Do I just go with the lowest quote for my heat pump?
Octopus are coming around at the end of the month to survey my house. Their quote is half the price quoted by BG.
I have had two heat loss surveys and they agree fairly closely with my own from Heatpunk at around 4kW.
They would both remove my boiler and put in a slimline tank and a Daikin Heat pump. BG quoted at 45C and Octopus will, I understand, at 50c but I may be able to get Octopus to quote lower.
My thinking is that if Octopus are happy to install I would go for that and see how things work out this winter. I would then have the difference in cost to spend on upgrading or adding radiators if needed even if Octopus do not want to replace any.
Basically it is the same hardware with the same pipes so why pay thousands more?
I would agree with you so long as the pipe work isn’t going to be changed.
Swapping a radiator or two isn’t expensive and well within the scope of a competent diyer.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Have you checked for any extras on the Octopus side? For example I had to either get artex removed or lift floorboards for an alternative pipe route - both at my own cost above their fixed quote.
@gunboatdiplomat Yes when I have had the survey and report I will check. The BG one was pretty perfunctory with little detail except that it is up to me to provide piping and cabling under the path.
@jancold since you’re choosing between BG or Octopus, basing your decision on price makes sense if they’re both offering similar installations. However, design remains the most crucial component. I’d definitely evaluate this and see if either is proposing a buffer tank. BG is supposed to be phasing these out from their designs and proposals, which could result in hardware savings as well as long-term running cost savings.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Yes my BG quote includes a buffer maybe as a thermostat or TRV was suggested downstairs (which I did not want had it been explained). I am questioning whether my BG man was an installer as he did not seem to be able to suggest, for instance, what I needed to provide for running the services under the path. He talked of piping but no mention of cables which are also rather necessary! I don't know if BG will produce a more detailed report after paying my deposit but anyway OE will not be surveying till 31st July. I wish I had started this process so much earlier as time is rushing by.
@jancold Just a thought, when you say the Octopus quote was half BG, what are we talking about here? Not £500 v £1000 I take it 🙂 If it was then of that order then the system designs would need to be scrutinised closely.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody It is £2300 for OE (assuming they do not alter it in the survey) and £4200 for BG which was down from £5900 initially. As you say I have to wait for the OE Survey and detailed report.
However if the boiler flow temp reading was reasonably accurate: I ran it 24/7 for the last two winters at an indicated 40C and only on the coldest days it fell below 19C. I know the Kitchen /Diner rad and Bathroom towel rail is far too small and maybe I need a rad at the top landing (according to the MCS rule book).
Since no piping changes were suggested the only changes can be the radiator output/size? and the system setup. About which I need to learn to understand before I even think about fiddling with it.
@jancold To me its a no-brainer then, a max 40C flow temp should give you a very pleasing SCOP. You seem aware that a buffer tank isnt usually a good idea so its not a plus point for BG.
What I managed to do in my house to keep costs down was change the largest radiator I needed to and then shuffle the others down to the next smallest room so pretty much everywhere got an upgrade.
I used 15mm plastic pipe to feed the rads which made for a very easy install and they have a large enough diameter to allow 1.89 kW at DT5 at 0.9mps flow (versus 2.75 kW for 15mm copper pipe)
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Octopus have now surveyed. He was very thorough and for instance felt the need to contact his electrical expert on a possible problem with my supply: thankfully all was good. All his measurements and photos are then passed to chair jockey designers so he suggested that if I am in disagreement with something to say no and make a counter proposal they want to please the customer.
I now await the detailed report but his heat loss was a lot higher than BG at 5.25 (BG 3.46) my heat punk result was 4.9 which agreed more closely. Also the radiator changes on the ground floor are closer to my Heatpunk predictions but as they require two new radiators they may want to charge me for them. So I guess it will be a 6kW Daikin.
They will also supply a larger towel rail though it has not got the required output. I may query this as I am not against a radiator and like a warm bathroom.
They will lay a gravel base for the Heatpump BG won't. I provide a trench for the pipework they do the rest. Surely If I made up an insulated pipe there could be problems with the warranty? BG made no mention of how to route the electrical supply or data cable.
I could have gone for the Cosy6 but he admitted it was not quite as efficient so I'm sticking with Daikin. It was suggested using the immersion in the summer and switch the heat pump off, that does not make sense to me.
Has anyone had a bathroom towel rail on the DHW circuit to dry towels all year round? Is this a bad idea?
I mentioned I would like a design temp of 45 and it was noted and, if necessary taken up with sales.
There will be a volumiser which he sometimes calls a buffer "to help with the defrost cycle" is this bull**It?
The property is about 2 meters above the road and he was concerned about lifting the heat monster up! I said I could rig a derrick (no not Derek M) or rent a Telehandler or platform surely that can be overcome fairly easily!
So now it is another wait...
@jancold The only reason i can think of to suggest using the immersion in summer would be to turn the heat pump off completely to avoid its standby losses, but I would be very surprised if they were large enough to make it profitable to do given the extra energy needed by the immersion.
Re the towel rail, do you mean just have the towel radiator heated when the DHW cycle is on, which would only be for an hour or two a day? The rest of the day it would be cold, so it doesnt seem like a good idea to me.
My understanding of a volumiser is to ensure that there is always enough volume of water in the system for the heat pumps minimum requirement to smooth out cycling and provide energy for defrosts. I dont have one as I know I have sufficient volume in my pipes and always open radiators
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@jancold We have an ‘oversized’ radiator in the bathroom as we wanted an elevated temperature compared with MCS guidelines. We achieve the 25 - 26 degrees C. - our installers took note of my requirements on this matter. We also have a towel rail above the radiator; we have a ‘dual fuel’ fitting and use the immersion element in it during the summer (approx. 300 watt consumption per hour) I close one of the towel rail valves if we want to heat the rail to the higher temperature in the winter. The element heats the rail to a higher temperature than the ASHP circuit would. I close the valve so that I am not returning hotter water to the ASHP system than it would expect to see as this I feel, would cause confusion to the control circuitry. The electrical element is controlled via a Myenergi Eddi; we use the relay board and I programme that to give power to the rail for 3 hours in the evenings. Anything else I can tell you - please ask! Regards, Toodles.
Toodles, he heats his home with cold draughts and cooks his food with magnets.
- 21 Forums
- 1,960 Topics
- 42.5 K Posts
- 48 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
Curtains and the loss through the window is what I was ...
By JohnR , 51 seconds ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 27 minutes ago
-
RE: SolarPV tables / online calculator
By Gary , 1 hour ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Yes, that sounds correct. I would say try both options...
By Old_Scientist , 10 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 11 hours ago
-
RE: Setback savings - fact or fiction?
The great thing about science is that it doesn't care o...
By JamesPa , 12 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 14 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 16 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 18 hours ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 19 hours ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 20 hours ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 23 hours ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 24 hours ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Towel rails. An unexpected final hurdle
@jamespa Beware; the use of the term ‘WC’ might lead to...
By Toodles , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
-
RE: Baxi Air Source Heat Pump tips and tricks please
@cathyem1 - thanks for the update. Let us know how it g...
By cathodeRay , 2 days ago
-
RE: Low COP and unevenly heated rooms with 12kW Samsung AE120MXTPEH / AE260TNWTEH
@editor But do you wear your peaked cap the right way r...
By Toodles , 2 days ago
Latest Topics
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 27 minutes ago
-
SolarPV tables / online calculator
By MichelleC 7 hours ago
-
Samsung Gen 7 R290 12kW is not behaving how I expected
By Joshua 19 hours ago
-
Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
By BAMi 22 hours ago
-
By Toodles 2 days ago
-
Solid manhole cover within r290 exclusion zone
By dbrb2 2 days ago
-
Towel rails. An unexpected final hurdle
By Davesoa 2 days ago