
By JamesPa , 21 hours ago
-
RE: Pressure drop Primary circuit
I've always regarded topping up heating systems as my j...
By JamesPa , 21 hours ago
-
RE: Heat pump solutions and/or installer recommendations for France
I’d travel to France for work if you were struggling wi...
By Damon Blakemore , 1 day ago
-
RE: 5 Star Service from Havenwise
That's always a danger with any new good idea, @morgan....
By Majordennisbloodnok , 1 day ago
-
Have your say in the Renewable Heating Hub Awards
It’s time to celebrate the best (and call out the worst...
By Mars , 2 days ago
-
-
RE: Mitsubishi cycling while on chilled water output
@iaack yes there's no denying that cold air sinks! I s...
By downfield , 2 days ago
-
RE: Weather compensated secondary circuits with Biomass
@andycoo that flooring sounds ideal. Extra volume is ...
By Sune , 2 days ago
-
If you are thinking of heating on the immersion conside...
By JamesPa , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@tomasmcguinness, I think your best bet would be using ...
By Aventus Eco , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles all depends on asking the right questions! And...
By Tim441 , 4 days ago
-
RE: Commencing on an ASHP Installation Process
I received confirmation this morning that my Greener Ho...
By Sheriff Fatman , 4 days ago